Fun with Samsung Gen 6 Yearly Schedules
Note: The following procedures will only work if you have the samsung controller configured as the thermostat, it does not apply to third party thermostat control.
I have recently been modifying my controller configuration for my bivalent heat pump / oil boiler system due to clashes between how the oil boiler and heat pump need to be controlled. It became apparent to me that having a single thermostat (Honeywell Home Smart Thermostat) to control both systems was not going to work long term and as I have now found a suitable cabling route (not realised during installation in 2023) in the house, I moved the Samsung controller from my external boiler room into the house.
Once I had completed the electrical work, I reconfigured the Samsung controller to become a room thermostat and enabled it to use its internal abilities to decide its own weather curve (flow temperatures) required to achieve the room target temperature versus outside temperature.
The other advantage of configuring the controller to be a room thermostat was it enabled me to take advantage of the additional Weekly and Yearly schedules alongside the Daily schedules. As there is little in the way of information on this topic (a couple of short YouTube videos) I thought I would share my setup experience in case it is useful for anyone else.
The yearly schedules I was aiming to configure are as follows:
Summer:
Active: June, July and August
CH state:
Off
Autumn:
Active: September and October
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Winter:
Active: November, December, January, February and March
CH state:
03:00hrs to 21:00hrs room temperature +21C
21:00hrs to 03:00hrs room temperature +19C
Spring:
Active: April and May
CH state:
05:00hrs to 19:00hrs room temperature +20C
19:00hrs to 05:00hrs room temperature +18C (setback)
Creating Groups:
The above season groups need to be created first by
1. Selecting the cog button
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok"
4. Select "Yearly Schedule" press "Ok"
5. Select "Add Group" press "Ok"
At this point you can select one of the following groups (Group 1, Group 2, Rainy, Dry, Spring, Summer, Autumn or Winter.
6. Select the appropriate group and press "Ok"
7. Switch on the months of the year this group will be active by using the navigation arrows to select the month and toggle the selected month "On" or "Off"
8. Press "Ok" when all months have been set for the group.
Creating Schedules:
At this stage you can now add individual schedules to the season groups. These steps are for configuring the above Winter group as an example but are the same steps for all other groups.
1. Press the cog button on the controller
2. Select schedules and press "Ok"
3. Select "Add Schedule" press "Ok".
4. At this step, highlight the "Winter" season group and press the on screen "Select" button by highlighting it and pressing "Ok" on the controller interface.
5. Set individual days of the week the schedule will run by toggling each day "On" or "Off" using the conroller navigation buttons, then press "Ok" when finished
6. Set the time of day to "03:00" for the schedule to become active and press "Ok"
7. Select "On" and "Zone" (if more than one zone available select the required zone) press "Ok"
8. Set "Heat" and set the room temperature to "21C" (or flow temperature if system is configured to use flow temp) press "Ok"
To add the set back simply repeat the above steps but set the time in step 6 to "19:00" and set the room temperature (or flow temp) in step 8 to "19C"
All the schedules associated with the Spring, Autumn and Winter groups should be in the "On" state so the heat pump will be active throughout the heating season. In the case of the Summer season, we want the heating to be off so step 7 in "Creating Schedules" in this case would be "Off" for the zone selected at the time set in step 6.
The "Off" will then become active and re-trigger every 24 hours to ensure the heating system remains off.
Hope the above is useful and if anyone finds errors in the above procedural steps please let me know
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss, deltaT = 8 degrees
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
4.1Kw Solar Panel Array
34Kwh GivEnergy Stackable Battery System
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 373 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Weather compensation- why you should use it
@batpred Yes, a heat battery (such as the one I use for...
By Toodles , 4 minutes ago
-
RE: Setback savings - fact or fiction?
By 'no recovery penalty' I mean no efficiency penalty b...
By JamesPa , 5 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Only the manual The commissioning documents state which...
By JamesPa , 33 minutes ago
-
RE: Electricity price predictions
As electricity prices continue to rise and specialist h...
By Mars , 57 minutes ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
Your installer is probably right. The L9 error means l...
By JamesPa , 1 hour ago
-
RE: New Fogstar 15.5kWh upright solution
Thank you. No-one did. You posted some links to ...
By Majordennisbloodnok , 2 hours ago
-
Just realised that this image of the cylinder cupboard ...
By Sheriff Fatman , 2 hours ago
-
RE: Rodents! A word of warning for heat pump owners
Two thoughts: 1: Let's ask @david-s if Primary Pro in...
By Transparent , 2 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
In the diagram below, I describe my understanding of th...
By Batpred , 3 hours ago
-
RE: Running from backup generaor in powercut?
@batpred Thanks for the warning. definately a job for a...
By Pipcart , 3 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@editor Mars, First of all thank you for your enco...
By Wally , 3 hours ago
-
I need to have a look out for it. I know IBM feeds some...
By Batpred , 3 hours ago
-
-
RE: Daikin Atherma ASHP Cycling 6 Times an Hour?
Thanks for your reply. Yes that's a good idea to try a...
By John Marshall , 9 hours ago
-
RE: Hot water heating in parallel with space heating
An external heat exchanger would need a pump which woul...
By bontwoody , 9 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
@ecobaker Thanks for this. I've had it in both slots. ...
By andbeck , 19 hours ago
-
RE: Air source heat pump circuit not operational
Welcome to the forums. If the thermostat shows it’s c...
By Mars , 19 hours ago
-
RE: Ecodan with FTC7 - True Weather Compensation
@danwright90 I've linked two videos below recorded this...
By Sheriff Fatman , 22 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
That makes plenty of sense. Perhaps more importantly, O...
By Majordennisbloodnok , 24 hours ago