How can we prevent our LG heat pump from freezing up in cold weather?
@paul_tanner which software version do you have on your controller? e.g. mine is 3.05.5a
It DOES have DHW scheduling.
With ToU tariff (I'm on IOG) ... I heat hot water at cheap rate at night to 50 deg.
During the day I use a top up schedule to just 40deg. We never run out. 40 deg still requires a little cold added!
As you may know the controller has a boost function from immersion and also the 40deg temp can be temp boosted from controller
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Yes @Tim441 I have the same controller version.
It does allow boosting of hot water but (I checked the installer menu again and) there is no facility for automatically switching off DHW on cold nights. That's why I suggested an external solution.
Fortunately my external immersion controller (eddi) does have timers to take advantage of our ToU tariff.
Please let me know if I'm missing something.
I misunderstood your comment I think. It has a scheduler but it's on fixed days/times not according to outside temp.Â
It's a very strange issue as heat pumps are used successfully in far colder climates. So I'm inclined to think something is wrong with your setup.
Suggest you ask in
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
-
Daikin problem
1 year ago
-
Heating Turned Off but Radiators Still Warm
2 years ago
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 40 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
Thanks @toodles for the update. My PW3 is due to be i...
By Old_Scientist , 53 minutes ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 2 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 5 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Well at least that solves the mystery of where the exce...
By JamesPa , 7 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 7 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 23 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 1 day ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 1 day ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 2 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 3 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 3 days ago