The defrosts are every couple of hours. I think it reverses the flow? Anyway it causes the flow temp to drop so it ramps up the power to heat it up, overshoots a bit and settles back down. It's very consistent.
Each of these peaks/troughs uses up about 130 Wh more energy than if the ASHP had kept going steadily.
I'll have a look at these settings you mention.
Kev
Thanks Kev,
The fact that the water flow temperature appears to be reasonably constant when the ASHP is running constantly, would indicate that the upper and lower limits are not being reached, so are not affecting the operation. The limits are probably why the heat pump stops for a short period after the defrost cycle has been completed.
Defrost operates in the same way as my A2A ASHP, in that it speeds up for a while during defrost and often stops the compressor for a short period before restarting.
Looking at the thermistor adjustment procedure, it would appear that it is just an offset similar to the weather compensation, rather than a full calibration. If you wish, you could adjust the water flow temperature indication (THW6) and the water return temperature indication (THW7) on the FTC controller to match the readings on your MMSP heat meter. You would then be able to see how the measurements vary as the required water flow temperature is varied by the weather compensation. A word of warning. Try making a 1C adjustment and note the affect, since a large adjustment may cause a change in the indoor temperature, before the controller readjusts. You will also need to adjust the weather compensation curve to match the new readings.
When time allows, I would suggest that you go through the FTC controller settings and note the values on a copy of the Engineers Form shown on pages 40 to 42. It may then be possible to see further ways in which your system could be optimised.
OK. I'll do a summary at the end of the month but here's the last few days. This is having most of the house 21-22C all day and night. Tonight's going to be over 40 I think:
Date | kWh | Ambient |
22/11/21 | 33.2 | 3.9 |
23/11/21 | 22.5 | 6 |
24/11/21 | 18.9 | 6.9 |
25/11/21 | 34.2 | 3.5 |
26/11/21 | 28.9 | 4.4 |
27/11/21 | 36.6 | 2.7 |
Kev
Posted by: @derek-mThanks Kev,
The fact that the water flow temperature appears to be reasonably constant when the ASHP is running constantly, would indicate that the upper and lower limits are not being reached, so are not affecting the operation. The limits are probably why the heat pump stops for a short period after the defrost cycle has been completed.
Defrost operates in the same way as my A2A ASHP, in that it speeds up for a while during defrost and often stops the compressor for a short period before restarting.
Looking at the thermistor adjustment procedure, it would appear that it is just an offset similar to the weather compensation, rather than a full calibration. If you wish, you could adjust the water flow temperature indication (THW6) and the water return temperature indication (THW7) on the FTC controller to match the readings on your MMSP heat meter. You would then be able to see how the measurements vary as the required water flow temperature is varied by the weather compensation. A word of warning. Try making a 1C adjustment and note the affect, since a large adjustment may cause a change in the indoor temperature, before the controller readjusts. You will also need to adjust the weather compensation curve to match the new readings.
When time allows, I would suggest that you go through the FTC controller settings and note the values on a copy of the Engineers Form shown on pages 40 to 42. It may then be possible to see further ways in which your system could be optimised.
You're assuming the installers didn't leave me this with their comprehensive handover pack and commissioning notes?
And you'd be right. 😆
Posted by: @kev-mOK. I'll do a summary at the end of the month but here's the last few days. This is having most of the house 21-22C all day and night. Tonight's going to be over 40 I think:
Date kWh Ambient 22/11/21 33.2 3.9 23/11/21 22.5 6 24/11/21 18.9 6.9 25/11/21 34.2 3.5 26/11/21 28.9 4.4 27/11/21 36.6 2.7 Kev
Thanks again Kev,
The above shows how a few degrees change in ambient air temperature can affect the operation and efficiency of an ASHP.
Will be very interested in the summary of November
I'm awaiting an isg for mine so I can monitor and tweak remotely, currently out of stock so every time I want to adjust mine I need to go into the loft!
My system has weather compensation and a curve monitor, any guidance on which settings I should potentially use?
My latest tweaks (can't resist 😆)
Weather compensation curve recalibrated so I can set my offset from -4 back to zero
DHW set to come on 12 noon-2pm only. We still have electric showers and don't use much HW. Better it comes on when it's a bit warmer out
And (most radically), heating is programmed to be off 12am-6am. I know the 'slow and steady wins the race' theory for ASHPs and I know the ASHP will have to work hard when it wakes up. But.... I have radiators, a relatively large ASHP and the house has a relatively low thermal mass. Six hours doing nothing will take a big chunk out of the kWh. It also just doesn't feel right heating the 12 other radiators when there's nobody there. If it's too cold in the night or morning I'll revert back. I also won't tell Mrs M and see if she notices or not. Risky, very risky ....
Well that sort of worked. The heating went off as planned. But it warmed up overnight and while the heating came on as planned, the radiators weren't really warm enough to heat the house quickly. Temperature was only down slightly though and a quick boost on the controller did the trick. It's going to be a cheaper day today thankfully.
Posted by: @kev-mWell that sort of worked. The heating went off as planned. But it warmed up overnight and while the heating came on as planned, the radiators weren't really warm enough to heat the house quickly. Temperature was only down slightly though and a quick boost on the controller did the trick. It's going to be a cheaper day today thankfully.
I have seen some users in the large government sponsored trials at the moment turn off their heat pumps overnight, but they have high temperature heat pumps and turn them back on a bit earlier than you did.
Whether they spend more over a year would very much depend on individual usage requirements as they are obviously giving up quite a bit of efficiency by having their heat pumps off perhaps several times a day. I can't imagine many users going down this route but it will be interesting to see what comes out of the trials if anything is published.
Are you going to try it a few more times to get some more data points for your setup?
Posted by: @kev-mMy latest tweaks (can't resist 😆)
Weather compensation curve recalibrated so I can set my offset from -4 back to zero
DHW set to come on 12 noon-2pm only. We still have electric showers and don't use much HW. Better it comes on when it's a bit warmer out
And (most radically), heating is programmed to be off 12am-6am. I know the 'slow and steady wins the race' theory for ASHPs and I know the ASHP will have to work hard when it wakes up. But.... I have radiators, a relatively large ASHP and the house has a relatively low thermal mass. Six hours doing nothing will take a big chunk out of the kWh. It also just doesn't feel right heating the 12 other radiators when there's nobody there. If it's too cold in the night or morning I'll revert back. I also won't tell Mrs M and see if she notices or not. Risky, very risky ....
@kev-m
Interested in the first sentence of your post. I too wish to return my offset back to zero in order to reclaim the full range of adjustment available to me. Currently I have set it to +4 and occasionally even +6 in this very cold snap. However I don’t know how to do it. I’m assuming it’s an adjustment to the compensation curve? All I know is putting on + figures makes the house warmer. Can you tell me please what I need to do in order for my current +4 can actually be my zero. In other words I reset to zero but it’s operating at the current +4. Hopefully that question makes sense. SWMBO is giving me a bit of grief suggesting it isn’t warm enough and even wanted the log burner in the lounge lit last night. I had a wisdom tooth extracted yesterday and feeling grumpy and under the weather (comp’ curve) so some peace would be good.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
- 22 Forums
- 2,060 Topics
- 45 K Posts
- 33 Online
- 3,318 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
Very well said. When people complain about 'the counc...
By JamesPa , 37 minutes ago
-
RE: Using AI to optimise your system
Some strange stuff comes out of AI, hope your output is...
By Johnmo , 4 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
Difference is I’m actively encouraging as much cycling ...
By Mars , 4 hours ago
-
RE: Discharging battery to grid whilst charging EV
@majordennisbloodnok I should probably clarify: I wasn'...
By AndrewJ , 10 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@grahamh-uk I looked into adding a Wifi kit to my Samsu...
By TechnoGeek , 12 hours ago
-
And here's a follow up article on the same subject that...
By Mars , 12 hours ago
-
RE: Renewables & Heat Pumps in the News
@johnmo Ours is powered from solar energy (with grid ba...
By Toodles , 16 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
I'm curious who you think are the reluctant ears. Cert...
By JamesPa , 1 day ago
-
RE: Commencing on an ASHP Installation Process
If that is the case then I would add to my earlier post...
By JamesPa , 1 day ago
-
RE: Battery sizing - How low can you go!
The second 6.5 kWh Growatt battery was installed today....
By ChandyKris , 3 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
So… I called them this morning and I’m up and running o...
By Westkent , 3 days ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Your system seems to be more modern than mine, mine was...
By abbote , 3 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
Braver person than me. No way I would go down that rout...
By Johnmo , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@arundalep yes I have no issue with this. The observati...
By benson , 4 days ago
-
-
RE: Rate the quality of your heat pump design and installation
So your Halo lite should really do nothing, when connec...
By Johnmo , 4 days ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
This is indeed welcome news. In addition the new legi...
By JamesPa , 4 days ago
-
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
@johnmo I think we’ve been trudging through the same...
By SUNandAIR , 5 days ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 7 days ago