I read a lot about Flow temperatures on various threads on the forums.

Are they crucial to get it right?

How do I know what the flow temperature should be and is it adjustable,
I have virtually no one locally that is able to help me run this system (Samsung 16 kW) as the installers went into liquidation and it been a nightmare getting the system running efficiently as far as I am able.

This topic was modified 2 months ago 2 times by Mars

   
Quote
bontwoody
(@bontwoody)
Noble Member Contributor
5014 kWhs
Joined: 3 years ago
Posts: 741
 

Hi Patrick

In a word yes. If you want an efficient heat pump system then you need to set the flow temperature as low as possible while still providing a comfortable house.

You need to set up Water Law in your Samsung controller. Do you have any idea how it is set up at the moment?

I have a Samsung so should be able to help.

Mark

 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@alfapat)
Reputable Member Member
1175 kWhs
Joined: 2 years ago
Posts: 158
Topic starter  

I will have a look at some downloads and see if I can spot some instructions thank you!


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5014 kWhs
Joined: 3 years ago
Posts: 741
 

@alfapat this shows how https://m.youtube.com/watch?v=FcXAtVjdRE8

I have a feeling though that he puts one of the figures in the wrong way around in the video though 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@alfapat)
Reputable Member Member
1175 kWhs
Joined: 2 years ago
Posts: 158
Topic starter  

OK THANKS, i THINK what I have is similar , I watched your video and will adopt similar settings . I will show a couple of pictures meantime.

thumbnail image0 (2)
Samsung 1

 


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5014 kWhs
Joined: 3 years ago
Posts: 741
 

That is an older controller you have so the procedure might be different unfortunately 

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote



(@alfapat)
Reputable Member Member
1175 kWhs
Joined: 2 years ago
Posts: 158
Topic starter  

so been to the 20 settings and I set 2011 to -5c , 2012 +15 weather comp, 2021 @50c, 2022 @ 32c going by gen6 vid above.2091 @1 . The only one corrected is 32 degrees c. That being the change I have put in , will that make adiffence do you think? 

I will update my system if I knew how to do it , interestingly I am considering a solar/battery installation as well.


   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5014 kWhs
Joined: 3 years ago
Posts: 741
 
IMG 0890
IMG 0889
IMG 0891

Here are my settings, I think the 201 settings in the video might be backwards. You can always check by feeling if your radiators are hotter in colder weather. I would try and get the flow temperature as low as possible, 50C particularly will be expensive. Just lower them gradually by a degree a day and see how it feels. If you get to 45C when its -5C outside and the room is too cool. then raise it by one and you have it. Same when the weather is warm.

Solar panels are always a good idea, batteries a little more nuanced as they are expensive. If you have an EV then you can access very cheap overnight tariffs to fill a battery.

Have a look at my blog which should give you a few ideas 🙂

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@alfapat)
Reputable Member Member
1175 kWhs
Joined: 2 years ago
Posts: 158
Topic starter  

So 2021 setting You reckon that the rads circ.@50 might be too high. It would be difficult to measure apart from laying a thermometer on it I suppose. If the Room temps are still reaching 22 , which its set for just now , incidently the room the thermostat it is in just now is still only 21.5 and should be 22 since 15.1 hrs , it takes a while ? At 2.0 degrees lower , I can try that to see if its easier to reach that tomorrow . Am I looking at the right path here, please.

 

Blog? Sorry where and how do you put thar stuff below about your system please.

This post was modified 2 months ago 2 times by Alfapat

   
ReplyQuote
bontwoody
(@bontwoody)
Noble Member Contributor
5014 kWhs
Joined: 3 years ago
Posts: 741
 

@alfapat So the absolute flow temperature isnt important. Just how it makes the room feel. If its been 15 hours and you still havent made the desired room temperature, thats an indication that you may need to increase flow temperature in the water law settings.

The problem is that high flow temperatures lead to inefficient operation, so you need to try and keep them as low as possible. If you find that you need a flow temperature of 50C when its cold, then the only thing you can do is improve the insulation of the house or fit bigger radiators.

House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60


   
ReplyQuote
(@alfapat)
Reputable Member Member
1175 kWhs
Joined: 2 years ago
Posts: 158
Topic starter  

@bontwoody Ah , ok I get it now. Thank you . No it’s only 5 hours thankfully. But it’s still a while @ 1 degree from 21 to 22 degrees.  I’ll try it lower and see if I get grumbles ! ☺️ I can check energy hub also .

It is after all said and done -4 just now , and the bungalow has pretty decent insulation including underfloor, roof but because it’s timber built on dwarf the outside plaster has a thin polystyrene coat . Airsource installed on energy trust grant approval 8 yrs ago 

This post was modified 2 months ago by Alfapat

   
ReplyQuote
(@alfapat)
Reputable Member Member
1175 kWhs
Joined: 2 years ago
Posts: 158
Topic starter  

Ah I see where you get 15hrs , no its 15.00hrs , (3pm)

Very cold yesterday but the system did cope , total of 114.68kwh £28.05.Trying to match heat pump with Octopus cosy they have three lower tariff slots and only got to grips with adjusting them yesterday after three days on new tariff. I will give this another day and drop down the flow temp to 48c.


   
ReplyQuote



Page 1 / 8
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security