12kW Samsung ASHP with Hive thermostat – help needed please
I have a 12kW Samsung ASHP with Hive thermostat that my installers (Greener Living) don't seem to be able to make work consistently or economically.
The whole system is installed into the loft with the thermostat down in the L shape living/dining room. about 2 weeks ago the bedroom it sits over can hear what i think is the expansion vessel working and its very annoying when trying to sleep! - wasn't that loud until then so not sure why it is loud all of a sudden)
It's been installed since end of December now and i'm struggling with it not heating up last two rads on the system (which are downstairs in the living/dining room). They have added a second pump onto the return side of the system and that seemed to help for a few hours when first installed but now not coming back on again. if i turn the TRV off on others earlier in the system off the last two do get warm but even then not hot)
so the system is taking a lot of kWh to run to get the living room up to temp and then the temp is dropping quickly once it reaches 18 degrees as not enough ambient heat from the working radiators on the system.
i have had to take to turning thermostat down as couldn't afford the £15 per day electricity bill it was generating.
We had solar installed at the time too (16 x 405w panels) and even that isn't working right at just 1-1.8kwh per day generation at the moment which seems extremely poor for this size of system that works on PV and min 7 hours daylight at the moment.
All in all feel at my wits end with it all
Did they repressurise after the settling in period? My Vaillant shut itself off when it detected the low pressure. Our installer warned us that this was going to happen and was on the scene as soon as it did.
@lfranklin. I've a similar system to you, 2 x 12kW Samsungs controlled by Hive and 5.6kW PV array, south facing.
The trouble with PV and ASHPs is the yield from the first is tiny just at the time the demand from second is greatest. These last couple of months have been similarly challenging for me, with a PV average for Jan 2kWh/day and December 1.5kWh/day although come the summer I'm expecting 10x these. I reckon yield and demand will be much closer matched in Spring/Autumn and then around 4 months of free power in summer. You should see similar so don't despair juat yet.
It sounds like your radiators aren't balanced. I had a load of air in mine for weeks after the ASHP commissioning so if you're not regularly bleeding them I'd start there. Make sure you keep repressurising or you'll find water not reaching all the extremities as well! Also worth checking how your system is controlled - is it in 'weather compensation' mode (the controller will say 'Water Law' if it is) and what the temperature settings are - the manual should tell you how to do this but if not please repost. Your radiators won't feel hot like with a gas boiler but should feel warm and - in weather compensation mode - should get warmer as it gets colder outside.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
@dunlorn can I ask how many KWH you're using roughly per day for each 12kw system?
What system are you using for monitoring.. I have shinephone app.
I've found my graph shows massive spikes of power regularly through day and thermostat only set to 17° 😭
Consumption is very much dependant on external temperature. In the recent freezing spells in December and early Jan (we're in Scottish Highlands) our system had a few days with a truly eye-watering 120-130kWh! A more typically cold day, say 1-3°C, will use around 60-70kWh and if it gets to a balmy 5 or 6° or more we'll see 50kWh or lower. In October/early Nov we were using 20-30kWh. I generally only use a single unit as not at all convinced that the second has any value other than increasing bills - it's something I've asked the installer to look at.
The consumption range has come as something of a surprise but, if you consider a single ASHP drawing around 5kW at low temperatures and on for 15-20hrs per day, then you can soon get to these numbers. At milder ambient temperature the unit may only draw 3kW, and be on for less of the day, so you can see the difference. Part of the reason for the drop in efficiency when you get near to freezing is the regular defrost cycles. Mine were happening around every 45 mins at peak and - whilst they need to happen - they do end up drawing heat from your system and can mean you never get up to set point water temperature.
I don't think your spikes are defrosts, more like on/off cycling. The Hive only has to drop 0.1°C from its target to start the heat pump. This isn't ideal. A lower water temperature may help but this is a matter for experimentation. I also tried moving my thermostat to different locations as I found some were very prone to generating on/off cycles.
I've deliberately not changed my installers settings for weather compensation (yet) but I think these are too high, 50°C at 2° ambient and 42°C at 15° ambient. Notwithstanding that, I've never seen my unit discharge water at more than 44°, even when freezing outside, so we never get near the set point!
There's no monitoring btw, just me popping my head in a few times a day and making a note. I certainly don't want to be doing this for the rest of my days!
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
Posted by: @dunlornConsumption is very much dependant on external temperature. In the recent freezing spells in December and early Jan (we're in Scottish Highlands) our system had a few days with a truly eye-watering 120-130kWh! A more typically cold day, say 1-3°C, will use around 60-70kWh and if it gets to a balmy 5 or 6° or more we'll see 50kWh or lower. In October/early Nov we were using 20-30kWh. I generally only use a single unit as not at all convinced that the second has any value other than increasing bills - it's something I've asked the installer to look at.
The consumption range has come as something of a surprise but, if you consider a single ASHP drawing around 5kW at low temperatures and on for 15-20hrs per day, then you can soon get to these numbers. At milder ambient temperature the unit may only draw 3kW, and be on for less of the day, so you can see the difference. Part of the reason for the drop in efficiency when you get near to freezing is the regular defrost cycles. Mine were happening around every 45 mins at peak and - whilst they need to happen - they do end up drawing heat from your system and can mean you never get up to set point water temperature.
I don't think your spikes are defrosts, more like on/off cycling. The Hive only has to drop 0.1°C from its target to start the heat pump. This isn't ideal. A lower water temperature may help but this is a matter for experimentation. I also tried moving my thermostat to different locations as I found some were very prone to generating on/off cycles.
I've deliberately not changed my installers settings for weather compensation (yet) but I think these are too high, 50°C at 2° ambient and 42°C at 15° ambient. Notwithstanding that, I've never seen my unit discharge water at more than 44°, even when freezing outside, so we never get near the set point!
There's no monitoring btw, just me popping my head in a few times a day and making a note. I certainly don't want to be doing this for the rest of my days!
I would suggest that you consider adjusting your weather compensation settings and then set your hive to 1C or 2C above the desired temperature. Doing so should hopefully reduce your consumption.
@derek-m thanks what setting would that be please ..in 201* &
202*
And what settings would you suggest I enter at first?
I work from home full time so tend to have at around 17-18° max through day and maybe 19-20° on an evening (well in a perfect world where its working ok)
@derek-m Thanks, I'll give that a go.
The installer (along with an engineer from Joules) has promised me a visit on 23rd Feb and I've a loooong list of questions. Most pressing is what controls the second (slave) unit, why it sends out water around 6° cooler than the master (when set-up appears identical) and why it makes no difference to comfort levels. Also, we've now had two days where for some reason LWT is stuck around 30°, and the system on constantly as it never reaches our 18 ° internal target. The list is getting longer.
2 x 12kW Samsung Gen6 ASHP, 5.6kW solar PV ground mounted c/w 10kWh Puredrive battery & Solis inverter.
Posted by: @lfranklin@derek-m thanks what setting would that be please ..in 201* &
202*
And what settings would you suggest I enter at first?
I work from home full time so tend to have at around 17-18° max through day and maybe 19-20° on an evening (well in a perfect world where its working ok)
I'm afraid that I have to go mow the grass (she who must be obeyed has spoken), so I will formulate a reply shortly.
Posted by: @lfranklin@derek-m thanks what setting would that be please ..in 201* &
202*
And what settings would you suggest I enter at first?
I work from home full time so tend to have at around 17-18° max through day and maybe 19-20° on an evening (well in a perfect world where its working ok)
Now that I am back with the 'living', so that there is no confusion, could you clarify what is meant by 201 & 202 and to which manual you refer. I don't have a Samsung heat pump to play with and have downloaded a number of Samsung manuals.
Using the reference number and the text description would probably be best.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 61 Online
- 2,276 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 13 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 40 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 2 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 3 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 22 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago