FTC cables broken - Can I use heat pump without? Ecodan Heat pump
Hi this may be a stupid question , but my dog somehow managed to tear 2 cables that new attached to the FTC on the circuit board it is marked - RD - CNW12, to is coming up with error code L5 and the heat pump doesn't seem to be kicking in
Any ideas if I can do a workaround or a way to fix ?
Posted by: @jonbonbabyHi this may be a stupid question , but my dog somehow managed to tear 2 cables that new attached to the FTC on the circuit board it is marked - RD - CNW12, to is coming up with error code L5 and the heat pump doesn't seem to be kicking in
Any ideas if I can do a workaround or a way to fix ?
The cable should be connected to THW1 - Flow Water Temperature Thermistor and THW2 - Return Water Temperature Thermistor.
To get your system operational I would suggest that you try to reconnect the four cores. Remove the plug from the circuit board and if you have a soldering iron then solder the broken wires together, or tape them if you don't have a soldering iron. The wires should be colour coded. When repaired replace the plug back in the socket.
You may be able to get replacement Thermistors later.
I doubt that the heat pump will function without these two signals since they are rather important for correct operation.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 192 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@jamespa Can I check something that I done some weeks a...
By trebor12345 , 22 minutes ago
-
RE: Electricity price predictions
Judging by the representatives I have spoken to locally...
By JamesPa , 42 minutes ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
Check on the heat pump controller. It will show whethe...
By JamesPa , 44 minutes ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
The problem I see with A2A (and I'm interested if there...
By Temperature_Gradient , 1 hour ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@temperature_gradient I specifically explained to my po...
By Toodles , 1 hour ago
-
RE: Grant Aerona Short Cycling
@damonc I was refering to the 'standard' energy sticker...
By MikeFl , 5 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas where do I find Havenwise Support? On...
By Morgan , 5 hours ago
-
RE: Grant Aerona circulation/system pump staying on
My AERONA 3 circulation pump runs constantly whatever t...
By damonc , 18 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Thanks, @sheriff-fatman. Happy for you to search any po...
By Majordennisbloodnok , 21 hours ago
-
Thanks, @cathoderay. I was aware of some changes to ...
By Majordennisbloodnok , 21 hours ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 1 day ago
-
This is what I answered, I really have no hope: "......
By Batpred , 2 days ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj oh yes they offer Daikin 8kW, they tried to fo...
By AgentGeorge , 2 days ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Good point! Just in case anyone re...
By Batpred , 2 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
A correct sized collector is all you need. Saying this,...
By greenlight , 2 days ago
-
-
RE: Here is my heat pump installation with questionable COP in Italy
@jamespa Sorry for the late reply, I apologize for the ...
By materox345 , 2 days ago
-
Thanks for your response. I have UFH downstairs and ...
By GeorgeA , 3 days ago