Help me optimise my ASHP Pipework
I've got a Nibe F2040 ASHP which has been installed for over a year now.
Whilst trying to optimise the system I've wondered if the buffer is causing me issues.
See attached drawing of my system. I have noticed that the pipework at point '1' is cooler than at point '2' and '3'.
The PWM motor is controlled by the Heat Pump to maintain a deltaT and the other 2 pumps are fixed speed (currently setting 2).
Does anyone have any suggestions on how I can better match the circulation pumps to the HP, or how I can prevent the mixing in the buffer.
I'm tempted to ask my installer to add a couple of valves to the top and bottom of the buffer so I can try isolating this completely?
I would suggest that you check your schematic, since it appears to make little sense. A buffer tank would normally have at least 4 connections, 2 in and 2 out. I also don't understand why pipe '1' would be cooler than pipes '2' and '3', if the direction of flow is as shown.
There is often an arrow on the pump body to indicate the direction of flow.
The schematic is correct as drawn and the buffer is Tee'd off the pipework that then goes towards the other 2 pumps.
Apologies pipe '1' was meant to say warmer not cooler.
What is the temperature difference?
Looking at the schematic, I suspect that the combined flow rate through the two pumps on pipes '2' and '3' is greater than the pump on pipe '1'. This will probably have the effect of drawing the cooler water in the return pipe, through the buffer tank, and hence causing it to mix and cool the water from the heat pump. Try reducing the speed of the pumps on pipes '2' and '3' to see if this increases the temperature in the aforementioned pipes.
@luke remove the buffer and it will work properly. The schematic is not a Nibe 2040 configuration. There is no need for the buffer. If you have a blending valve and pump on your under floor manifold, this should be removed and, firstly, I would try to run the system on a single temperature with the internal sensor to control the house temperature, if that does not have adequate control, then set up 2 separate zones through the controller.
Posted by: @derek-mWhat is the temperature difference?
Looking at the schematic, I suspect that the combined flow rate through the two pumps on pipes '2' and '3' is greater than the pump on pipe '1'. This will probably have the effect of drawing the cooler water in the return pipe, through the buffer tank, and hence causing it to mix and cool the water from the heat pump. Try reducing the speed of the pumps on pipes '2' and '3' to see if this increases the temperature in the aforementioned pipes.
I have slowed the pumps down to speed 1 and will report back. I'm not sure of the temperature difference, but it was noticeable by hand. I have access to a thermal camera so I'll get hold of this.
Posted by: @heacol@luke remove the buffer and it will work properly. The schematic is not a Nibe 2040 configuration. There is no need for the buffer. If you have a blending valve and pump on your under floor manifold, this should be removed and, firstly, I would try to run the system on a single temperature with the internal sensor to control the house temperature, if that does not have adequate control, then set up 2 separate zones through the controller.
I agree that ultimately I want the buffer removed or at least put in series as I don't think it has any benefit and we should have sufficient volume in the circuits.
There is no blending valve on the UFH manifold and I run the whole system in WC using the internal sensor to 'adapt' the curve. All TRVS open and heating circulation pump thermostat set as a max stop limit only.
Looking at the below schematic, my system is I believe a similar setup to this, excluding CP6 and EB1 and any associated valves / pipework. CP5 is shown as the buffer vessel (which in my case is a Nibe UKV 20-40)
When looking at that installation manual for the UKV it doesn't actually show my configuration with the buffer, which I would say is different to the SMO20 installer manual screenshot?
Here are a couple of pictures of my setup before it was finished and insulated.
@luke Your valve is fine, remove the items circled and you will have very good performance. You have plenty of system volume for the heat pump.
@heacol thanks for this. I will take these comments back to my installer.
May I ask why you would remove the TF1 filter for a strainer? Is this just to improve flow? Will there be other detrimental effects?
Also I presume you are saying that the system will run from just the charge pump as you are suggesting removal of both heating medium circulation pumps. (I like this idea as it will reduce base load, but I expect my installer will be hesitant to recommend this considering he installed both!)
@luke TF1 filter for a strainer? Is this just to improve flow? Will there be other detrimental effects? just to improve flow and stop parasitic losses. It will have no detrimental effect. It can be put back in parallel with the strainer if you are worried.
The installer will probably balk at removing them, but you are the customer.
- 26 Forums
- 2,418 Topics
- 54.8 K Posts
- 322 Online
- 6,098 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
The issue of earth bonds to pipework doesn't yet seem t...
By Transparent , 3 minutes ago
-
RE: Is my Samsung gen6 outside air temp sensor missing a sheath/sleeve?
Mystery solved courtesy of @aventus-eco (thanks Sean) w...
By Mars , 13 minutes ago
-
RE: Daikin Wireless Thermostat
@toodles Yes, it's the Daikin hardwired room stat th...
By Bash , 16 minutes ago
-
Just a brief update to keep things transparent. Secti...
By DREI , 32 minutes ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
Sorry forgot about the three choices. It’s the 2nd one ...
By Davesoa , 1 hour ago
-
RE: Reliable, easy to use home battery options
@batpred We are also in the SE., I would say that 30 - ...
By Toodles , 2 hours ago
-
I continue to receive emails from homeowners sharing he...
By Mars , 2 hours ago
-
RE: Water outage in the the south-east
We think alike @editor ! All those bottles (and I expec...
By Toodles , 2 hours ago
-
Perhaps I am just a fuss pot - but I am curious too!
With all the talk in the past about reducing ‘distortio...
By Toodles , 3 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Thats great thanks. TBH setting the low end o...
By JamesPa , 4 hours ago
-
RE: Say hello and introduce yourself
@mrfield, welcome to the forums. Please go here and ...
By Mars , 4 hours ago
-
RE: Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
@ashp-bobba Thanks for the reply. Would it not work ...
By Patch321 , 5 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
I did not hear back from the tech team. (Assume they ar...
By swwils , 6 hours ago
-
RE: How to use my Hanchu battery storage for home without it feeding back into the grid?
Hi. My Hanchu battery system is controlled by the (Lux...
By SKD , 8 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In the Home Assistant firmware the data points...
By F1p , 19 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@johnbroome if it is not the pressure in the expansion ...
By ASHP-BOBBA , 19 hours ago
-
So I hear the export MPAN that UKPN assigned should be ...
By Batpred , 22 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@toodles Thank you for your input. As the days have got...
By Synthbuilder , 1 day ago
-
RE: Fan unit Making terrible noise HELP!!
@gutoffowc Oh no, sorry to hear that, are you in the Ke...
By ASHP-BOBBA , 1 day ago