Ecodan ASHP low flow rate 6L
Hi I've been trying to setup my ASHP in wc mode recently as been running it just like a gas boiler recently found out that was stupid and was why the cost of electricity was sky high
Been on a mission to learn as much as possible about the ftc5 to get this sorted I've got the WC setup but pump just kept cycling through reading and learning I've found out the flow rate is 6l my unit PUZ-WM85 should be around 15l the pump speed is at 5 dhw is also at 5 but speed is still 6L I drained the tf1 filter nothing much came out and the prrssure in the system is at 1.5bar
Anyhelp would be appreciated
How old are your radiators? Might they have a build up of sludge? Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
They were installed same time as the heating they are the thicker radiators aswel when trying to bleed through radiators just the clean antifreeze that comes out they do heat up evenly also
@davidm Maybe there is a restriction caused by a partially open/shut valve? It sounds as though, though the pumps are working hard, there is an obstruction to a free flow of water through the system. A partially open or shut valve would cause a restriction, turbulence and probably additional noise.
Other than that might there be some obstruction from ‘gunk’ that was dislodged during the plumbing work that has lodge itself in a pipe (possibly at a joint). A lot to check I know but if pump is working its’ socks off and the water isn’t flowing fast enough - it is almost bound to be an obstruction or restriction - or (shudder) a kinked pipe! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Yeah that's what I seems like to me if you up the pump speed on the actual pump the flow still doesn't change, unfortunately I'm not equipped to take apart any of that
it was a company that fitted the system and my housing association plumbers ain't clued up on the ASHP at all, they sent someone round before when I moved in to help me setup didn't have a clue what to do, taken it upon myself to learn and I enjoy tinkering but at a loss what to do now
@davidm welcome to the forums.
It sounds like your Ecodan system could benefit from some adjustments to optimise both flow rates and pump sizing. With pre-plumbed Ecodan cylinders, the internal pumps are often undersized for anything but the best-designed systems, and they may not provide the 12–14 L/min flow rate recommended for an 8 kW unit like yours. This kind of consistent flow is critical for efficient heating and to reduce unnecessary cycling, especially in weather compensation (WC) mode.
If you have system separation, such as a buffer tank, it might be worth considering removing it. By eliminating it, your system can circulate more freely and reach the needed flow rates more consistently.
Also, controlling valves across all rooms can reduce flow efficiency. Instead, consider limiting smart TRVs to just bedroom zones if a cooler environment is desired overnight. For the best results, aim to keep all other valves open, allowing the system to circulate freely without restriction. This should help the heat pump function more smoothly in WC mode, minimise cycling and improve efficiency – keeping those energy bills in check.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
All my trv valves are full open around the whole house removing anything wouldn't be a option as it doesn't belong to me (housing association)
You say reaching needed flow rates consistently it doesn't reach them at all it's just 6l on pump speed 5 if I turn it to 3 flow rate goes to 0
Kind of looking for information to pass onto the h/a to maybe actually get somewhere with it as their own plumbers ain't clued with these as most houses around are gas but the small village I'm in doesn't have gas most are oil heating or electric here
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 201 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
Interesting to see home energy storage being pushed as ...
By Jeff , 2 minutes ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
@adamk yes they equalise once off
By jeegnesh , 2 minutes ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@toodles Yep, and it is not even a sticking plaster ...
By Jeff , 31 minutes ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
yup, it is definitely over working. You can hear the co...
By lukewarmbath , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
I agree, imperfect systems like voting for politicians ...
By Batpred , 5 hours ago
-
RE: Gov wants to alter our FIT contracts from rpi to cpi
The consultation is just part of the normal process for...
By Jeff , 5 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@mairie - Your constituency member, Dr Zubir Ahmed MP, ...
By Transparent , 6 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Some tweaks of WC may indeed be necessary, if its too h...
By JamesPa , 6 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred I think you probably got the wrong end of the ...
By swwils , 17 hours ago
-
@transparent @old_scientist Quick update, I submitted...
By Batpred , 21 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Lol. I know they CAN be calibrated, it’s just ...
By Crimson , 21 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
Yes thats true, but that cant happen unless the room te...
By JamesPa , 22 hours ago
-
@jamespa thanks appreciate the comments. Simon
By simonwig , 22 hours ago
-
Do Heat Pumps need to start up at Full Power?
When our heat pump starts up, (Daikin EDLA08 8 kW Monob...
By Toodles , 23 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@colinc good luck with your project! UFH is the absolut...
By Judith , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Just wondering if/where Ideal might be on your de...
By simonwig , 2 days ago
-
@judith I haven't noticed any noise myself yet, nor my ...
By Eliuccio , 3 days ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@ectoplasmosis Buderus is a subsidiary of the Bosch Gro...
By Steelbadger , 3 days ago
-
RE: Confusion over Octopus Tariffs
@agentgeorge I can’t recall when and the details but Co...
By Toodles , 3 days ago