Incidentally this is the sort of thig you can do if you can measure your consumption, in this case from half hourly gas meter readings.  Its how I sized my heat pump.  Two professional surveys (3 hrs each, one costing £300 the other free but still worthless) said 16kW, actual is 7kW. 

Hence why I am always very cautious about surveyed heat loss most particularly in older buildings that have had miscellaneous fabric upgrades and other difficult to determine factors.

 

 

PS - Back to cascades - I think Mitsubishi are one of the go to manufacturers.  If you got the 11.2kW and 8kW R290 - the latter of which has 2 compressors 2kW fixed and 6kW variable - you could go all the way from 19.2kW to 2kW without cycling, given the right control.  Now that would be a smart way to run a cascade heat pump and its more or less guaranteed to cover your heat loss both at top and bottom ends.


This post was modified 4 hours ago 4 times by JamesPa
This post was modified 3 hours ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@guydeb)
Eminent Member Member
Joined: 4 months ago
Posts: 15
Topic starter  

So this is from Grant - can't fault them for speed of response to an email about 2 x 10kW:

When using two R32 Aerona³ heat pumps connected in a cascade configuration, one of the two (the supplementary unit) will be controlled by the other (the lead unit).

Under this hydraulic arrangement the lead unit can be used to provide both Heating and DHW, but the supplementary unit will be used only for Heating.

Unfortunately, as per the above, it is not possible to supply two separate flow temps simultaneously. Normal operation would be to target the higher temperature circuit ( Rads ) and use a blending/mixing set to control the UFH circuit.

*Please be aware, Grant UK R290 heat pumps are not currently suitable for cascade configuration.



   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2856
 

Posted by: @guydeb

So this is from Grant - can't fault them for speed of response to an email about 2 x 10kW:

When using two R32 Aerona³ heat pumps connected in a cascade configuration, one of the two (the supplementary unit) will be controlled by the other (the lead unit).

Under this hydraulic arrangement the lead unit can be used to provide both Heating and DHW, but the supplementary unit will be used only for Heating.

Unfortunately, as per the above, it is not possible to supply two separate flow temps simultaneously. Normal operation would be to target the higher temperature circuit ( Rads ) and use a blending/mixing set to control the UFH circuit.

*Please be aware, Grant UK R290 heat pumps are not currently suitable for cascade configuration.

Fair enough.  As I suggested above there are all sorts of games that could be played,  but which are easily doable depends on the capability of the controller, which may vary widely  As you are considering a cascade this is may be an important area of study unless you want to tinker with home assistant etc. 

I doubt the grant R290 pumps are inherently impossible to cascade, but it's entirely possible that the controller doesn't have the required features.    Cascades are unusual in a domestic context so there is little market for the software.  In the commercial world cascades are relatively common but so are sophisticated building management systems.  In fact the simplest control is probably exactly the same as a supplementary heater, off of the same contact and software, just switching in the secondary when the OAT goes low enough.  I wouldn't be surprised if that's what the grant one is based on their description.

Of course you could have 2 separate systems not cascaded, one for upstairs one for down.  That would allow 2 separate flow temperatures.  However you would lose the modulation depth advantage.  Possibly some clever plumbing could overcome this off course.  Unfortunately my knowledge of cascades in practice is very limited although I do seem to remember that Mitsubishi are a go to, perhaps their cascade controller is particularly good?

 


This post was modified 30 minutes ago by JamesPa
This post was modified 23 minutes ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@guydeb)
Eminent Member Member
Joined: 4 months ago
Posts: 15
Topic starter  

hmmmm - sadly the Mitsi's are more expensive (£2,700 the pair) and wider (by 300mm the pair). The Mitsi R32s are a little cheaper, do they have the same cascade capabilities?



   