Flow rate issues?
When our 11.2KW Ecodan was serviced back in October the engineer remarked that the flow rate was a little on the low side, approx 20 litres/min. He didn't think it would cause any major issues, but just advised us to be aware of it.
Roll forward to the current cold snap, and we've a couple of issues, and I'm just wondering if they could be attributable to the low flow rate.
1. When running a water cycle (set to 45C) the flow temp rises to about 47C and stays there until the tank starts to get close to the target temperature and then seems to drop to about 45C. Sometimes the flow temp might creep up again to 46C, but generally it just sits at 45C still running the water heating cycle, presumably because the tank hasn't reached a high enough temperature for the controller to be satisfied. I now work around this by using the iBoost to give a quick 15 minute burst on the immersion heater when the tank temperature reaches about 40C. Probably ought to mention that we don't have an immersion connected to the controller. If I don't use the iBoost the water cycle will continue until it has reached the 60 minute heating time set by the controller, then go back to space heating for 30 minutes before starting the water cycle again. If left to its own devices it will just continue in this loop.
2. We have radiators upstairs and underfloor heating on the ground floor. Upstairs temperature is fine - sits at a fairly steady 19-20C, but ground floor rooms are a bit too low for our liking (17.5 - 18C). We are running weather compensation, set to 42C at -3C, 20C at 18C. With the outside temperature below 0C I am seeing a water temperature of about 30C at the UFH manifold, mixer valve is set to maximum (65C). UFH has its own circulating pump.
The main pump and the UFH pump are both set to their maximum speed.
Any thoughts before I call an engineer out to charge me £££££'s for diagnosing the problem?
Thanks
For a typical 5degK delta T between flow and return, to provide 11kW you ideally need 11/(5x4.2) = 0.524l/s or 31l/min. Suggest the flow needs to increase or check and adjust the deltaT setting on the Ecodan if possible. Generally, the lower you set the weather compensated maximum supply temperature, the higher the flow needs to be because the deltaT between flow and return decreases. That's just how the physics of heat loss works.
What flow temperature have you the hot water boost set to? Medium temperature ASHPs may struggle to reach 50degC flow temperature or higher at the moment due to the very cold weather and also periodically defrosting. The flow temperature goes up like a saw tooth blade. It keeps dropping back during each defrost cycle.
Posted by: @allyfishFor a typical 5degK delta T between flow and return, to provide 11kW you ideally need 11/(5x4.2) = 0.524l/s or 31l/min. Suggest the flow needs to increase or check and adjust the deltaT setting on the Ecodan if possible. Generally, the lower you set the weather compensated maximum supply temperature, the higher the flow needs to be because the deltaT between flow and return decreases. That's just how the physics of heat loss works.
What flow temperature have you the hot water boost set to? Medium temperature ASHPs may struggle to reach 50degC flow temperature or higher at the moment due to the very cold weather and also periodically defrosting. The flow temperature goes up like a saw tooth blade. It keeps dropping back during each defrost cycle.
I don't think the deltaT can be adjusted on the Ecodan - it's not something I can see in the controller manual.
The hot water flow temperature is, I assume, set by the controller on the basis of the desired tank temperature. Again, I can't see anything about setting it manually. It seems to reach about 2C above the desired temperature and then drop back down as the tank comes up.
We're currently defrosting about every 60 to 80 minutes, and it seems to take about 15 minutes from the start of a defrost before the flow temperature returns to what it was.
- 22 Forums
- 2,049 Topics
- 44.7 K Posts
- 47 Online
- 3,277 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Hydronic plinth heaters and ASHPs
@jamespa we should be ok as the model I'm looking at ha...
By benson , 8 minutes ago
-
RE: Renewables & Heat Pumps in the News
Let me add two other points to what @lucia has just pos...
By Transparent , 13 minutes ago
-
RE: Yes, the "zoning with ASHP" topic again...
@harryrea I agree entirely with the concept of zoning ...
By Heatgeek , 1 hour ago
-
RE: Help optimising my system!
@wh0am3ye you’re absolutely right that what you’re seei...
By Mars , 3 hours ago
-
RE: Additional Battery v Wind Turbine v Ripple
There was a call today for Ripple investors and amongst...
By Judith , 19 hours ago
-
@heatgeek I kind of get it… but aren’t you still in the...
By SUNandAIR , 21 hours ago
-
-
RE: Commencing on an ASHP Installation Process
I think you may very well be right and of course A2A ca...
By JamesPa , 1 day ago
-
-
RE: Agile: average import cost vs other tariffs?
@old_scientist We are with SSEN and our G99 application...
By Toodles , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Yes. Storing the solar generation within the home is gr...
By Transparent , 3 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15, @heacol cover your area… I’d strongly recom...
By Mars , 3 days ago
-
RE: Warm weather and heat pumps.
@editor Oh nothing right now because $ needed for struc...
By Lucia , 4 days ago
-
RE: Potentially more choice including air to air heat pump grants
@jeff Such documents are far too wordy for my ‘daily re...
By Toodles , 4 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@grahaml I cannot agree that it is a small percentage o...
By benson , 5 days ago
-
RE: Samsung Gen6 16kW tribulations
@emceed, can you please give us an update on your syste...
By Mars , 6 days ago
-
What's the problem you are trying to solve. The answer...
By JamesPa , 1 week ago
-
Good luck. For what it is worth my system was very def...
By JamesPa , 1 week ago
-
RE: Massive Electricity Cost for Running My Air Source Heat Pump
I agree @mark-h The Building Regs are now very readable...
By Transparent , 1 week ago