Hello.
I am not a professional, just a householder. My house is an old barn with very thick stone walls.
I had a Daikin Altherma 3 ystem fitted in the summer under the ECO4 system.
Outside model: EBLA 11 DAV 3
Inside model; EDLA 11 DA 3V3
The installer has created 2 zones (upstairs and downstairs).
They also fitted new radiators , solar panels, and wall insulation throughout the house. I previously had oil fired heating and changed because the installer said an ASHP system would save me money.
Now we have snow and freezing temperatures outside, it seems that we have serious heating problems.
The setpoint is set to 39 degress, but the Daikin control panel shows an actual temperature of only 34 degrees. Does this indicate a fault with the system? I have emailed the installer and Daikin, but not redceived an answer.
The third party thermostats (one for each zone) are set to 15.5 degrees, but only 13.5 degrees is being achieved. The actual room temperatures are down as low as 11 degrees, whereas before the cold weather they were reaching a comfortable 17+ degrees.
The radiators have been bled and the pressure is fine at 1.4 bar.
So, our heating is not reaching comfortable levels any more, yet the cost has jumped astronomically from £6.70 a day to £29 a day (equivalent to over £800 a month) I am a pensioner (71) and cannot afford to pay that kind of money, and for a cold house to boot.
Can anyone advise on what action, if any, I should take?
If the tank temperature will not reach the setpoint, I am wondering if the unit may be the wrong size for my house. How can I tell?
Many thnaks and best wishes.
Tog 🙂
@togfather - I too have an old stone built home, a cottage rather than a barn, though listed. Unless you have done a lot of insulation and leak fixing work, your home is likely to have a relatively high heat loss for its size. The first questions any here is going to ask is (a) what is your calculated heat loss and (b) what is the nominal rating of your heat pump setup (it may be in the model numbers - 11? - but I am not familiar with Daikin model numbering, I have a Midea heat pump). The first thing to be aware of is the nominal output is usually far in excess of the actual output when it is cold outside, something that tends not to be mentioned by manufacturers and installers. But first, let us know the building heat loss, and the pump's nominal output. Others will be along soon to chip in as well, no doubt.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay I have a Daikin EDLA08 monobloc and the number on yours suggests that it is indeed an 11 kW model. As CatodeRay mentioned; more information needed please; did you have a heat loss survey carried out? Is your pump on continuously without pausing at all? As this has only shown signs of underpowering since low temperatures have come about, it rather sounds though the heat losses exceed the system’s capabilities. How is the heat pump set up - WC on? Have you set up the MMI for the keaving water temperature and the points on the X axis for control of the slope? Question - questions I know but, our house is well insulated, 98 sq. metres, semi of 1930’s build and we are getting a cop of 2.4 when it is 1 - 2 degrees below freesing and this may use 2 kW/h when running in these conditions. We are using Octopus Cosy and charge two Powerwalls at the lowest rate for the two x three hours slots to keep us off the grid when higher rates apply.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
You’ll never beat Oil, it’s the cheapest form of heating out there.
You need to do the following:
1. Turn all room stats right up to 25 so they stay on permanently.
2. Get your weather compensation curve adjusted to 38.5@15, 50@0…. This means that at 15 degrees outside temperature, your radiators will be at 38 ish degrees and feel ‘warm’. At current outdoor temperatures, the radiators will be at 50 degrees and will feel ‘nice and warm’.
Your high energy consumption could easily be caused by a backup heater inside the heatpump running. That needs to be disabled, as there’s no need for that.
Do you have the heat loss and radiator sizing schedule from your installers?
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Many thanks to all for your comments.
Here is more information requested.
1) The rating of the Altherma 3 is 11KW ( EBLA 11 DAV 3)
2) It is not set to weather curve, but to static setpoint at 39 degrees, but it is not achieving that.
3) The installer supplied heat loss calculations of Area: 157.72m2, Power(W): 10211, Energy(kWh): 24722. Also supplied Emitter Log showing total output of 12785 (W)
4) Pump is on continuously.
5) All external walls are insulated, except for kitchen and bathroom. Some are insulated internally and some are insulated externally. The loft area that is not used for rooms is insulated, and the two rooms in the loft also have wall/eaves insulation.
6) Pump has automatic defrost system. To avoid freezing it can dump water, after which the radiators need bleeding and the pressure needs topping up to around 1.4bar.
7) Pump often makes loud noise, like a car with choke on.
I hope this information is useful and thank you so much for replying.
Tog 🙂
A few quick calculations suggest your heat pump is effectively running as an electric boiler.
Assuming oil is about 75p per litre and 1 litre of oil produces about 10kW of energy. Your £6.70 a day therefore suggests about 9 litres a day which in turn means about 90kW. Note - I've ignored boiler efficiency which is probably around 85%.
Similarly your £29.00 a day for electricity is about 100kW - approx 30p per unit and therefore about 100 units (100kW).
Adding a heat pump will not change the heat load from your house for the same temperatures. If you added insulation you should need fewer kWs.
If your heat pump was running efficiently and we assume a COP of 3, or 300% efficient it should be using about 30 units a day, say £9.00.
On your Daikin MMI panel go to Information and then sensors - post a photo of what it shows. It should say things like compressor: on, back up heater: off etc.. Also again under Information look at Enenrgy Information - there are two options - energy in and heat out. These will give you a basic idea of the COP.
Lastly under the Information sensors option what's the flow rate - it will be the bottom number in the list and you may have to scroll down to see it.
@chrislay Sorry, the £6.70 a day was not the oil. It was the electricity cost during October, after the ASHP was fitted.
When I had oil, I spent about £1,400 a year on oil, but the ASHP looks as if it will cost at least £2,500 a year.
@togfather as I said before, you won’t beat oil with a heat pump….. Oil really is the cheapest heat source out there.
Anyway, back to the original issue. I expect this is all related to the backup heater that Daikin like to use.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@hughf Thank you. You may well be right, and I regret the decision to move, but they told me it would save me money, and I foolishly believed them. I will have to wait for a full year to see the actual additional cost, and even then cannot afford legal fees to sue, so i am now stuck with it and need to find the best way to reduce costs and try and keep comfortable.
@chrislay Today the temperature has risen to around 7 degrees outside. The new setpoint of 43 dgrees is being achieved. The room thermostat is set to 17 degrees now, but only acieving 16 degrees, which is more comfortable than the 13 degrees yesterday.
Electricity used in the last 24 hours is down to 67 kWh, which is an improvement.
Maybe the setpoint was too low. Should i increase it again to see what happens?
Attached are imaghes of the sensor menu.
Best wishe.
@hughf Hi Hugh Im curious as to your evidence for saying you wont beat oil with a heat pump. Ive just checked and an average price for heating oil over the last 2 years is about 85p/lt. At 10.35 kW per litre and a typical efficiency of 85% for the boiler, that gives 9.66p/kWh.
Assuming an electricity price of 31p/kWh a heat pump would only have to average a SCOP of 3.2 for equity, thats very easy to do. In fact using TOU tariffs you can get appreciably better rates, Im currently paying about 20p/ kWh which makes the heat pump a massive winner?
You also have the wide variability of oil prices and delivery hassle to deal with. My sister in law couldnt even get a delivery recently and ran out!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@togfather Hi, as mentioned by others, if you really want to get your bill down you need to abandon using a fixed flow temperature and use weather compensation. This makes your heat pump much more efficient.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
-
How can we prevent our LG heat pump from freezing up in cold weather?
5 days ago
-
Daikin Octopus installation update - I saw my first defrost. 😍😂
1 month ago
-
Daikin Error Code 7H05
3 months ago
-
British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
5 months ago
-
Daikin COP / energy used measurement from MMI
11 months ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 58 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
All agreed. if you want to delete our exchange for cla...
By JamesPa , 8 minutes ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 53 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 1 hour ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 2 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 2 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 4 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 6 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 8 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 20 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 23 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 8 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 9 hours ago
-
SolarPV tables / online calculator
By MichelleC 16 hours ago
-
By Toodles 2 days ago