Heat pump install overloads home fuse - 80A limitations
I've had the DNO application back and they've passed it.
Taking out the 40A electric shower made it ok.
When I say take out, I just mean out the equation not physically off the wall, not yet anyway till heat pump is so up and running then I won't need it anyway so it'll be removed permanently .They just want it down on paper.
Still got solar, induction hob, double oven microwave and soon to be installed heat pump so it'll still be way up there.
But chatting to electrician says 80A will easily take 100A for a few hours anyway.
@njtt Great news that you've had it back approved. I found the DNO (NG in my case) were more than reasonable and very helpful.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Yes NG for me too.
They even rang me up 2 days after application was sent in to say
"I thought you like to know it was accepted"
That's 2 dealings I've had on the phone with NG with upgrade to fuse and the heat pump and both very pleasant and quickly sorted.
Posted by: @njtAn 100A fuse would have made my life much easier.
I just applied to the DNO for a fuse upgrade as octopus after their heat pump survey said I needed one.
Getting in contact with the DNO was easy and fuse upgraded within days for free but stated their policy will only allow up to 80A fuse.
As I've already mentioned they removed neighbours 100A fuse and replaced it with an 80A
I've just addressed this issue here in the topic DIY solar upgrade.
I've spoken with the senior NGED engineer who issues their operational specifications and represents their interest at the Electricity Networks Association.
He's friendly, helpful... and deeply knowledgeable.
When he says they need to downgrade to 80A Service Fuses, then he won't have done that lightly.
As others here have pointed out, a Service Fuse is a very long time-delay device!
You can draw 100A through it for maybe an hour before it gives out.
A high proportion of homes which need to draw more than 80A (19kW) have inefficiencies within them which really ought to be addressed!
Yes, an electric shower is a very high demand appliance... more so than an EV charger.
And there's a lot of them in houses which have had additional loft insulation installed by morons on top of the electrical supply cable!
Let's hope that the need to downgrade to an 80A Service Fuse will cause more home-owners to re-evaluate their 10kW electric shower !
Let me end with a photograph showing 'loft flooring' which has been done properly:
A shows the original ceiling joists.
The span length is 4.6m, so these old 3-inch deep timbers aren't capable of taking the new floor.
B are the new floor joists which have been placed alongside the ceiling joists.
That leaves plenty of space below the new chipboard floor (C) for insulation,
and the re-routing of power cables (2.5mm² and larger) above the insulation layer.
Save energy... recycle electrons!
@transparent A concern of mine regarding the ability of an 80A fuse to carry in excess of 100A for a significant time is that if this is done regularly the fuse could deteriorate over a period of time and eventually fail (you might say this wouldn't be a bad thing).
- 22 Forums
- 2,096 Topics
- 46.2 K Posts
- 103 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 I asked Wattson: What is ‘intell...
By Toodles , 19 minutes ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 4 hours ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 6 hours ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 1 day ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 1 day ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 2 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 2 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
Can we have some links to those you're considering plea...
By Transparent , 2 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 3 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 4 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 4 days ago
-
RE: When will heat pumps and install prices come down?
... which of course is impossible because the world mov...
By JamesPa , 4 days ago