Legionnaires and heat pumps
I'd like to find out what people think about the Anti-Legionnaires settings on the Ecodans (& probably other ASHP's too). Look at @rv3's power usage graph a few posts back. Look at the orange DHW (Hot Water) readings. Every 15 days, look at the Anti-Legionnaires peak. I'm not advising anyone to do anything that might pose a health risk, but I am interested in an honest discussion about it. Particularly since the insulation on those tanks means that it keeps heat in beautifully. Does anyone know how long & at what temp we have to keep it to be safe? Also, how often?
Good topic.
I think the risk of catching Legionnaires from an ASHP heating/DHW system is very, very small. It's primarily an airborne pathogen and since most ASHP systems are unvented, it's hard to see how it would get into the water. It could concievably enter at the water treatment plant but these are quite sterile environments and a lot of our water has stuff added to it that is likely to kill off any nasties.
If any make it into your DHW, they won't be very happy. This from Wikipedia.
Temperature affects the survival of Legionella as follows:[3]
- Above 70 °C (158 °F) – Legionella dies almost instantly
- At 60 °C (140 °F) – 90% die in 2 minutes (Decimal reduction time (D) = 2 minutes)
- At 50 °C (122 °F) – 90% die in 80–124 minutes, depending on strain (D = 80–124 minutes)
- 48 to 50 °C (118 to 122 °F) – can survive but do not multiply
- 32 to 42 °C (90 to 108 °F) – ideal growth range
- 25 to 45 °C (77 to 113 °F) – growth range
- Below 20 °C (68 °F) – can survive, even below freezing, but are dormant
So the Legionnaires cycle decreases the risk from very, very small to vanishingly small. If your DHW is at 50C constantly anyway, 60C for 3 hours once a week isn't going make a lot of difference.
Should you do it/keep doing it?
Only you can decide. 😉
@kev-m, that’s all bang on. I didn’t realise Legionnaires died so quickly at over 60C. Interesting.
Our DHW is set to 44C. The heat pump was set to take it to 60C for a least an hour once a week. I changed that to 10 days. We have an iBoost that heats our hot water to over 60C using excess solar - today we produced loads of solar so the ASHP system has reset its 10 day countdown.
The likelihood of getting Legionnaires via your tank is slim, but I still keep our settings activated and let the iBoost do its thing, as we’d rather be safe than sorry. In a world that’s going more and more bonkers with each passing day, we’ve opted to be cautious.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
The risk is very very small in catching legionella, in the whole of England and wales for 2016 there were 208 cases (most recent data found)
- 22 Forums
- 2,037 Topics
- 44.4 K Posts
- 35 Online
- 3,250 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
Welcome to the forum, @patch. I've nothing to add ove...
By Majordennisbloodnok , 8 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, in terms of ballpark pricing, if we assume a st...
By Mars , 2 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
@jamespa I used an assumed indoor temperature of 18C. I...
By Ad3628 , 15 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 16 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 19 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@editor Attached images of external insulation. Think...
By Dwynwen , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 2 days ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 2 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 2 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 2 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 2 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 3 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 4 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 4 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 4 days ago