Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Room Temperature Mode
Just wondering if there is anyone running their Ecodan in Room Temperature (Room Adaptation) Mode? If so, how are you finding it?
We now have our system set up to use this mode, and, while it seems to work well for the radiators, it does not seem ideally suited to UFH, although there are a few compromises with our system as a result of the way it has been installed.
The UFH is downstairs only and is split into 3 zones, each with its own thermostat. When one of these calls for heat, the UFH controller sends a demand to the FTC. So far, so good, but here is the compromise, the main FTC controller is located on our first floor landing next to the airing cupboard, and in order for heat to get from the ASHP to the UFH, both the UFH controller and the FTC controller need to be calling for heat! This means that in order for the UFH to work off the zone stats, the FTC controller needs to be set so that it is always on. I don't think this can possibly work correctly; there is no meaningful feedback from the rooms being heated to the FTC controller. One option is to get another Mitsubishi wireless controller and locate it downstairs, but I don't really want to shell out for this unless I know it's going to work.
I was under the impression, perhaps wrongly, that in room adaptation, the FTC used some form of weather compensation to determine the flow temperature, perhaps depending on both the outside temperature and the difference between measured and demanded temperature? What we are seeing is the flow temperature going up to over 50C whenever the UFH is triggered, irrespective of the outdoor temperature. Very inefficient, when, even on the coldest nights, we never used to get above 43C in weather compensation mode.
We have had some nice sunny days here recently, so the house gets nicely warmed by the sun during the day, meaning that the UFH is off from about 9.00 until probably 1.00 or 2.00 in the morning. This obviously means that the floor temperature (concrete slab) drops considerably, so the ASHP then has to work hard to get it back up to temperature before the rooms start getting heated again. I don't know if room adaptation mode, if it had the correct feedback, would preemptively kick the ASHP in to life to prevent the rooms dropping too much below the desired temperature. However, this would imply some sort of intelligence to predict how far the room temperature is going to drop based on the outside temperature - perhaps I'm expecting a bit too much!
I'll probably try giving Mitsubishi a call to find out a bit more, but I am starting to think that straightforward Weather Compensation may the be best way forward.
what is FTC?
are you using ECOdan mixers and room thermostats for the underfloor heating too?
If not, don’t expect anything near optimal performance…
Professional installer
Posted by: @alec-morrowwhat is FTC?
are you using ECOdan mixers and room thermostats for the underfloor heating too?
If not, don’t expect anything near optimal performance…
FTC is the Mitsubishi Flow Temperature Controller.
It is the standard Mitsubishi controller for heat pumps. It has been upgraded lots of times over the years. Consumers use it to control weather compensation, heat pump schedules etc.
FTC is the Mitsubishi Flow Temperature Controller
The ASHP was retrofitted so the UFH uses controller and stats from Uponor as originally fitted approx 15 years ago
stats from uponoor and their mixing valve will be the issue
broadly speaking mixing simple on off signals which are the uponoor stats, with controls that vary flow temp won’t work effectively.
heat pumps are one industry where we definitely need to adopt German or Swedish practices.. they use compensation controllers on electronic mixing valves to optimise efficiency comfort and reliability
Professional installer
I don't see how what you're doing will work. Auto-adaptation uses outside temperature and room temperature to try and work out the best way to run the ASHP. If you set the FTC controller high so that it's always calling for heat then it will keep increasing the flow temp until it reaches its set room temp. If your ufh stats are set at the proper target room temp, lower than the FTC one, then it never will and you are going to end up with a high temp ufh system, which is what it sounds like you have.
If you want to use the FTC and auto adaptation then turn your ufh stats up high so they are always calling and let the FTC control the flow and room temps. I don't think this will support multiple zones though.
I'm very interested in this as it's what I'm going to try next. I have two zones, both radiators and I was planning on turning them both right up and letting FTC/auto adaptation control things.
BTW you can get a remote room temperature sensor for the FTC off ebay for about £15.
This is some info on Auto Adaptation
You might be better off with weather compensation
Thanks for that information, it confirms what I thought was happening.
I'm not going to write off Room Adaptation just yet, but may have to revert to Weather Compensation while I investigate if a wireless controller can take over from the FTC, in which case we can set the UFH stats high and use the wireless controller for room adaptation.
@kev-m A quick update.
After thinking about the problem for a little while and re-reading the manual I came up with really simple solution - swap the existing sensors over! I can't believe our installer didn't think of it, or that I didn't think of it sooner.
We have a wireless controller already, that was located on the top floor of the house and being used to control the radiators, so I simply went into the system settings and swapped that to be the sensor for the UFH zone, and the FTC controller to be the sensor for the radiators. The wireless controller is now downstairs in our dining room, set to 20C, with all the UFH zone stats set to ~21C. Overnight it dropped to about 6C here. The house was already warm because it had been a nice sunny day, so the house didn't cool down enough for the ASHP to kick in until about 2am. Once it kicked in the temperature stabilised at 20C and has been there ever since. Flow temperatures not getting anywhere near the 50C I was seeing previously. Now wondering if I can convince the wife that 19C is an acceptable temperature 😀
The final thing I have to do is tweak the setting on the FTC controller to keep my office, which is on the top floor, at a comfortable temperature.
I am hoping that this should keep the house at a more stable temperature. We are in quite an exposed location on the edge of the Fens, so when the wind blew the house was chilling down a bit when we were just using weather compensation. Although we hopefully won't find that out now until next winter!
I assume it's the Mitsubishi wireless controller you're talking about. I didn't think you could have the wireless and the main FTC controller monitoring separate zones; I thought when the wireless was installed, it in effect became the main FTC sensor. I could well be wrong though.
If the ufh stats are at 21 and the wireless one is set at 20 then that should let auto adaptation work properly downstairs. Upstairs, it depends on whether the FTC main controller can be set separately to the wireless one. If so, you can choose your temp and off you go. If not then I assume your upstairs zones will open up when downstairs calls for heat and will get the same flow temperature as downstairs (which will be decided by auto adaptation). In effect, you'd have one big zone.
I also don't see how auto adaptation would work if the FTC and the remote sensor both monitor room temps. Which one would it use?
All very interesting. BTW I assume you have the latest FTC manual for this?
Kev
Yes, it is the Mitsubishi wireless controller that I am using.
You raise an interesting point because obviously there is no way to have two independently controlled flow temperatures. Although we have, notionally, 2 heating zones, I am not able to change how each one operates independently. Space heating can either be room, flow or curve. Whatever I set becomes the heating mode for both zones. The way it is working at the moment, zone 1 appears to be the "master", controlled by the wireless. Zone 2 (which hasn't turned on since I made the changes) will, I think, be a "slave" where its 2-port valve is controlled by the FTC, and the flow temperature is set by the "master".
I do have the latest version of the manual, but trying to relate what it says to the way our system has been plumbed and wired is not easy!
I will continue to experiment and see what happens with flow temperature when zone 2 starts calling for heat.
Thanks for your comments - always useful to have somebody else's take on things.
Peter.
@peterr Mitsubishi almost certainly have mixing valves and controllers for second and third circuits. Ideally each circuit would have a mixing valve thus minimising flow from buffer.
why not ring or email Mitsubishi to find out?
Professional installer
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 446 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 3 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 4 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 5 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 7 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 7 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 8 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 8 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 11 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 13 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 13 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 13 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 14 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 1 day ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago

![auto asa]] auto asa]]](https://renewableheatinghub.co.uk/wp-content/uploads/wpforo/attachments/15/thumbnail/1105-auto-asa.jpg)