Help me optimise my ASHP Pipework
I've got a Nibe F2040 ASHP which has been installed for over a year now.
Whilst trying to optimise the system I've wondered if the buffer is causing me issues.
See attached drawing of my system. I have noticed that the pipework at point '1' is cooler than at point '2' and '3'.
The PWM motor is controlled by the Heat Pump to maintain a deltaT and the other 2 pumps are fixed speed (currently setting 2).
Does anyone have any suggestions on how I can better match the circulation pumps to the HP, or how I can prevent the mixing in the buffer.
I'm tempted to ask my installer to add a couple of valves to the top and bottom of the buffer so I can try isolating this completely?
I would suggest that you check your schematic, since it appears to make little sense. A buffer tank would normally have at least 4 connections, 2 in and 2 out. I also don't understand why pipe '1' would be cooler than pipes '2' and '3', if the direction of flow is as shown.
There is often an arrow on the pump body to indicate the direction of flow.
The schematic is correct as drawn and the buffer is Tee'd off the pipework that then goes towards the other 2 pumps.
Apologies pipe '1' was meant to say warmer not cooler.
What is the temperature difference?
Looking at the schematic, I suspect that the combined flow rate through the two pumps on pipes '2' and '3' is greater than the pump on pipe '1'. This will probably have the effect of drawing the cooler water in the return pipe, through the buffer tank, and hence causing it to mix and cool the water from the heat pump. Try reducing the speed of the pumps on pipes '2' and '3' to see if this increases the temperature in the aforementioned pipes.
@luke remove the buffer and it will work properly. The schematic is not a Nibe 2040 configuration. There is no need for the buffer. If you have a blending valve and pump on your under floor manifold, this should be removed and, firstly, I would try to run the system on a single temperature with the internal sensor to control the house temperature, if that does not have adequate control, then set up 2 separate zones through the controller.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @derek-mWhat is the temperature difference?
Looking at the schematic, I suspect that the combined flow rate through the two pumps on pipes '2' and '3' is greater than the pump on pipe '1'. This will probably have the effect of drawing the cooler water in the return pipe, through the buffer tank, and hence causing it to mix and cool the water from the heat pump. Try reducing the speed of the pumps on pipes '2' and '3' to see if this increases the temperature in the aforementioned pipes.
I have slowed the pumps down to speed 1 and will report back. I'm not sure of the temperature difference, but it was noticeable by hand. I have access to a thermal camera so I'll get hold of this.
Posted by: @heacol@luke remove the buffer and it will work properly. The schematic is not a Nibe 2040 configuration. There is no need for the buffer. If you have a blending valve and pump on your under floor manifold, this should be removed and, firstly, I would try to run the system on a single temperature with the internal sensor to control the house temperature, if that does not have adequate control, then set up 2 separate zones through the controller.
I agree that ultimately I want the buffer removed or at least put in series as I don't think it has any benefit and we should have sufficient volume in the circuits.
There is no blending valve on the UFH manifold and I run the whole system in WC using the internal sensor to 'adapt' the curve. All TRVS open and heating circulation pump thermostat set as a max stop limit only.
Looking at the below schematic, my system is I believe a similar setup to this, excluding CP6 and EB1 and any associated valves / pipework. CP5 is shown as the buffer vessel (which in my case is a Nibe UKV 20-40)
When looking at that installation manual for the UKV it doesn't actually show my configuration with the buffer, which I would say is different to the SMO20 installer manual screenshot?
Here are a couple of pictures of my setup before it was finished and insulated.
@luke Your valve is fine, remove the items circled and you will have very good performance. You have plenty of system volume for the heat pump.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@heacol thanks for this. I will take these comments back to my installer.
May I ask why you would remove the TF1 filter for a strainer? Is this just to improve flow? Will there be other detrimental effects?
Also I presume you are saying that the system will run from just the charge pump as you are suggesting removal of both heating medium circulation pumps. (I like this idea as it will reduce base load, but I expect my installer will be hesitant to recommend this considering he installed both!)
@luke TF1 filter for a strainer? Is this just to improve flow? Will there be other detrimental effects? just to improve flow and stop parasitic losses. It will have no detrimental effect. It can be put back in parallel with the strainer if you are worried.
The installer will probably balk at removing them, but you are the customer.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
- 22 Forums
- 2,025 Topics
- 44.1 K Posts
- 25 Online
- 3,226 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Replacing Worcester oil boiler with an ASHP
Is this something you are thinking of doing? Or have th...
By Cliff-Arnold , 6 minutes ago
-
RE: Say hello and introduce yourself
Hi Mars Thanks for inviting me to join the forum, I h...
By Cliff-Arnold , 15 minutes ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
The trouble is that I do not know enough about how heat...
By trebor12345 , 2 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
I have three CT monitors on my solar output via the mi...
By IanMK13 , 3 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
Agree with the above. Without knowing what the modulati...
By Old_Scientist , 4 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@agentgeorge Not with Eon Next. The only reson I left O...
By Andris , 6 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I apologise if this has been covered already but have y...
By JamesPa , 6 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
The difficulty with this discussion is that it's referr...
By Transparent , 7 hours ago
-
@rhh2348 it’s clear you are wanting to run your heat pu...
By SUNandAIR , 7 hours ago
-
Is this normal? Click of the DHW returning to space heating
This has been bugging me for a while and I just wanted ...
By Grantmethestrength , 1 day ago
-
@sandman1600 you need to measure whats going on real...
By davidnolan22 , 2 days ago
-
@brandon-r is this a project that you could assist with...
By Mars , 2 days ago
-
Has anyone installed these on their ASHP fed radiator s...
By Grantmethestrength , 3 days ago
-
Just an update on the responses received by Smart Heati...
By Eliuccio , 3 days ago
-
RE: Is your gut better than Math
By SUNandAIR , 3 days ago
-
RE: Would You Find Value in a Premium Installer-Supported Forum?
We are very pleased to announce that Brendon Uys (@heac...
By Mars , 3 days ago
-
RE: Ecodan 11.2kw Wireless thermostat drop outs
@skyecraig I've had our FTC7 wireless thermostat lose...
By RobS , 4 days ago
-
RE: Signenergy AI Mode - How long does it take to learn a usage pattern?
I am definitely interested in this as I am considering ...
By Grantmethestrength , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Hitachi Yutaki SCombi Heat Pump(Indoor Unit ) RWD-3.0RW...
By trebor12345 , 4 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
ми не граємо в карти
By Transparent , 4 days ago
Most Active This Week
# | Name | kWhs |
---|---|---|
1 | JamesPa | 317 |
2 | Mars | 295 |
3 | AdamK | 139 |
4 | trebor12345 | 136 |
5 | Heatgeek | 136 |
6 | SUNandAIR | 135 |
7 | Gary | 131 |
8 | Toodles | 123 |
9 | RobS | 103 |
10 | bontwoody | 103 |