Legionnaires and heat pumps
I'd like to find out what people think about the Anti-Legionnaires settings on the Ecodans (& probably other ASHP's too). Look at @rv3's power usage graph a few posts back. Look at the orange DHW (Hot Water) readings. Every 15 days, look at the Anti-Legionnaires peak. I'm not advising anyone to do anything that might pose a health risk, but I am interested in an honest discussion about it. Particularly since the insulation on those tanks means that it keeps heat in beautifully. Does anyone know how long & at what temp we have to keep it to be safe? Also, how often?
Good topic.
I think the risk of catching Legionnaires from an ASHP heating/DHW system is very, very small. It's primarily an airborne pathogen and since most ASHP systems are unvented, it's hard to see how it would get into the water. It could concievably enter at the water treatment plant but these are quite sterile environments and a lot of our water has stuff added to it that is likely to kill off any nasties.
If any make it into your DHW, they won't be very happy. This from Wikipedia.
Temperature affects the survival of Legionella as follows:[3]
- Above 70 °C (158 °F) – Legionella dies almost instantly
- At 60 °C (140 °F) – 90% die in 2 minutes (Decimal reduction time (D) = 2 minutes)
- At 50 °C (122 °F) – 90% die in 80–124 minutes, depending on strain (D = 80–124 minutes)
- 48 to 50 °C (118 to 122 °F) – can survive but do not multiply
- 32 to 42 °C (90 to 108 °F) – ideal growth range
- 25 to 45 °C (77 to 113 °F) – growth range
- Below 20 °C (68 °F) – can survive, even below freezing, but are dormant
So the Legionnaires cycle decreases the risk from very, very small to vanishingly small. If your DHW is at 50C constantly anyway, 60C for 3 hours once a week isn't going make a lot of difference.
Should you do it/keep doing it?
Only you can decide. 😉
@kev-m, that’s all bang on. I didn’t realise Legionnaires died so quickly at over 60C. Interesting.
Our DHW is set to 44C. The heat pump was set to take it to 60C for a least an hour once a week. I changed that to 10 days. We have an iBoost that heats our hot water to over 60C using excess solar - today we produced loads of solar so the ASHP system has reset its 10 day countdown.
The likelihood of getting Legionnaires via your tank is slim, but I still keep our settings activated and let the iBoost do its thing, as we’d rather be safe than sorry. In a world that’s going more and more bonkers with each passing day, we’ve opted to be cautious.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
The risk is very very small in catching legionella, in the whole of England and wales for 2016 there were 208 cases (most recent data found)
- 26 Forums
- 2,356 Topics
- 53.4 K Posts
- 249 Online
- 6,017 Members
Join Us!
Worth Watching
Latest Posts
-
RE: External pipework insulation
So I did find out that the insulation is Primary Pro an...
By jeegnesh , 16 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
I can't figure that one out either. The person I spoke...
By AndrewJ , 25 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Tax evasion is illegal - Tax Avoidance is an a...
By Toodles , 45 minutes ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@grahamf Another possibility that may be worth trying… ...
By Toodles , 56 minutes ago
-
RE: Advice on internal circulation pump noise
I dont think there is any material limitation but you d...
By JamesPa , 57 minutes ago
-
RE: Mitsubishi Ecodan Auto Adaption trial to stop cycling.
The interval you talk of, i think, will be 60min for an...
By F1p , 1 hour ago
-
RE: Electricity price predictions
Does anyone have a current graphic, visual or breakdown...
By Mars , 5 hours ago
-
Agree with @majordennisbloodnok on the setbacks. We hav...
By ChandyKris , 19 hours ago
-
RE: New Fogstar 15.5kWh upright solution
It is a matter of luck. 2ith Fogstar "instructions", to...
By Batpred , 20 hours ago
-
RE: Speedcomfort radiator fans
@deltona the way the links were added broke the page. A...
By Mars , 21 hours ago
-
RE: Setback savings - fact or fiction?
I agree! Even more so if we get an answer! But the chal...
By cathodeRay , 23 hours ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
This has been delayed from what I believe to be this ye...
By dgclimatecontrol , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
this is why I provided current flow temperatures in the...
By ksim , 1 day ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
There's many homes that would be quite a disruption for...
By dgclimatecontrol , 1 day ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@rhh2348 ...maybe this option is what you want? Alter...
By benson , 1 day ago
-
RE: Free Ecoheat Heat Pump Install
@old_scientist This does make the unit smaller as the b...
By dgclimatecontrol , 1 day ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
@old_scientist hiya mate, did you ever get to the botto...
By 9jwr9 , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
@majordennisbloodnok I think the HPDHD diagnosis may be...
By Sheriff Fatman , 2 days ago