Does legionella cycle also heats up radiators?
Hello. Beginner's question:
I have a system with a ASHP and a hot water tank.
When the legionella cycle (Friday 1pm for 1 hour) kicks in my radiators also heat up. Is this supposed to happen?
I am suspecting the valve that controls where the hot water from the pump goes (diverting to DHW or Heating) is not working well, and DHW is leaking to the radiators.
Welcome to the forums @bbmorales
No, that shouldn’t be happening. It sounds like you’re on the right track with your diagnosis though. During the legionella cycle, only your hot water tank should be heating up, not the radiators. This suggests that the diverter valve may be faulty and allowing hot water to flow into the heating circuit. A photo of the diverter valve would be helpful.
The other question this poses is that I assume your heating is off at the moment and you’re only using your heat pump for hot water production. So why is your system coming on at all and distributing heat to your rads. Does your circulation pump come on when the legionella cycles starts?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi @editor Mars, many thanks.
Regarding the images, I've uploaded two, hopefully this gives you an idea of the system.
Regarding your other question
"Does your circulation pump come on when the legionella cycles starts? "
Apologies for the question, but where is this pump and how to I verify this?
I have not disabled completely the heating, but I can try doing so next Friday (disable completely the heating, leaving on only DHW).
Thanks for your help!
@bbmorales let's backtrack a little bit. Can you please share more information about the system you have (brand and model of heat pump would be a good starting point)? We'll need to ascertain whether your heating is in fact off.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
There is no need, imo, to run a legionella cycle as often and it would be better run during the night on cheaper rate electricity. The ASHP heats to 50c and the immersion takes over to 60c. Expensive on day time rate on a weekly basis. Needn’t be for as long as an hour either so far as I know.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Faulty 3 port diverter….
Easiest fix is to disable the legionella program.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@bbmorales it's a personal preference and depends on the likelihood of bacteria proliferating in your tank. We run a Legionella cycle every two weeks. Since we work from home and use hot water frequently, the water in our cylinder is constantly being drained and replaced, preventing stagnation. This routine works for us. However, some homeowners choose to turn it off completely.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 75 Online
- 5,744 Members
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
@editor this is exciting! It will be great to hear how...
By GrahamF , 4 minutes ago
-
RE: Powerwall 3 or Myenergi or something else?
I think you need to be sure you are comparing like for ...
By Old_Scientist , 37 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
Water pump will certainly make a hum (which could conce...
By JamesPa , 3 hours ago
-
@jamespa Thanks. Yeah any adjustments Ive made at pr...
By cliffhanger , 3 hours ago
-
RE: Mitsu PAR-WT60R Wireless Controller - options
I have been running mine in auto adapt since 2019 and i...
By Abernyte , 5 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 16 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 4 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 6 days ago