Is My Midea Heat Pump Inherently Defective?
Posted by: @bobtskutterSwapping the radiator for a fan coil might not give you additional heat output because it's not the radiator that's causing the "restriction".
Absolutely, I am very aware of that! Moving to a fan coil is an (major) aesthetic improvement, but only once I know it will have adequate flow.
I am still trying to think of a way of making a diagnosis ie where is the obstruction, and what is it. I know how to drain the system and so also know it is not a trivial undertaking, and I would prefer to know if possible what I need to fix while it is drained down. I am also not inclined to do it during one of the coldest month's of the year, in case something goes wrong!
Midea 14kW (for now...) ASHP heating both building and DHW
Naturally I was concerned that increasing the energy out (delivered to the house) by opening up the lock shield valves might increase the energy in (used). I now have enough data to be able to plot hourly energy in and mean room temp for hours at a particular OAT for before and after I opened up the valves. I have done this for year to date (note date time axis is categorical, they are just the hours that match the OAT criteria), for mean OATs of 5 (5.0-5.9, normal running) and 2 (2.0-2.9, defrost territory) , and marked when the valves were opened with a down pointing arrow:
Interestingly, no obvious penalty, in fact very possibly (need more data, and there are things I haven't controlled for...) an improvement! In both charts the mean room temp improves a bit (as expected) and in both charts the energy in appears to fall. It's more marked at 5 degrees than 2 degrees OAT, but still present on both charts. Truly heat pumps are a miracle, that surpasseth all understanding...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayTruly heat pumps are a miracle, that surpasseth all understanding...
I've just remembered...two days after I opened the LSVs I dropped the weather compensation curve 2 degrees, and then 2 days later I dropped it by another 2 degreees.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayI dropped the weather compensation curve
That'll do it 😉
Can you go lower?
Bob
Posted by: @bobtskutterCan you go lower?
Very possibly. The IAT is at the warm end of my preferred range, and it looks like we'll have fairly settled though cool weather here over the next few days so a good time to experiment. Watch this space...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayTruly heat pumps are a miracle, that surpasseth all understanding...
Somehow that feels like the basis of a motto/strapline.
Without a doubt the combination of the nonlinear response to the main variables, the inherent complexity of the thermal dynamics of houses, contrasted with the extremely simplicity of the thermodynamics on which it is all based, really does make them fascinating beasts.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cathoderay any updates in this mild spell are you boiling indoors yet?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithany updates in this mild spell are you boiling indoors yet?
Thanks for asking. Yes, the indoor air temperature has certainly been more consistent, a bit higher by a degree or two despite the fact I have lowered the leaving water temperature by a few degrees. The Mark 1 Human Sensor (me) also reports good comfort levels. All in all a success, and I don't think my costs have increased greatly, if at all, the lower LWT appears, as expected, to mean better performance, with COPs at times in the 4-5 range. Sometimes I think we forget how much difference a change in COP can make. For example, a seemingly not very large change, at least in absolute terms, from a COP of 3 to 4.5 means, all other things being equal, including having the same heating load, the unit costs part of my electricity bill falls by one third - where I would have paid £100, I now only pay £66.66, not a trivial saving.
Here's my chart for the last week. On Monday, I restarted the overnight setback (using room stat down to 16 degrees between 2100 and 0300), as I am interested to see how the now all valves open system copes with the recovery period after the setback. Previously it struggled, sometimes taking 12 hours or so to get back to temperature. On Tuesday morning, after a mild night, it recovered well, back to where it should be by 0700. Last night was significantly colder, and the recovery has been a bit slower, but by no means a disaster, despite being in defrost territory. Bear in mind this is partly managed by my auto-adapt script, which adjusts the LWT depending on how far the actual IAT deviates from the desired IAT. At the moment the script is set up to do one degree of LWT change for every degree of actual vs desired IAT deviation, up to a max of 3 degrees eg if desired IAT is 19, actual IAT is 17, deviation is 2 degrees and LWT increases by 2 degrees. These parameters are easily changed, by editing the script and restarting it. I am going to run the system as is for a week, and then see if it needs any tweaking.
Note: subsequent comments here about setback running have now been moved to another thread here.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,378 Topics
- 53.9 K Posts
- 197 Online
- 6,060 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Radiator sizing sanity check
No chance! Largely, hence my suggestion to do some...
By JamesPa , 3 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
As it turns out this is correct! All I needed to do was...
By benson , 4 hours ago
-
Here is an update of the setback we operate on our syst...
By SUNandAIR , 6 hours ago
-
RE: Grant ASHP 17.5 kw. weather curve
@chinkoa Sorry there are two separate thoug...
By JamesPa , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@transparent As easy as putting sparklers in champag...
By Papahuhu , 7 hours ago
-
@f1p Looks good, and will likely be something I use whe...
By Sheriff Fatman , 10 hours ago
-
RE: Cascade 2x Grant Areona 10kw ASHP - Ongoing setup issues
Either complete Bow Locks or at best a marginal effect....
By JamesPa , 12 hours ago
-
Hi all I’m looking to get some insight on what others...
By Renewables345 , 13 hours ago
-
RE: The Great British Heat Pump Owner Persona Survey: Let's Build Our Archetype!
@mosibi, go on then, complete the survey. Let's get the...
By Mars , 13 hours ago
-
RE: Water Hammer After Heat Pump Install
@jaynieq I wish you luck with this one. I think the ma...
By JamesPa , 15 hours ago
-
RE: Optimum new build house design for Heat Pump
From first principles I would say: Definitel...
By JamesPa , 1 day ago
-
RE: Weather compensation- why you should use it
As good a place as any to drop this video:/p>
By Mars , 1 day ago
-
RE: Forum updates, announcements & issues
@transparent D'Oh - I did look before I posted but I mi...
By dr_dongle , 1 day ago
-
Compatibility with Samsung AE080RXYDEH
I am new to all this. We have a SamsungAE080RXYDEH that...
By John999 , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Maybe you should buy your additional batter...
By Bash , 2 days ago
-
RE: Data Accuracy Problem: Daikin 8kW Heat Pump's Onecta App vs MMI Power Consumption
@nursethescreens Yes, comfort and happiness of the fami...
By Toodles , 2 days ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
Thanks folks. I had tried googling an ethernet lab adap...
By z8lccda , 2 days ago
-
RE: Changing from 4-port buffer to volumizer
@toodles I'm not concerned that the behaviour is not no...
By Andy1618 , 2 days ago
-
-
RE: Setback savings - fact or fiction?
I agree, and I think there are two things in play here....
By cathodeRay , 2 days ago