Ecodan Room Temperature Mode
Just wondering if there is anyone running their Ecodan in Room Temperature (Room Adaptation) Mode? If so, how are you finding it?
We now have our system set up to use this mode, and, while it seems to work well for the radiators, it does not seem ideally suited to UFH, although there are a few compromises with our system as a result of the way it has been installed.
The UFH is downstairs only and is split into 3 zones, each with its own thermostat. When one of these calls for heat, the UFH controller sends a demand to the FTC. So far, so good, but here is the compromise, the main FTC controller is located on our first floor landing next to the airing cupboard, and in order for heat to get from the ASHP to the UFH, both the UFH controller and the FTC controller need to be calling for heat! This means that in order for the UFH to work off the zone stats, the FTC controller needs to be set so that it is always on. I don't think this can possibly work correctly; there is no meaningful feedback from the rooms being heated to the FTC controller. One option is to get another Mitsubishi wireless controller and locate it downstairs, but I don't really want to shell out for this unless I know it's going to work.
I was under the impression, perhaps wrongly, that in room adaptation, the FTC used some form of weather compensation to determine the flow temperature, perhaps depending on both the outside temperature and the difference between measured and demanded temperature? What we are seeing is the flow temperature going up to over 50C whenever the UFH is triggered, irrespective of the outdoor temperature. Very inefficient, when, even on the coldest nights, we never used to get above 43C in weather compensation mode.
We have had some nice sunny days here recently, so the house gets nicely warmed by the sun during the day, meaning that the UFH is off from about 9.00 until probably 1.00 or 2.00 in the morning. This obviously means that the floor temperature (concrete slab) drops considerably, so the ASHP then has to work hard to get it back up to temperature before the rooms start getting heated again. I don't know if room adaptation mode, if it had the correct feedback, would preemptively kick the ASHP in to life to prevent the rooms dropping too much below the desired temperature. However, this would imply some sort of intelligence to predict how far the room temperature is going to drop based on the outside temperature - perhaps I'm expecting a bit too much!
I'll probably try giving Mitsubishi a call to find out a bit more, but I am starting to think that straightforward Weather Compensation may the be best way forward.
what is FTC?
are you using ECOdan mixers and room thermostats for the underfloor heating too?
If not, don’t expect anything near optimal performance…
Professional installer
Posted by: @alec-morrowwhat is FTC?
are you using ECOdan mixers and room thermostats for the underfloor heating too?
If not, don’t expect anything near optimal performance…
FTC is the Mitsubishi Flow Temperature Controller.
It is the standard Mitsubishi controller for heat pumps. It has been upgraded lots of times over the years. Consumers use it to control weather compensation, heat pump schedules etc.
FTC is the Mitsubishi Flow Temperature Controller
The ASHP was retrofitted so the UFH uses controller and stats from Uponor as originally fitted approx 15 years ago
stats from uponoor and their mixing valve will be the issue
broadly speaking mixing simple on off signals which are the uponoor stats, with controls that vary flow temp won’t work effectively.
heat pumps are one industry where we definitely need to adopt German or Swedish practices.. they use compensation controllers on electronic mixing valves to optimise efficiency comfort and reliability
Professional installer
I don't see how what you're doing will work. Auto-adaptation uses outside temperature and room temperature to try and work out the best way to run the ASHP. If you set the FTC controller high so that it's always calling for heat then it will keep increasing the flow temp until it reaches its set room temp. If your ufh stats are set at the proper target room temp, lower than the FTC one, then it never will and you are going to end up with a high temp ufh system, which is what it sounds like you have.
If you want to use the FTC and auto adaptation then turn your ufh stats up high so they are always calling and let the FTC control the flow and room temps. I don't think this will support multiple zones though.
I'm very interested in this as it's what I'm going to try next. I have two zones, both radiators and I was planning on turning them both right up and letting FTC/auto adaptation control things.
BTW you can get a remote room temperature sensor for the FTC off ebay for about £15.
This is some info on Auto Adaptation
You might be better off with weather compensation
Thanks for that information, it confirms what I thought was happening.
I'm not going to write off Room Adaptation just yet, but may have to revert to Weather Compensation while I investigate if a wireless controller can take over from the FTC, in which case we can set the UFH stats high and use the wireless controller for room adaptation.
@kev-m A quick update.
After thinking about the problem for a little while and re-reading the manual I came up with really simple solution - swap the existing sensors over! I can't believe our installer didn't think of it, or that I didn't think of it sooner.
We have a wireless controller already, that was located on the top floor of the house and being used to control the radiators, so I simply went into the system settings and swapped that to be the sensor for the UFH zone, and the FTC controller to be the sensor for the radiators. The wireless controller is now downstairs in our dining room, set to 20C, with all the UFH zone stats set to ~21C. Overnight it dropped to about 6C here. The house was already warm because it had been a nice sunny day, so the house didn't cool down enough for the ASHP to kick in until about 2am. Once it kicked in the temperature stabilised at 20C and has been there ever since. Flow temperatures not getting anywhere near the 50C I was seeing previously. Now wondering if I can convince the wife that 19C is an acceptable temperature 😀
The final thing I have to do is tweak the setting on the FTC controller to keep my office, which is on the top floor, at a comfortable temperature.
I am hoping that this should keep the house at a more stable temperature. We are in quite an exposed location on the edge of the Fens, so when the wind blew the house was chilling down a bit when we were just using weather compensation. Although we hopefully won't find that out now until next winter!
I assume it's the Mitsubishi wireless controller you're talking about. I didn't think you could have the wireless and the main FTC controller monitoring separate zones; I thought when the wireless was installed, it in effect became the main FTC sensor. I could well be wrong though.
If the ufh stats are at 21 and the wireless one is set at 20 then that should let auto adaptation work properly downstairs. Upstairs, it depends on whether the FTC main controller can be set separately to the wireless one. If so, you can choose your temp and off you go. If not then I assume your upstairs zones will open up when downstairs calls for heat and will get the same flow temperature as downstairs (which will be decided by auto adaptation). In effect, you'd have one big zone.
I also don't see how auto adaptation would work if the FTC and the remote sensor both monitor room temps. Which one would it use?
All very interesting. BTW I assume you have the latest FTC manual for this?
Kev
Yes, it is the Mitsubishi wireless controller that I am using.
You raise an interesting point because obviously there is no way to have two independently controlled flow temperatures. Although we have, notionally, 2 heating zones, I am not able to change how each one operates independently. Space heating can either be room, flow or curve. Whatever I set becomes the heating mode for both zones. The way it is working at the moment, zone 1 appears to be the "master", controlled by the wireless. Zone 2 (which hasn't turned on since I made the changes) will, I think, be a "slave" where its 2-port valve is controlled by the FTC, and the flow temperature is set by the "master".
I do have the latest version of the manual, but trying to relate what it says to the way our system has been plumbed and wired is not easy!
I will continue to experiment and see what happens with flow temperature when zone 2 starts calling for heat.
Thanks for your comments - always useful to have somebody else's take on things.
Peter.
@peterr Mitsubishi almost certainly have mixing valves and controllers for second and third circuits. Ideally each circuit would have a mixing valve thus minimising flow from buffer.
why not ring or email Mitsubishi to find out?
Professional installer
- 24 Forums
- 1,402 Topics
- 29.4 K Posts
- 18 Online
- 1,185 Members
Join Us!
Latest Posts
-
RE: Recommended ASHP installers in Hampshire
@editor we are just south of Petersfield. Octopus- la...
By benson , 6 hours ago
-
By Mars , 7 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I've learned some more from my discussions with Aira. ...
By IvanOpinion , 9 hours ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
The most you're likely to get from a regulator like MCS...
By Transparent , 10 hours ago
-
RE: New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
@macfxd LLH = Low Loss Header - it's on the right of ...
By MikeFl , 11 hours ago
-
RE: ASHP Cut-off Temperatures: What's Your Setting and is a Your Heating Still On?
@technogeek Yes it does. It's in the field settings
By LeChillou , 12 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Yes, its on 21C 24/7 from end Sept until start of May. ...
By Vince31 , 13 hours ago
-
Vaillant Arotherm Settings for New Installation
Im just helping my brother in law with his new 7kW Arot...
By bontwoody , 15 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
Hello @hem. And I see that @editor has very quickly fou...
By Transparent , 16 hours ago
-
RE: Say hello and introduce yourself
@editor I'm in Shropshire I had read that microbor...
By IRMartini , 18 hours ago
-
RE: Are Solar Diverters Necessary for Homes with ASHPs and Solar PV?
Yeah, my diverter is off almost all the time since we h...
By Andris , 1 day ago
-
RE: Creating a second zone on Mitsubishi Ecodan ASHP
Thanks for your time with this Gary. I have a wireless...
By BryanB , 2 days ago
-
RE: Error on Immersun – Error 8 Load Short Circuit
@julesmp8 After a whole battery of tests? 😉
By Toodles , 2 days ago
-
RE: Delivering a smart and secure electricity system: government consultation
@abernyte Well, anything is possible, after all, we hav...
By Toodles , 2 days ago
-
RE: Heat Pump Paradox: The Industry's Adoption Divide
@majordennisbloodnok 😆
By Toodles , 3 days ago
-
RE: How to increase DHW water temperature on Samsung Gen 6 Control Panel
@jamespa I have the Samsung high temp quiet model and w...
By TechnoGeek , 3 days ago
-
RE: Need a bit of help please: problematic heat pump installation
Thanks for the replies, and looking back it is a bit va...
By Seagrave , 3 days ago
-
RE: GSHP running UFH but no feedback loop yet.
thanks! It did turn out to be a sort of fault - well, ...
By petew , 3 days ago
-
RE: My ASHP is not performing as well as I’d hoped: COP just over 2
@hcas - exactly so. I did read one other persons simila...
By HarriUp , 5 days ago
-
RE: The EPC Dilemma: How Current Ratings Fail Heat Pumps
@toodles your EPC is a limited tool that needs to be af...
By ajn9000 , 5 days ago
Latest Topics
-
By Mars 7 hours ago
-
Recommended ASHP installers in Hampshire
By benson 7 hours ago
-
Vaillant Arotherm Settings for New Installation
By bontwoody 15 hours ago
-
EV charger installation question – I don't want to bury the cable
By Hem 16 hours ago
-
Creating a second zone on Mitsubishi Ecodan ASHP
By BryanB 5 days ago