How to increase DHW water temperature on Samsung Gen 6 Control Panel
When I attempt to raise the temperature of the DHW from its value of 50 degrees C I get an error message indicating that this is the maximum. It's in Standard mode. I can't find any reference online to rasing this maximum. Does anyone know where this setting is?
We're trying to indentify what makes so much noise it wakes us up at night. We want to find out if getting the heat pump to heat the DHW is a cause by turning the water heating on and off and seeing if the noise comes and goes in unison.
Which model Samsung. if its an older one and the max FT is 55, which is quite possible, then its equally possible that the DHW is limited to 55-5=50. I dont know this from Samsung specifically, just applying general principles
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@imb123 There are some settings that you need to adjust for DHW max setting:
1. You need to go into the "Field Settings" and navigate to #3021 which sets the maximum the pump can heat to
2. Navigate to field setting #3022 and ensure it is set to zero otherwise the pump will only heat to Max - Stop value
3. Ensure you have enough user tank temperature control range by checking field setting #1051
I assume your pump is capable of acheiving 55 C tank temperature which would require a leaving water temp of approx 63 C? (High Temp ASHP)
Hope this helps.
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
@imb123 which model do you have?
DHW temperature can be set higher but anything above 50C will probably engage the immersion heater. As far as I know though, this setting is not accessible to homeowners.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @editorDHW temperature can be set higher but anything above 50C will probably engage the immersion heater. As far as I know though, this setting is not accessible to homeowners.
As you say that will almost certainly be the case with an 'older' (low or medium temp) Samsung model, but possibly not with the HT models.
Vaillant, for example, with their R290 models, do the disinfection run natively and don't (by default) rely on or require any connection with the immersion heater at all. I have no idea if Samsung do similar but of course this is only possible with models where FT can go up to 70/75C
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I have the Samsung high temp quiet model and when set to economic mode the pump can heat to a maximum of 55C. To heat it higher (Standard etc) it has to engage the immersion but also the user temp range needs to have been set to allow this. Mine is currently set to 65C however the pump never gets there because I do not have immersion support set up on the pump (it is controlled independently). 🙂 The pump and controller are less than a year old so should be the latest model.
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
@technogeek I have the very same issue. I've bought HT Quiet (R32) just because it is capable to heat water to 70C (at least this is what they say in advertising) but for some reason I can't set up more than 55C for DHW. Also disinfection cycle is not working without booster heater connected do DHW tank (written in manual). This is huge disappointment an honestly does not understand why is that. I understand that flow temp must be higher to achieve 55 water temp but I would expect more. Did you find any solution for that ? What water temperature do you use for DHW ? Seems my only possibility is to buy 3KW booster heater.
@misiak Hello. The Samsung pump is capable of generating a flow temperature of up to 70C. The heat transfer into DHW (depends on storage tank efficiency) from the tanks coil is about 8C - 10C less. This means your heat pump on its own can only produce up to 55C DHW. To achieve 60C or above you need to finish the DHW cycle using the immersion boost if fitted.
Its a matter of physics, the flow temperature needs to be at least 8C hotter than the required DHW temperature for heat transfer to happen.
Using this process is expensive and to be honest not needed. You will find 55C plenty hot enough. If you have a high turnover of hot water then a legionella cycle is only required after being on holiday or a length of extended time the water has been stagnant in the tank.
The HeatGeek team do a very good video on the subject of DHW generation and legionella cycles etc, well worth a watch 🙂
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
@technogeek thanks for a reply. I really found a field setting for controller which allows to set 70Cbut (it was set to 55C so I was confused at first) as you have said this is not possible to achieve without immersion heater. At 70C this is a torture for the pump anyway and it yields with max. 60C for a DHW temperature.
So now it matters what do you consider as stagnant water. I've intentionally bought a bigger tank (280L) to run with a lower temp ~48C. Before I had 120L electric boiler with 70C water. My turnover is mostly 25%. Middle week and weekend maybe 50 - 75%. But some days it could be even less than 25%. Can you see it as a problem with water heated to 48C (middle of the tank) or it's fine. For me this legionella is kind of theoretical problem since I've never encountered any issue from it so not sure if this is overrated issue or not.
Would you mind to share video to that cycle ?
Thanks!
@misiak I think this is a link to the heatgeek resource
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
Im just in the process of connecting up my mixergy cylinder coil to my Samsung Gen 6 and have a similar problem. Only in my case the max temperature is 45C. Ive tried the FSV changes about but its stuck there. Im guessing that its the maximum my heat pump can attain without engaging the immersion (R32). Ive told the Samsung controller not to use that as I want to use the Mixergy app to schedule it.
I dont have the mixergy HP control box, but imagined I could still run the DHW via the heat pump without it. It just wouldnt record the energy used in the app. I guess though that without it the destratification pump wont run and with the coil being at the upper end of the cylinder that will be a problem 🙁
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 1,098 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
That’s my pleasure, @andrewj. The only challenge now is...
By Majordennisbloodnok , 2 hours ago
-
RE: Electricity price predictions
@toodles @skd Then there is not going to be much from t...
By ChandyKris , 3 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I reckon Andy might know a thing or 2 about...
By Bash , 3 hours ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 4 hours ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 4 hours ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 5 hours ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 5 hours ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 6 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 9 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 12 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 14 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 2 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 2 days ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago