Fun with Samsung Gen 6 Yearly Schedules
Note: The following procedures will only work if you have the samsung controller configured as the thermostat, it does not apply to third party thermostat control.
I have recently been modifying my controller configuration for my bivalent heat pump / oil boiler system due to clashes between how the oil boiler and heat pump need to be controlled. It became apparent to me that having a single thermostat (Honeywell Home Smart Thermostat) to control both systems was not going to work long term and as I have now found a suitable cabling route (not realised during installation in 2023) in the house, I moved the Samsung controller from my external boiler room into the house.
Once I had completed the electrical work, I reconfigured the Samsung controller to become a room thermostat and enabled it to use its internal abilities to decide its own weather curve (flow temperatures) required to achieve the room target temperature versus outside temperature.
The other advantage of configuring the controller to be a room thermostat was it enabled me to take advantage of the additional Weekly and Yearly schedules alongside the Daily schedules. As there is little in the way of information on this topic (a couple of short YouTube videos) I thought I would share my setup experience in case it is useful for anyone else.
The yearly schedules I was aiming to configure are as follows:
Summer:
Active: June, July and August
CH state:
Off
Autumn:
Active: September and October
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Winter:
Active: November, December, January, February and March
CH state:
03:00hrs to 21:00hrs room temperature +21C
21:00hrs to 03:00hrs room temperature +19C
Spring:
Active: April and May
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Creating Groups:
The above season groups need to be created first by
1. Selecting the cog button
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok"
4. Select "Yearly Schedule" press "Ok"
5. Select "Add Group" press "Ok"
At this point you can select one of the following groups (Group 1, Group 2, Rainy, Dry, Spring, Summer, Autumn or Winter.
6. Select the appropriate group and press "Ok"
7. Switch on the months of the year this group will be active by using the navigation arrows to select the month and toggle the selected month "On" or "Off"
8. Press "Ok" when all months have been set for the group.
Creating Schedules:
At this stage you can now add individual schedules to the season groups. These steps are for configuring the above Winter group as an example but are the same steps for all other groups.
1. Press the cog button on the controller
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok".
4. At this step, highlight the "Winter" season group and press the on screen "Select" button by highlighting it and pressing "Ok" on the controller interface.
5. Set individual days of the week the schedule will run by toggling each day "On" or "Off" using the conroller navigation buttons, then press "Ok" when finished
6. Set the time of day to "03:00" for the schedule to become active and press "Ok"
7. Select "On" and "Zone" (if more than one zone available select the required zone) press "Ok"
8. Set "Heat" and set the room temperature to "21C" (or flow temperature if system is configured to use flow temp) press "Ok"
To add the set back simply repeat the above steps but set the time in step 6 to "19:00" and set the room temperature (or flow temp) in step 8 to "19C"
All the schedules associated with the Spring, Autumn and Winter groups should be in the "On" state so the heat pump will be active throughout the heating season. In the case of the Summer season, we want the heating to be off so step 7 in "Creating Schedules" in this case would be "Off" for the zone selected at the time set in step 6.
The "Off" will then become active and re-trigger every 24 hours to ensure the heating system remains off.
Hope the above is useful and if anyone finds errors in the above procedural steps please let me know
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 499 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: PV Panels on roof in Conservation Area
@majordennisbloodnok Fnaargh, I was thinking about try...
By colinc , 11 minutes ago
-
RE: Electricity price predictions
@jamespa Ah, you mean MPs that have not pro...
By Batpred , 1 hour ago
-
-
RE: Buying large amp bidirectional RCD and RCBO
Exactly @transparent , this type of RCBOs are not easil...
By Batpred , 1 hour ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - though I realise I am a Canute, I have an...
By cathodeRay , 1 hour ago
-
RE: Mitsubishi Ecodan R290 10kW performance
I don't have any obvious issues with the MELCloud data ...
By Sheriff Fatman , 2 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@jamespa Yup! 😉 Toodles.
By Toodles , 4 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And just when I think great they’re coming next week to...
By Crimson , 4 hours ago
-
RE: Very Much Awake – Renewing the Heating Industry One Step at a Time
I feel that that attitude shared by Aadil from Heat Gee...
By Toodles , 5 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
I have recently gone through the whole process. I got q...
By debT , 7 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
and we have some of the strongest tidal flows anywhere ...
By Old_Scientist , 7 hours ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
This looks OK. Overall you have roughly the right amoun...
By Old_Scientist , 8 hours ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
I'm not familiar with Hive thermostats/controllers, but...
By Old_Scientist , 8 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Thanks @grantmethestrength and @cathoderay . The reas...
By benson , 22 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa mine seems changing albeit not by much, 3.21, ...
By AdamK , 1 day ago
-
@majordennisbloodnok The migration hasn't started in th...
By HCas , 1 day ago
-
RE: One room is colder than the rest of the house
@jamespa thanks for all the advice. Just so you know, ...
By AndrewJ , 1 day ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
My MMI is in the loft but I checked the pump flow rate ...
By RadWhisperer , 1 day ago
-
RE: Grant Aerona 3 and Drayton system questions
Good man/woman that plumber! Very likely....
By JamesPa , 1 day ago