Hi I've been trying to setup my ASHP in wc mode recently as been running it just like a gas boiler recently found out that was stupid and was why the cost of electricity was sky high

 

Been on a mission to learn as much as possible  about the ftc5 to get this sorted  I've got the WC setup but pump just kept cycling through reading and learning I've found out the flow rate is 6l my unit  PUZ-WM85 should be around 15l  the pump speed is at 5 dhw is also at 5 but speed is still 6L I drained the tf1 filter nothing much came out and the prrssure in the system is at 1.5bar 

 

Anyhelp would be appreciated 


   
Quote
Toodles
(@toodles)
Famed Member Contributor
11253 kWhs
Veteran
Joined: 2 years ago
Posts: 1818
 

How old are your radiators? Might they have a build up of sludge? Toodles.

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote
(@davidm)
Active Member Member
43 kWhs
Joined: 5 months ago
Posts: 4
Topic starter  

They were installed same time as the heating they are the thicker radiators aswel when trying to bleed through radiators just the clean antifreeze that comes out they do heat up evenly also


   
ReplyQuote
Toodles
(@toodles)
Famed Member Contributor
11253 kWhs
Veteran
Joined: 2 years ago
Posts: 1818
 

@davidm Maybe there is a restriction caused by a partially open/shut valve? It sounds as though, though the pumps are working hard, there is an obstruction to a free flow of water through the system. A partially open or shut valve would cause a restriction, turbulence and probably additional noise.

Other than that might there be some obstruction from ‘gunk’ that was dislodged during the plumbing work that has lodge itself in a pipe (possibly at a joint). A lot to check I know but if pump is working its’ socks off and the water isn’t flowing fast enough - it is almost bound to be an obstruction or restriction - or (shudder) a kinked pipe! Regards, Toodles.

Toodles, he heats his home with cold draughts and cooks his food with magnets.


   
ReplyQuote
(@davidm)
Active Member Member
43 kWhs
Joined: 5 months ago
Posts: 4
Topic starter  

Yeah that's what I seems like to me if you up the pump speed on the actual pump the flow still doesn't change, unfortunately I'm not equipped to take apart any of that

it was a company that fitted the system and my housing association plumbers ain't clued up on the ASHP at all, they sent someone round before when I moved in to help me setup didn't have a clue what to do, taken it upon myself to learn and I enjoy tinkering but at a loss what to do now


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26254 kWhs
Veteran
Joined: 4 years ago
Posts: 2979
 

@davidm welcome to the forums.

It sounds like your Ecodan system could benefit from some adjustments to optimise both flow rates and pump sizing. With pre-plumbed Ecodan cylinders, the internal pumps are often undersized for anything but the best-designed systems, and they may not provide the 12–14 L/min flow rate recommended for an 8 kW unit like yours. This kind of consistent flow is critical for efficient heating and to reduce unnecessary cycling, especially in weather compensation (WC) mode.

If you have system separation, such as a buffer tank, it might be worth considering removing it. By eliminating it, your system can circulate more freely and reach the needed flow rates more consistently. 

Also, controlling valves across all rooms can reduce flow efficiency. Instead, consider limiting smart TRVs to just bedroom zones if a cooler environment is desired overnight. For the best results, aim to keep all other valves open, allowing the system to circulate freely without restriction. This should help the heat pump function more smoothly in WC mode, minimise cycling and improve efficiency – keeping those energy bills in check.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote



(@davidm)
Active Member Member
43 kWhs
Joined: 5 months ago
Posts: 4
Topic starter  

All my trv valves are full open around the whole house removing anything wouldn't be a option as it doesn't belong to me (housing association)

You say reaching needed flow rates consistently it doesn't reach them at all it's just 6l on pump speed 5 if I turn it to 3 flow rate goes to 0 

Kind of looking for information to pass onto the h/a to maybe actually get somewhere with it as their own plumbers ain't clued with these as most houses around are gas but the small village I'm in doesn't have gas most are oil heating or electric here


   
ReplyQuote



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security