Ecodan Long Cycling and AA behaviour in one day.
This is a recording of one day operation of an Ecodan 8.5, reviewing new settings in an attempt to extend the cycling period during milder weather (13c to 7c).
I have used the MELCloud hourly record and marked up the changing room temperatures (IAT) and manual changes to target room temperatures. These have been written on the hourly graphs to produce a timeline of alteration so as the room and outside temperatures have changed. 8am to 9pm.
The reason for doing this was to experiment with new monitoring period settings and understand Auto adaptive behaviour. And hopefully some users might also find the results useful. The graphs start at 8am yesterday.
The next 4 hours
I will post the next batch on a separate post
Posted by: @sunandairThis is a recording of one day operation of an Ecodan 8.5, reviewing new settings in an attempt to extend the cycling period during milder weather (13c to 7c).
I have used the MELCloud hourly record and marked up the changing room temperatures (IAT) and manual changes to target room temperatures. These have been written on the hourly graphs to produce a timeline of alteration so as the room and outside temperatures have changed. 8am to 9pm.
The reason for doing this was to experiment with new monitoring period settings and understand Auto adaptive behaviour. And hopefully some users might also find the results useful. The graphs start at 8am yesterday.
The next 4 hours
I will post the next batch on a separate post
This is excellent data, and just goes to prove that a correctly optimised system can operate in an efficient and effective manner.
Towards the evening the rapidly dropping outside temperature appears to make the system react and over shoot the target temperature by one degree.
Posted by: @sunandairTowards the evening the rapidly dropping outside temperature appears to make the system react and over shoot the target temperature by one degree.
I think that the increase in IAT may be due to the WC curve not being fully optimised.
My understanding is that in AA mode the controller responds primarily to the WC, with fine tuning from the AA in response to changes in IAT. Because changes in IAT occur slowly, correction by AA is also very slow, so may not be able to respond quickly if the WC is overreacting.
The final chart does show that the AA appears to be pulling back the LWT and reducing the DT in an effort to lower the IAT.
As a test, you could try switching off AA for a period to see how well the system copes operating in just WC mode, then compare this with AA mode.
@derek-m thanks for your comments… yes there could be a need to change the WC. I’ve not changed it since we removed the LLH. I’m also conscious that our AA SETUP is still learning since we’ve not had any rapid drops in outdoor temperature since we started using it again. Last night had quite a fast drop in temp.
I’ll let you know if any adjustments change things. 👍🏻
I was going to start a new topic but I'll join this one if that's OK. I've been running AA for about a year and am pretty happy with it. It uses about the same amount as energy as WC, maybe even a bit less. AA COP is worse than WC but then it's not running for as long. Below are two similar days; one on WC and one on AA. I get almost no cycling on AA. However, LWT is higher than WC and like you, IAT overshoots by as much as 1.5 degrees. It does chase target IAT quite aggressively, something I'd like to avoid. BTW I have 2 zones; I have them set to do the same thing but because the use different temperature sensors they are not always quite in sync. I'm sure you can tell which one is which...
Use translate in browser.
1. https://www.haustechnikdialog.de/Forum/p/2913017
2. https://www.haustechnikdialog.de/Forum/p/2913032
3. https://www.haustechnikdialog.de/Forum/p/2913145
3.
https://www.mitsubishi-les.com/assets/documents/12445/1/ph-ecodan-de.pdf
4. https://www.haustechnikdialog.de/Forum/p/2920861
5. https://www.haustechnikdialog.de/Forum/p/3082635
Posted by: @fazelUse translate in browser.
1. https://www.haustechnikdialog.de/Forum/p/2913017
2. https://www.haustechnikdialog.de/Forum/p/2913032
3. https://www.haustechnikdialog.de/Forum/p/2913145
3.
https://www.mitsubishi-les.com/assets/documents/12445/1/ph-ecodan-de.pdf
4. https://www.haustechnikdialog.de/Forum/p/2920861
5. https://www.haustechnikdialog.de/Forum/p/3082635
Interesting. That explains why the IAT is always above the set point.
Posted by: @kev-mI was going to start a new topic but I'll join this one if that's OK. I've been running AA for about a year and am pretty happy with it. It uses about the same amount as energy as WC, maybe even a bit less. AA COP is worse than WC but then it's not running for as long. Below are two similar days; one on WC and one on AA. I get almost no cycling on AA. However, LWT is higher than WC and like you, IAT overshoots by as much as 1.5 degrees. It does chase target IAT quite aggressively, something I'd like to avoid. BTW I have 2 zones; I have them set to do the same thing but because the use different temperature sensors they are not always quite in sync. I'm sure you can tell which one is which...
Hi Kev, Glad you can join in the discussion. We have made some changes to our system so it looks like we can get some better cop outcomes and so far it’s looking really promising. I think last time we spoke I said I was hoping to break into the low cop4’s. However as you may know the MELCloud system has regularly added 2.8kwh to the daily energy usage data so we can’t fully rely on the data it produces. However notwithstanding that, the past 10 days we have had 4 days at cop4.0, a cop4.71 and a cop4.25 the remainder were 3.5 and 3.8. We are comforted that if the data system has added fictional energy usage then our data will be under reporting its efficiency and not over reporting.
Looking at you’re charts it’s clear the AA chart has less cycling. This may be due to the interval you’ve set for data gathering. I say that because I had mine set to every 20 minutes and it cycled twice per hour. I now have it set to 30 minutes (as per the above graphs) so it may run for a full 30 minutes before varying it’s output or stopping.
After a year, do you have any clearer understanding of the specific function of the over-temperature and under temperature parameter? I have shortened my temperature parameters.
interested to hear what’s you thoughts!
Posted by: @fazelUse translate in browser.
1. https://www.haustechnikdialog.de/Forum/p/2913017
2. https://www.haustechnikdialog.de/Forum/p/2913032
3. https://www.haustechnikdialog.de/Forum/p/2913145
3.
-- Attachment is not available -- -- Attachment is not available --
https://www.mitsubishi-les.com/assets/documents/12445/1/ph-ecodan-de.pdf
4. https://www.haustechnikdialog.de/Forum/p/2920861
5. https://www.haustechnikdialog.de/Forum/p/3082635
interesting forum comments @fazel.
Do you think the forum member comments are factual? Because I spoke to a tech advisor back in April who stated the AA system does make reference to the weather compensation curve. Could it be we are just fed whatever sounds plausible.
Whats your system doing? How are things operating for you?
ps I couldn’t translate any other docs but I’ll try again when I’m on my laptop.
- 21 Forums
- 1,744 Topics
- 37.3 K Posts
- 34 Online
- 2,035 Members
Join Us!
Latest Posts
-
RE: In the Bleak Midwinter... Midea heat pump performance, poor COP and windchill in action
A similar pattern happened again last night and into th...
By cathodeRay , 5 hours ago
-
RE: Do thick walls make for warm houses?
@bontwoody A lot of the reason the u value doesn’t s...
By robl , 6 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
@crimson A raise in flow temperature to 45 deg. C shoul...
By Toodles , 6 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@mikeh, thanks a lot for the video. I found them very i...
By trungdong , 7 hours ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor I suspect I need both. We're still trying to ge...
By Odd_Lion , 1 day ago
-
RE: Samsung HP secondary pump wiring
Thanks for the reply. I have asked a couple of days ago...
By Chris-in-Kemnay , 1 day ago
-
RE: New Samsung 12KW Heat Pump Help
@mike-h It has been a few days since we’ve changed t...
By dinhp , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Two other things that greatly effect SCOP but havent be...
By bontwoody , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Hi All We have 2 ASHPs, Solar/Battery system and soon...
By AlanB , 1 day ago
-
@westkent OK , Interesting , Im surprised that Airsourc...
By Alfapat , 1 day ago
-
RE: Post Buffer Tank DUCA Circulating Pump Settings
@potatoman I raised this with Secon, and here's what th...
By Mars , 1 day ago
-
RE: Smart meter installation – seamless or a potential nightmare?
@transparent, now hosted on our site as attached.
By Mars , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
That's actually not too bad, or, to put it another way,...
By cathodeRay , 1 day ago
-
RE: Air source heat pump roll call
Ecodan PUZ-WM85VAA1.7 slimline Stelrad Softline Comp...
By Westkent , 1 day ago
-
RE: Baffled by heat pump size/ choice!
Try reducing the DHW hysteresis setting and schedule th...
By JohnR , 3 days ago
-
RE: Vaillant ASHP Weather Compensation with Octopus Cosy
Your Sensocomfort is the thermostat and it does work as...
By Judith , 3 days ago
-
@raiph I apologise for my incorrect assumption. A PWM p...
By Mike H , 3 days ago
-
RE: Should We Rethink the Name “Heat Pump” for Homeowners?
Not sure you need the "re". Caleferator sounds fine to...
By downfield , 3 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
Thanks for this Mars. I've actually found out the issue...
By dnagre , 4 days ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
The ASHP, just like a boiler, can supply water at only ...
By JamesPa , 4 days ago
Latest Topics
-
Samsung HP secondary pump wiring
By Chris-in-Kemnay 2 days ago
-
Post Buffer Tank DUCA Circulating Pump Settings
By Potatoman 2 days ago
-
Baffled by heat pump size/ choice!
By zuluwarrior 4 days ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 6 days ago
-
By R0y124 6 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 7 days ago
-
By TheHolyHeatPump 1 week ago
-
Flow temperature- At what point?
By Westkent 1 week ago
-
Excessive performance/system issues with GSHP
By didjerama_uk 1 week ago