Flow rate issues?
When our 11.2KW Ecodan was serviced back in October the engineer remarked that the flow rate was a little on the low side, approx 20 litres/min. He didn't think it would cause any major issues, but just advised us to be aware of it.
Roll forward to the current cold snap, and we've a couple of issues, and I'm just wondering if they could be attributable to the low flow rate.
1. When running a water cycle (set to 45C) the flow temp rises to about 47C and stays there until the tank starts to get close to the target temperature and then seems to drop to about 45C. Sometimes the flow temp might creep up again to 46C, but generally it just sits at 45C still running the water heating cycle, presumably because the tank hasn't reached a high enough temperature for the controller to be satisfied. I now work around this by using the iBoost to give a quick 15 minute burst on the immersion heater when the tank temperature reaches about 40C. Probably ought to mention that we don't have an immersion connected to the controller. If I don't use the iBoost the water cycle will continue until it has reached the 60 minute heating time set by the controller, then go back to space heating for 30 minutes before starting the water cycle again. If left to its own devices it will just continue in this loop.
2. We have radiators upstairs and underfloor heating on the ground floor. Upstairs temperature is fine - sits at a fairly steady 19-20C, but ground floor rooms are a bit too low for our liking (17.5 - 18C). We are running weather compensation, set to 42C at -3C, 20C at 18C. With the outside temperature below 0C I am seeing a water temperature of about 30C at the UFH manifold, mixer valve is set to maximum (65C). UFH has its own circulating pump.
The main pump and the UFH pump are both set to their maximum speed.
Any thoughts before I call an engineer out to charge me £££££'s for diagnosing the problem?
Thanks
For a typical 5degK delta T between flow and return, to provide 11kW you ideally need 11/(5x4.2) = 0.524l/s or 31l/min. Suggest the flow needs to increase or check and adjust the deltaT setting on the Ecodan if possible. Generally, the lower you set the weather compensated maximum supply temperature, the higher the flow needs to be because the deltaT between flow and return decreases. That's just how the physics of heat loss works.
What flow temperature have you the hot water boost set to? Medium temperature ASHPs may struggle to reach 50degC flow temperature or higher at the moment due to the very cold weather and also periodically defrosting. The flow temperature goes up like a saw tooth blade. It keeps dropping back during each defrost cycle.
Posted by: @allyfishFor a typical 5degK delta T between flow and return, to provide 11kW you ideally need 11/(5x4.2) = 0.524l/s or 31l/min. Suggest the flow needs to increase or check and adjust the deltaT setting on the Ecodan if possible. Generally, the lower you set the weather compensated maximum supply temperature, the higher the flow needs to be because the deltaT between flow and return decreases. That's just how the physics of heat loss works.
What flow temperature have you the hot water boost set to? Medium temperature ASHPs may struggle to reach 50degC flow temperature or higher at the moment due to the very cold weather and also periodically defrosting. The flow temperature goes up like a saw tooth blade. It keeps dropping back during each defrost cycle.
I don't think the deltaT can be adjusted on the Ecodan - it's not something I can see in the controller manual.
The hot water flow temperature is, I assume, set by the controller on the basis of the desired tank temperature. Again, I can't see anything about setting it manually. It seems to reach about 2C above the desired temperature and then drop back down as the tank comes up.
We're currently defrosting about every 60 to 80 minutes, and it seems to take about 15 minutes from the start of a defrost before the flow temperature returns to what it was.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 18 Online
- 5,673 Members
Podcast Picks
Latest Posts
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
@editor Have ‘signed up’ for an interview Mars, looks i...
By Toodles , 1 hour ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 2 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@patrickvito We have had car dealers re-powder coat the...
By ASHP-BOBBA , 3 hours ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 3 hours ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 3 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 3 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 8 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 9 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 11 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 21 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago