Heatmeiser smart controls with ashp
Yes, the unit shows the ASHP and zones come on when thermostat temps are raised - I’ve checked them all. Lights come on the unit, the valve on the appropriate zone lifts 2-3mm and the red in the tube indicator drops. (Only exception is the spare bedroom where all indicators work except the red in the tube which only partially moves.)
Posted by: @emmajgYes, the unit shows the ASHP and zones come on when thermostat temps are raised - I’ve checked them all. Lights come on the unit, the valve on the appropriate zone lifts 2-3mm and the red in the tube indicator drops. (Only exception is the spare bedroom where all indicators work except the red in the tube which only partially moves.)
That's fine, the red indicator shows the water flow rate, which should have been balanced the the heat demand of each particular room.
With reference to your original post. Probably the most efficient way to operate your heat pump would be to have all the heatmiser thermostats set to 1C above the desired level, with the Vaillant controller using the WC curve to adjust the Leaving Water Temperature (LWT), to help maintain the desired Indoor Air Temperature (IAT) under varying Outside Air Temperatures (OAT). The flow rate through the UFH loops should then be adjusted to achieve the desired room temperatures.
If a particular room gets too warm then the relevant solenoid valve should close to bring the temperature back down.
When all the thermostats are set low, does the heat pump stop, though the water pump may run on for several minutes.
Posted by: @emmajgHelpful video! It’ set at 0.45
Okay, if your home is getting too warm then you could try selecting a lower curve.
If you make an adjustment remember that the system will take quite some time to stabilse, so don't expect an immediate drop in temperature, unless you open all the doors and windows. 😋
@derek-m This has been enormously helpful. I have one last question. How does the desired temp set on the vaillant controller relate to those I set in the individual room thermostats? (Which one wins?)
Please forgive me jumping in. We have a Vaillant ASHP and have the same room controllers as you, ours are wired though. Who wins depends on the settings. We tried both ways and have now got it set so the Vaillant controller is the only heat reference. The neostat V2 no longer control the rooms. The valves are disconnected, and the stats just indicate the temp in each room. This has done wonders for our COP.
Drew
Posted by: @emmajg@derek-m This has been enormously helpful. I have one last question. How does the desired temp set on the vaillant controller relate to those I set in the individual room thermostats? (Which one wins?)
The Vaillant controller actually controls the heat pump, the heatmiser thermostats just open the solenoid valves and start and stop the heat pump, assuming it has been connected correctly.
Posted by: @drew-paPlease forgive me jumping in. We have a Vaillant ASHP and have the same room controllers as you, ours are wired though. Who wins depends on the settings. We tried both ways and have now got it set so the Vaillant controller is the only heat reference. The neostat V2 no longer control the rooms. The valves are disconnected, and the stats just indicate the temp in each room. This has done wonders for our COP.
Drew
By all means jump in Drew, particularly since you have a similar system and possibly the same problems.
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 85 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Plug and play solar. Thoughts?
Actually I'm going to jump but in the same direction as...
By Majordennisbloodnok , 5 minutes ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 1 hour ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Well at least that solves the mystery of where the exce...
By JamesPa , 3 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 3 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 19 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 1 day ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 1 day ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 2 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 2 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 3 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 3 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 4 days ago