@johnmo max flow temp of 32C! Do you have huge radiators or very little heat loss? You can’t be describing ufh since it’s responding too quickly.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@johnmo max flow temp of 32C! Do you have huge radiators or very little heat loss? You can’t be describing ufh since it’s responding too quickly
It's UFH on 300mm centres, but prior to starting today I had been messing about with the heat pump a few days, so floor (or return temp was 20.8 this morning) so not much energy was needed to get it back to steady state. The return temp has been sitting at 21.1 degs for the last 10 hrs with no further heat input. Even though its cool here, we have no real need to add heat, but it was cool enough to play with ASHP.
Run data
Run 1 started at 07.55. Force stopped first cycle at 27.5 flow temp at 25 min run time (08:25).
Run 2 starts 08.35 (10 mins off) stops at 09.05 run time 30 mins. No changes
Run 3 starts 09.25 (20 mins off) stops at 09.45 run time 20 mins. No changes
Run 4 start 10.10 flow temp 21.5 at restart (25 mins off) stops at 10.35 run time 15 mins. Increase B25 to 0.5 to increase off time and run time.
Run 5 temp 21.2 at restart 11.12. 35 mins off. Run. Stops 11.30 run time 18 mins
Run 6 DHW 35 mins
Sun comes out house at 21.5. return temp 21.1
Running curve set to 25 degs at 12 OAT and 32.6 at -5 OAT. Restart delta 6.8 so unlikely to automatically restart until OAT gets down to about 8 or 9 degs, which should be fine. May need to fine tune a little in the heating season.
Had to make a small change this morning as the summer house had cooled to 18 degs this morning, because the heat pump wasn't starting. The 25 degs start temp on the WC curve was slightly too low. So instead of the WC curve starting at 25, I changed to 26 at 10 OAT. It did 4 starts between 7 and midday running an hour and 33 mins in total run time. Weather got warmer once house hits 21 ASHP sits waiting. Return temp is about 0.2 degs above the restart temp at the moment.
Just thought I would post back in this thread for any future viewers as what what Ive discovered.
It appears that the Samsung controller does not have any way of allowing a user to alter the hysteresis settings directly. They are set to the Samsung default.
Indirectly you can manipulate the level of cycling by opening/having more emitters and raising the flow temperature. This means that even though you might be able to heat your house at a lower flow temperature, you may need to keep it artificially high (and at a reduced COP) to reduce cycling.
Samsung heat pumps can be fitted with an extra PCB (MIM-B19N) to allow reading and setting of operating values directly via modbus. I would be interested to know if the hysteresis settings can be changed this way, if anyone has any experience of using the board.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoodyappears that the Samsung controller does not have any way of allowing a user to alter the hysteresis settings directly. They are set to the Samsung default.
The method applied here (below) can get around the issue with water law and thermostat. Basically run time is dictated by thermostat hysterisis on top of the water law curve.
Take a look here, post 28 of 63
@johnmo Thanks for the link. I am in effect running it in pure weather compensation mode as my samsung controller/thermostat is in my hall not my living room and set to 24C (which it never reaches). I am wondering if it might be better to extend the cable and put it in the living room and lower the thermostat temperature to turn off the pump when it hits 22.5C.
I have seen some posts which mention changing FSV #2092 which supposedly changes the amount of time the pump runs for after the heat pump is turned off. This would seem to be helpful but I cant verify these settings looking at the Samsung documentation.
If the hysteresis setting could be changed via modbus then its something i would like to play around with. If nothing else it would make a nice project 😉
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Some people even enjoy weeding their gardens I’m told!😉 Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodles@bontwoody Some people even enjoy weeding their gardens I’m told!😉 Toodles.
If you like weeding, we have a nice 45 Deg bank full of weeds, or is that a wild flower meadow? I think it's a wild flower meadow, the wife weeds.
@johnmo Beauty is in the eye of the beholder…😉 Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodles@bontwoody Some people even enjoy weeding their gardens I’m told!😉 Toodles.
LOL at least I can do my hobby out of the rain!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @AnonymousPosted by: @bontwoodyappears that the Samsung controller does not have any way of allowing a user to alter the hysteresis settings directly. They are set to the Samsung default.
The method applied here (below) can get around the issue with water law and thermostat. Basically run time is dictated by thermostat hysterisis on top of the water law curve.
Take a look here, post 28 of 63
This is essentially how I have been running my Samsung - FSV #2091/2092 set to option 1 so the compressor can only be turned off by the 3rd party room stat. My unit is oversized and wants to cycle because it's putting out too much heat. I'd like LWT of 30C at 15C OAT, but the lowest the unit will achieve is 33-34C.
So I just let the 3rd party room stat switch ON/OFF calling for heat, set to 19C (we like it on the cooler side) and let the unit find it's own minimum LWT. Additionally, I can vary the hysteresis of my room stat.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @bontwoodyIndirectly you can manipulate the level of cycling by opening/having more emitters and raising the flow temperature. This means that even though you might be able to heat your house at a lower flow temperature, you may need to keep it artificially high (and at a reduced COP) to reduce cycling.
The COP may actually be better at that higher flow temp due to the reduced (or elimination of) cycling? All else being equal, a lower flow temp will give a better COP, but all else isn't equal when the unit is constantly cycling.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 47 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa That flow rate sounds rather high James! Regar...
By Toodles , 28 minutes ago
-
@jamespa thanks, I appreciate the offer. For n...
By DREI , 11 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
@transparent what I don't understand about these "rogue...
By Scalextrix , 13 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have 3 women in the house, 2 little ones, so my heati...
By DREI , 16 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 16 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
Mostly, I think, but with some caveats. I set the TI...
By cathodeRay , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 4 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 4 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 5 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 5 days ago