Having possibly increased the size of the body type from *18 to *25, it may be useful to try adding bytes 23, 24 and 25, to see if the body type has actually been increased.
@derek-m - I don't think it has, recall I checked the actual message length after making the change from *18 to *25, and it stayed exactly the same (see post here).
Meanwhile I am still struggling to get my data back. Like last time, it is still present, but corrupted, and HA refuses to use it.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderay@derek-m - I don't think it has, recall I checked the actual message length after making the change from *18 to *25, and it stayed exactly the same (see post here).
Meanwhile I am still struggling to get my data back. Like last time, it is still present, but corrupted, and HA refuses to use it.
When you checked the message length, did you add additional items to the requested list? If not it could be just supplying the requested items and have the capability of providing more.
Posted by: @derek-mWhen you checked the message length, did you add additional items to the requested list? If not it could be just supplying the requested items and have the capability of providing more.
I don't think I did, but can't remember for sure. But by the apparent logic of the code (we may of course be wrong about that), *25 should produce a byte array of 25 bytes, and what I would expect to see is a message string longer by 25-18 = 7 bytes, with the added bytes remaining as 00. I am reluctant to add the higher data_offset numbers because in the past doing so has always broken the code (it fails to load).
Possible explanations for observed behaviour:
(a) although it looks as though it might, ''return bytearray([0x00] * 25)" doesn't in fact set up a byte array of 25 bytes. However, some clearer than usual python documentation does appear to suggest that bytearray(n) where n is an integer does create a byte array of size n, all items in the array initialised to null (in plain English, it creates an egg box for n eggs, but with no eggs in it):
Syntax:
bytearray(source, encoding, errors)
Parameters:
source[optional]: Initializes the array of bytes
encoding[optional]: Encoding of the string
errors[optional]: Takes action when encoding fails
If source is an integer, creates an array of that size and initialized with null bytes.
# size of array
size = 3
# will create an array of given size and initialize with null bytes
array1 = bytearray(size)
print(array1)
Output:
bytearray(b'\x00\x00\x00') <= suggests the *25 should produce a byte array of \x00 x 25
(source) <=link)
I wonder, is there a clue in 'bytearray([0x00] * 25)' rather than just 'bytearray(25)'?
(b) "'return bytearray([0x00] * 25)" does initialise a byte array of 25 bytes, but it is only part of he code that does so, ie there is something else involved that we have missed.
Midea 14kW (for now...) ASHP heating both building and DHW
I have been doing some further investigation into the structure of the message body with the following results. The actual length of the whole message, header + body, is actually shown within the header at byte position 2. Looking at a recent message header gives the following:-
aa23c300000000000003
aa is a standard flag, probably used to indicate that it is the header.
23 is the total message length, header + body, which in decimal is 35. Since the header is always 10 bytes, then the message body must be 25.
As a test, reset the * 25 back to * 18, to see if the 23 changes to 1c. If the value does not change then this would indicate that the message length is being set elsewhere.
I can check that by looking at old logs (I have kept some) the header stays the same, always aa23c300000000000003, before and after changing from * 18 to * 25.
While I had core/message.py open (to check current value, it is still 25), I noticed this a few lines above the * 25 line:
@property def _body(self): raise NotImplementedError ... @property def _body(self): return bytearray([0x00] * 25) # was 18
Apparently "raise NotImplementedError" is python for "To Do", a sort of place holder. Presumably it is overridden by the later code...
I did a "find in files" for "def _body(" crops up in the device message.py files in multiple places, including this last mention in c3/message.py (still has your suggested additions):
@property def _body(self): # Byte 1 zone1_power = 0x01 if self.zone1_power else 0x00 zone2_power = 0x02 if self.zone2_power else 0x00 dhw_power = 0x04 if self.dhw_power else 0x00 # Byte 7 zone1_curve = 0x01 if self.zone1_curve else 0x00 zone2_curve = 0x02 if self.zone2_curve else 0x00 disinfect = 0x04 if self.disinfect else 0x00 fast_dhw = 0x08 if self.fast_dhw else 0x00 room_target_temp = int(self.room_target_temp * 2) zone1_target_temp = int(self.zone_target_temp[0]) zone2_target_temp = int(self.zone_target_temp[1]) dhw_target_temp = int(self.dhw_target_temp) outdoor_temperature = int(self.outdoor_temperature) # Add return bytearray([ zone1_power | zone2_power | dhw_power, self.mode, zone1_target_temp, zone2_target_temp, dhw_target_temp, room_target_temp, outdoor_temperature, # Add zone1_curve | zone2_curve | disinfect | fast_dhw ])
Presumably as it is the last mention, at least in this file, it is the one that gets implemented.
Midea 14kW (for now...) ASHP heating both building and DHW
I have also been trying to figure out where the message type, and hence structure is being selected within the code.
Looking at the header for a type 04 message gives the following:-
aab9c300000000000004
The total message length is shown as b9 (185 bytes), which is indeed correct for the message received. So it would appear that the length of the message body can indeed be changed.
This now bring us to the actual structure of the message body, and whether and/or how it can be changed.
As you have already discovered, MessageType 0x03 initiates the query instruction, where the Python software sends a message to the Midea Controller, instructing it to send data by return. On the other hand the MessageType 0x04, labelled notify1, instructs the Python software to listen for any messages sent out by the Midea Controller, and take a copy of the message.
I have just received your post about message length, which would indicate that the body length is being set elsewhere, either being set by the body_type selection of 0x01 within midea/devices/C3/message.py, or it may even be fixed within the Midea Controller. If it is the latter then it may not be possible to add additional data to that already being obtained.
What we need to establish is where the structure of the different body_type's is being produce, is it coded within the Midea Controller and merely being selected by the Python software, or is it being selected from a list stored elsewhere.
As a test you could try changing the body_type 0x01 some other value. This would need to be done within the code shown below.
midea_ac_lan/custom_components/midea_ac_lan/midea/devices/c3/message.py class MessageQuery(MessageC3Base): def __init__(self, device_protocol_version): super().__init__( device_protocol_version=device_protocol_version, message_type=MessageType.query, body_type=0x01) class MessageC3Response(MessageResponse): def __init__(self, message): super().__init__(message) body = message[self.HEADER_LENGTH: -1] if (self._message_type in [MessageType.notify1, MessageType.query] and self._body_type == 0x01) or \ self._message_type == MessageType.notify2: self._body = C3MessageBody(body, data_offset=1) self.set_attr()
Even if you do not receive the message body, if the header is produced it may provide some useful information.
When you first discovered the type 04, notify1 message, was the data obtained as provided by recent messages, or did you manage to obtain additional data be modifying the Python code?
@derek-m - that all makes sense, and I think these two (ignore the NotImplementedError) in c3/message.py are indeed where the types given in the full message are set:
class MessageC3Base(MessageRequest): def __init__(self, device_protocol_version, message_type, body_type): super().__init__( device_protocol_version=device_protocol_version, device_type=0xC3, <= hard wired, because this is a c3 unit message_type=message_type, body_type=body_type ) @property def _body(self): raise NotImplementedError class MessageQuery(MessageC3Base): def __init__(self, device_protocol_version): super().__init__( device_protocol_version=device_protocol_version, message_type=MessageType.query, <= gets the query message tyoe number from core.message.py body_type=0x01) <= hard wired
I will try your suggestion, and see what happens.
The class MessageC3Response(MessageResponse) class you show above is not my current version (which you do have, sent as part of recent attachments), my current one looks like this:
class MessageC3Response(MessageResponse): def __init__(self, message): super().__init__(message) body = message[self.HEADER_LENGTH: -1] if (self._message_type in [MessageType.notify1, MessageType.query] and self._body_type == 0x01) or \ self._message_type == MessageType.notify2: self._body = C3MessageBody(body, data_offset=1) elif self._message_type == MessageType.notify1 and self._body_type == 0x04: self._body = C3Notify1MessageBody(body, data_offset=1) elif self._message_type == MessageType.notify2 and self._body_type == 0x05: self._body = C3Notify2MessageBody(body, data_offset=1) self.set_attr()
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @derek-mWhen you first discovered the type 04, notify1 message, was the data obtained as provided by recent messages, or did you manage to obtain additional data be modifying the Python code?
In effect yes, I added code (the key bits are in c3/message.py, with other necessary definitions in midea_devices.py and c3/device.py) and got the byte_09 to byte_16 data, and by deduction worked out byte_09 was almost certainly ambient temp, and byte_14 current set (not actual) LWT.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @derek-mWhen you first discovered the type 04, notify1 message, was the data obtained as provided by recent messages, or did you manage to obtain additional data be modifying the Python code?
In effect yes, I added code (the key bits are in c3/message.py, with other necessary definitions in midea_devices.py and c3/device.py) and got the byte_09 to byte_16 data, and by deduction worked out byte_09 was almost certainly ambient temp, and byte_14 current set (not actual) LWT.
What happens if you add byte_17 to byte_25?
- 22 Forums
- 2,084 Topics
- 45.9 K Posts
- 18 Online
- 3,377 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@jamespa absolutely I guess the take home is, the risks...
By Bart , 1 hour ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 13 hours ago
-
A good start but I’m glad I didn’t need to learn someth...
By Judith , 13 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 18 hours ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 22 hours ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 22 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@benson I have gone down the Home Assistant and wavesha...
By Grantmethestrength , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 1 day ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@editor excellent news, congratulations and well deserv...
By ASHP-BOBBA , 1 day ago
-
RE: Vaillant AroTherm Plus 7kW
Depends on the flow temperature; the Czech data sheet i...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 3 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 3 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 4 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 4 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 4 days ago