How are Ecodan CoP quotes from MelCloud setups?
Posted by: @harriupMy surplus power 'consumed' last year was around 630kWh, so around 1.75kWh every day. Some fairly random variation either side of this, not related to consumption, and certainly not a straightfoward percentage overestimate. A standard deduction would get you closer to the figure, but if you want accuracy then the most cost effective would be a standard electric meter (c£40ish?) that has a pulse output which can be plugged into the FTC controller and will replace the units guesstimates with accurate measurements.
glpinxit
I also spent a long period at first noting down daily figures from the controller - most tedious. But then mastered looking at the code generated by MelCloud in a browser window (in my case Firefox >Tools >Browser Tools >Developer Tools> then Network and Response options) and have managed to create an entire history of the unit's performance in a spreadsheet. This is much more useful to make comprisons with.
I have just been looking at the Ecodan manual for a different reason and remembered your post. So taking your figures of 630kWh last year, that gives 1.726kWh per day, or 71.9178W for each hour.
According to the manual, Water Pump 4 in the Energy Monitor settings has a default value of 72W.
Has anyone checked the settings within their system?
The surplus consumption appears even when the heating is off over the summer, sometimes weirdly high, ie 3kWh - and though there is proportional relationship to the heat generated when the unit does run, it is quite loose.
I have a 20W continuous draw, partly the controller board, but I also suspect the MelCloud wifi module is responsible for some of that. Given that the units can draw several kW of power I think that the lower current draws in particular are not being measured accurately. And Mitsubushi are quite clear that if you want an accurate measure of the energy consumed you should fit a proper meter.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Posted by: @harriupThe surplus consumption appears even when the heating is off over the summer, sometimes weirdly high, ie 3kWh - and though there is proportional relationship to the heat generated when the unit does run, it is quite loose.
I have a 20W continuous draw, partly the controller board, but I also suspect the MelCloud wifi module is responsible for some of that. Given that the units can draw several kW of power I think that the lower current draws in particular are not being measured accurately. And Mitsubushi are quite clear that if you want an accurate measure of the energy consumed you should fit a proper meter.
I fully appreciate that an external power meter will probably be more accurate than any internal equipment.
The point that I am making is that even an external power meter will only provide truly accurate system power consumption, if all the auxiliary equipment (pumps, valves, heaters etc.) are actually powered via such an external power meter. I assume that the external power meter is monitoring the power being fed to the outside unit. If you have the pre-piped Ecodan water cylinder, the power for the control box can be via the outside unit or from an alternative power supply. If it is from an alternative power supply then the power used by all the equipment connected to the cylinder control box will not be measured by the external power meter. This could be the reason why the external and internal readings differ.
According to my interpretation of the information contained within the manual, the controller can accommodate up to 4 water pumps, and if each of these water pumps had its own dedicated power meter, the controller could accept a power meter reading for each, and collate these values along with all the other power used by the system. In the absence of dedicated power meters for any water pumps, it is possible to set an estimated value of power consumption for each of the 4 possible water pumps that could be installed. The default setting for water pump 4 is 72W, which I assume will be the value used by the controller in its calculations whether pump 4 is installed and is running or not.
I would again suggest that you check the values that have been set within the service menu, covering water pumps and any other equipment that could be using power.
Currently viewing this topic 1 guest.
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 26 Online
- 5,656 Members
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@carlo the 16kw rating refers to output.. afaik? So w...
By Tim441 , 10 hours ago
-
Anyone still weathering it out with Agile?
Being curious, I have continued to monitor the daily ra...
By Toodles , 16 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 21 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 2 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 2 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 4 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 4 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 4 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 5 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 5 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago