Kev-M's ASHP Performance
The next round is to try and use weather compensation and thermostats together. Here’s what happened.
The theory is that setting a compensation curve that would normally make the house a few degrees too warm and limiting it by on/off thermostats will reduce cycling while keeping the house at a steady temperature. The aim is to get something like the below 45 deg set flow but with lower flow temps. Although even this didn't prevent all cycling.
But what actually happens is the weather compensation and thermostats just end up getting in each other's way. The thermostat causes ons and offs but in between there is a lot of cycling. This is because the ASHP will stop heating when either the thermostat temp (21 deg in my case) or the weather comp flow temp is reached and won’t start until the thermostat calls for heat and the weather comp flow temp is low. So the thermostat calls for heat and the ASHP starts heating. But the target flow temp is reached before the thermostat set temp, so the ASHP stops, even though the thermostat is still calling for heat. The flow (and the house) cool down a bit then the ASHP kicks in again. And repeats this until the thermostat set temp is eventually reached, at which time the ASHP stops, whether or not its flow temp is reached. The house then cools from 21.5 deg or so to 20.5 deg or so, the thermostat calls for heat and does it all again.
The below graph illustrates the above. You can see the 5am start up, the steady state running, the gaps when the thermostats switch the ASHP off and the 3pm DHW peak. There are only four periods of ASHP heating but these all include as much cycling as letting the ASHP run constantly.
The obvious way to stop the cycling is to increase the flow temp so that it requires a high enough output/flow, a bit like the fixed flow above. To get this to work the compensation curve is going to have to be very flat, not a million miles from the fixed flow.
But does it matter? Cycling for me is about twice an hour or so and in these conditions my COP is good. This was a warmish day using weather compensation only. I’d rather get the cold weather performance right...
But I like tinkering so I have now bumped up the warm end of the curve so that it’s 42 @ -2 and 33 at 20 and the thermostats are controlling the room temp. I'll report back.
This is what happened. There is almost no cycling. The outside temp was 0-12C. Is it better/cheaper? The house temperature varies more, which isn't as good. I don't know if it's cheaper but I suspect there won't be much in it. Although there are periods when the ASHP is off, the flow temp is several degrees higher than it needs to be. It's interesting to see the COP is low at very low ASHP consumption. This is because the ASHP itself is slightly less efficient at very low outputs and also because with the way COP is measured in my set up, the consumed energy is everything; the pumps, FTC controller the immersion (if it's used) and these are running all the time the ASHP is.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 16 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@heat-pump-newbie as I suspected. I measure/monitor my ...
By Old_Scientist , 7 hours ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 11 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 2 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 2 days ago
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 2 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 2 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 4 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 4 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 4 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 4 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 4 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 6 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 6 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 7 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 1 week ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 1 week ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 1 week ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 1 week ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
Members Online
No online members at the moment