Hot water temperatures
Come early evening after 3 showers and quite a bit of washing up throughout the day my ecodan with a 170L tank shows a temperature of 16c.
As it seemed that the water coming out the kitchen tap was still too hot for the hands I put a gauge to it and it shows 50c.
My tank is set to heat to 60c at 3.30am.
How could this be happening??
Not necessarily a massive problem I know.
Any advice appreciated.
The hot water is taken from the top of the tank, to be replaced by cold water at the bottom of the tank with a minimising of disturbance. (I am presuming you have a Mitsubishi tank, though this should still hold true for different tanks to different degrees.) This keeps a decent stratification between the blocks of hot water and cold water, the boundary gradually rising up the tank. Your tank will probably have two thermistors measuring the temperatures at different heights. If I recall correctly it is the lower of the two that is displayed as the tank temperature so it can drop surprisingly low while there is still a lot of hot water remaining in the tank above its level.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Posted by: @westkentCome early evening after 3 showers and quite a bit of washing up throughout the day my ecodan with a 170L tank shows a temperature of 16c.
As it seemed that the water coming out the kitchen tap was still too hot for the hands I put a gauge to it and it shows 50c.
My tank is set to heat to 60c at 3.30am.
How could this be happening??
Not necessarily a massive problem I know.
Any advice appreciated.
Thats sounds like seriously good news, you have a tank that is well stratified! Rejoice!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks for the replies.
My mind is at rest although it would be great to have more of an idea when it about to run out of H/W.
Yes it is a Mitsubishi tank.
8.5 system.
No pipes around tank with pipe insulation so will look to sort that.
- 22 Forums
- 2,086 Topics
- 46 K Posts
- 26 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Vaillant AroTherm Plus 7kW
@scalextrix if your under unit heater is like our Myson...
By Judith , 39 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@cathoderay how did you get a script to run for that- d...
By benson , 2 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness bold choice on the Kronoterm. Nice! Wi...
By Mars , 7 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 1 day ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 2 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 3 days ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 3 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 3 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 3 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 5 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 6 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 6 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 6 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 6 days ago