Ecodan - Legionnaires Cycle
Does anyone else observe this behaviour with their Ecodan?
When the Legionnaires cycle kicks in, the ASHP raises the LWT to around 60 degrees very quickly but as soon as it gets there it peaks and then starts falling again, at which point the immersion kicks in.
However, I never really get the tank temperature up to 60 degrees. I would have thought the ASHP could have operated for longer at 60 degrees LWT and use that to do a longer job of heating up the tank.
Is it something to do with how long I have set the ‘hold at temperature’ setting for? I thought this was referring to holding the tank temperature but perhaps it means holding the LWT temperature?
Thoughts?
Posted by: @hjdDoes anyone else observe this behaviour with their Ecodan?
When the Legionnaires cycle kicks in, the ASHP raises the LWT to around 60 degrees very quickly but as soon as it gets there it peaks and then starts falling again, at which point the immersion kicks in.
However, I never really get the tank temperature up to 60 degrees. I would have thought the ASHP could have operated for longer at 60 degrees LWT and use that to do a longer job of heating up the tank.
Is it something to do with how long I have set the ‘hold at temperature’ setting for? I thought this was referring to holding the tank temperature but perhaps it means holding the LWT temperature?
Thoughts?
I hadn't looked at this before but I did and this is what mine does. This was one of mine in October. I don't know if the immersion is used; I didn't think it was but I have never looked. Looks similar to what you describe.
With a 60degC legionella set point, my ASHP takes the DHW temperature up to 50degC and then goes to standby, and the immersion heater takes over for the rest of the legionella cycle. I've seen it work the same way at a 65degC set point too. The immersion seems happy to support whatever duraiton I specify for holding the tank temperature. The immersion is the 3kW Ecodan element that came with their water cylinder.Posted by: @hjdDoes anyone else observe this behaviour with their Ecodan?
When the Legionnaires cycle kicks in, the ASHP raises the LWT to around 60 degrees very quickly but as soon as it gets there it peaks and then starts falling again, at which point the immersion kicks in.
However, I never really get the tank temperature up to 60 degrees. I would have thought the ASHP could have operated for longer at 60 degrees LWT and use that to do a longer job of heating up the tank.
Is it something to do with how long I have set the ‘hold at temperature’ setting for? I thought this was referring to holding the tank temperature but perhaps it means holding the LWT temperature?
Thoughts?
What rating of immersion element do you have?
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh LFP battery storage
PHEV; Zappi charger
@skd I think the pump will raise the LWT temp to the setting for the maximum heat pump flow temperature. I increased that to 60C and during the legionella cycle it raised the tank temp and handed over to the immersion. My actual normal Hot Water tank temp is 46 - we have a big tank and low usage.
Unfortunately my issue it that I have two thermostats: one on the immersion and one measuring temperature for the heat pump. The immersion is in the middle of the tank, not the bottom and stratification happens quickly when it's running so the tank immersion cuts out even though it's set at it's maximum thermostatic setting because the layer of water it's in is over the temp, however just a little below it is the heat pump temperature sensor where it can be 5-20c lower temp, and even lower towards the bottom of the tank.
Result: Heat pump gets the whole tank well over 50 then stops, immersion takes over until it cuts out when the top layer of the tank is maybe over 65 but I can't heat the whole tank to 60, I can get most of it well above 50 and then I try and make sure it's left there for at least 4 hours which is a fair legionella killer.
In an unvented system, I really don't feel the legionella risk is high and this is reasonable mitigation once every 30 days.
I need a destrat pump.
@rod thanks, yes that figures. My max ASHP temp is currently set to 50degC. I need to increase it too
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh LFP battery storage
PHEV; Zappi charger
Thanks all. Very helpful. I shall have a play changing some of the settings
- 26 Forums
- 2,364 Topics
- 53.6 K Posts
- 156 Online
- 6,027 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
Looking at your figures, I'm guessing you'd ideally nee...
By Old_Scientist , 26 minutes ago
-
I agree, I'm equally predisposed to a cold sunny winter...
By Old_Scientist , 48 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj they will release smarter controls, its been m...
By swwils , 3 hours ago
-
RE: Speedcomfort radiator fans
Thats true, but having tried (and succeeded) in constru...
By JamesPa , 3 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@bash brilliant, thanks for the feedback
By energy9165 , 5 hours ago
-
RE: Setback savings - fact or fiction?
The OpenWeatherMap API provides plenty of historical da...
By Majordennisbloodnok , 5 hours ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair There I was, feeling grumpy, he said “Cheer u...
By Toodles , 7 hours ago
-
RE: Grant Aerona: Is there a setting to keep the 2-port valve open during pump blockade
Depends on OAT. Mine cycles at OAT>10 and of course...
By JamesPa , 8 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent My conclusion is as you have noted, tha...
By Bash , 9 hours ago
-
That makes sense to me,although we don't know what the ...
By Transparent , 11 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
And to you too. Wishing you a very enjoyable festive s...
By Sheriff Fatman , 11 hours ago
-
RE: External pipework insulation
They do? But that isn't apparent from the photos we'r...
By Transparent , 13 hours ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@editor Thank you so much for looking into this for me ...
By Caron , 14 hours ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 1 day ago
-
Daikin EDLA11D3V3 DHW Settings
I have a newly installed EDLA11D3V3 which I'm still get...
By Velcro , 1 day ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Hi @mickamills . Welcome to the forum. It sounds like...
By bontwoody , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
@curlykatie did you get sorted with this?
By MickaMills , 1 day ago
-
RE: MyVaillant Connect Regular Disconnect
Thanks. Yes, if the time is consistently 11pm every nig...
By buckwem , 2 days ago