Ecodan ASHP low flow rate 6L
Hi I've been trying to setup my ASHP in wc mode recently as been running it just like a gas boiler recently found out that was stupid and was why the cost of electricity was sky high
Been on a mission to learn as much as possible about the ftc5 to get this sorted I've got the WC setup but pump just kept cycling through reading and learning I've found out the flow rate is 6l my unit PUZ-WM85 should be around 15l the pump speed is at 5 dhw is also at 5 but speed is still 6L I drained the tf1 filter nothing much came out and the prrssure in the system is at 1.5bar
Anyhelp would be appreciated
How old are your radiators? Might they have a build up of sludge? Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
They were installed same time as the heating they are the thicker radiators aswel when trying to bleed through radiators just the clean antifreeze that comes out they do heat up evenly also
@davidm Maybe there is a restriction caused by a partially open/shut valve? It sounds as though, though the pumps are working hard, there is an obstruction to a free flow of water through the system. A partially open or shut valve would cause a restriction, turbulence and probably additional noise.
Other than that might there be some obstruction from ‘gunk’ that was dislodged during the plumbing work that has lodge itself in a pipe (possibly at a joint). A lot to check I know but if pump is working its’ socks off and the water isn’t flowing fast enough - it is almost bound to be an obstruction or restriction - or (shudder) a kinked pipe! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Yeah that's what I seems like to me if you up the pump speed on the actual pump the flow still doesn't change, unfortunately I'm not equipped to take apart any of that
it was a company that fitted the system and my housing association plumbers ain't clued up on the ASHP at all, they sent someone round before when I moved in to help me setup didn't have a clue what to do, taken it upon myself to learn and I enjoy tinkering but at a loss what to do now
@davidm welcome to the forums.
It sounds like your Ecodan system could benefit from some adjustments to optimise both flow rates and pump sizing. With pre-plumbed Ecodan cylinders, the internal pumps are often undersized for anything but the best-designed systems, and they may not provide the 12–14 L/min flow rate recommended for an 8 kW unit like yours. This kind of consistent flow is critical for efficient heating and to reduce unnecessary cycling, especially in weather compensation (WC) mode.
If you have system separation, such as a buffer tank, it might be worth considering removing it. By eliminating it, your system can circulate more freely and reach the needed flow rates more consistently.
Also, controlling valves across all rooms can reduce flow efficiency. Instead, consider limiting smart TRVs to just bedroom zones if a cooler environment is desired overnight. For the best results, aim to keep all other valves open, allowing the system to circulate freely without restriction. This should help the heat pump function more smoothly in WC mode, minimise cycling and improve efficiency – keeping those energy bills in check.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
All my trv valves are full open around the whole house removing anything wouldn't be a option as it doesn't belong to me (housing association)
You say reaching needed flow rates consistently it doesn't reach them at all it's just 6l on pump speed 5 if I turn it to 3 flow rate goes to 0
Kind of looking for information to pass onto the h/a to maybe actually get somewhere with it as their own plumbers ain't clued with these as most houses around are gas but the small village I'm in doesn't have gas most are oil heating or electric here
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 77 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@jamespa cannot find loss calculation. When they get i...
By BAMi , 17 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 59 minutes ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 3 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 5 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 5 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 6 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 17 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 20 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 24 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 5 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 6 hours ago
-
SolarPV tables / online calculator
By MichelleC 13 hours ago
-
By Toodles 2 days ago