Note: The following procedures will only work if you have the samsung controller configured as the thermostat, it does not apply to third party thermostat control.
I have recently been modifying my controller configuration for my bivalent heat pump / oil boiler system due to clashes between how the oil boiler and heat pump need to be controlled. It became apparent to me that having a single thermostat (Honeywell Home Smart Thermostat) to control both systems was not going to work long term and as I have now found a suitable cabling route (not realised during installation in 2023) in the house, I moved the Samsung controller from my external boiler room into the house.
Once I had completed the electrical work, I reconfigured the Samsung controller to become a room thermostat and enabled it to use its internal abilities to decide its own weather curve (flow temperatures) required to achieve the room target temperature versus outside temperature.
The other advantage of configuring the controller to be a room thermostat was it enabled me to take advantage of the additional Weekly and Yearly schedules alongside the Daily schedules. As there is little in the way of information on this topic (a couple of short YouTube videos) I thought I would share my setup experience in case it is useful for anyone else.
The yearly schedules I was aiming to configure are as follows:
Summer:
Active: June, July and August
CH state:
Off
Autumn:
Active: September and October
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Winter:
Active: November, December, January, February and March
CH state:
03:00hrs to 21:00hrs room temperature +21C
21:00hrs to 03:00hrs room temperature +19C
Spring:
Active: April and May
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Creating Groups:
The above season groups need to be created first by
1. Selecting the cog button
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok"
4. Select "Yearly Schedule" press "Ok"
5. Select "Add Group" press "Ok"
At this point you can select one of the following groups (Group 1, Group 2, Rainy, Dry, Spring, Summer, Autumn or Winter.
6. Select the appropriate group and press "Ok"
7. Switch on the months of the year this group will be active by using the navigation arrows to select the month and toggle the selected month "On" or "Off"
8. Press "Ok" when all months have been set for the group.
Creating Schedules:
At this stage you can now add individual schedules to the season groups. These steps are for configuring the above Winter group as an example but are the same steps for all other groups.
1. Press the cog button on the controller
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok".
4. At this step, highlight the "Winter" season group and press the on screen "Select" button by highlighting it and pressing "Ok" on the controller interface.
5. Set individual days of the week the schedule will run by toggling each day "On" or "Off" using the conroller navigation buttons, then press "Ok" when finished
6. Set the time of day to "03:00" for the schedule to become active and press "Ok"
7. Select "On" and "Zone" (if more than one zone available select the required zone) press "Ok"
8. Set "Heat" and set the room temperature to "21C" (or flow temperature if system is configured to use flow temp) press "Ok"
To add the set back simply repeat the above steps but set the time in step 6 to "19:00" and set the room temperature (or flow temp) in step 8 to "19C"
All the schedules associated with the Spring, Autumn and Winter groups should be in the "On" state so the heat pump will be active throughout the heating season. In the case of the Summer season, we want the heating to be off so step 7 in "Creating Schedules" in this case would be "Off" for the zone selected at the time set in step 6.
The "Off" will then become active and re-trigger every 24 hours to ensure the heating system remains off.
Hope the above is useful and if anyone finds errors in the above procedural steps please let me know
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
- 26 Forums
- 2,114 Topics
- 46.4 K Posts
- 287 Online
- 3,410 Members
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist Cosy is a really good tariff for heat pu...
By ChandyKris , 13 hours ago
-
RE: Wood burner with ASHP - direct air?
This depends on the size of your wood burner and size/t...
By Lucia , 15 hours ago
-
RE: Difficult positioning of air source heat pump
@rikiarn It's a not a buffer it's a volumiser which is ...
By Lucia , 15 hours ago
-
RE: Is your heat pump insured?
To make things clear, lots of insurance companies cover...
By Lucia , 15 hours ago
-
RE: Boxt Heat Pump Installation Experience
@adrian any updates since installation? How is it perfo...
By Ashfp , 20 hours ago
-
Benefits of an extra horizontal loop for GSHP
Hello everyone, We're in the process of installin...
By thewiseoldbird , 2 days ago
-
RE: Say hello and introduce yourself
Hi @seatonian - Yes, I know Seaton, and I have the Nat...
By Transparent , 2 days ago
-
RE: Buffers, hot water and cooling
The principal reason that heat pumps have minimum flow ...
By JamesPa , 2 days ago
-
@seatonian got your email. Will connect you with a reco...
By Mars , 2 days ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 4 days ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 5 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 5 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 5 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 5 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 7 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 7 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 1 week ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 1 week ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 1 week ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 1 week ago