Bivalent system questions - ASHP with oil boiler
As some of you may know, we have a bivalent system – our air source heat pump "replaced" our oil boiler, but we kept the oil boiler a a backup, and I'm glad we did.
We have now configured the system to work in the following manner: when temperatures drop below 7C outside, the ASHP hands over the heating duties to the oil boiler, as this is the point where our ASHP efficiencies start to drop, and with electricity tariffs of 24p/kWh we just can't afford to run the heat pump 24/7.
So the question is about the oil boiler. Because our flow rate is set to 40C, the boiler comes on frequently, for short bursts. As an example, it'll come on for 10-15 seconds at a time, and it can come on 2-3 times a minute. Is this a "healthy" way of operating the boiler?
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editorAs some of you may know, we have a bivalent system – our air source heat pump "replaced" our oil boiler, but we kept the oil boiler a a backup, and I'm glad we did.
We have now configured the system to work in the following manner: when temperatures drop below 7C outside, the ASHP hands over the heating duties to the oil boiler, as this is the point where our ASHP efficiencies start to drop, and with electricity tariffs of 24p/kWh we just can't afford to run the heat pump 24/7.
So the question is about the oil boiler. Because our flow rate is set to 40C, the boiler comes on frequently, for short bursts. As an example, it'll come on for 10-15 seconds at a time, and it can come on 2-3 times a minute. Is this a "healthy" way of operating the boiler?
Hi Mars,
I'm not an expert on oil boilers, but what I think is happening is similar to our gas boiler when it operates for a longer period of time. When the boiler initially fires up, it starts heating the water being pumped through, but because it can supply much more heat energy than is required, the water soon gets up to temperature. Because there is still a heat demand from your home, the water continues to be pumped around the system, so cooler water is still flowing into the boiler, and will cool the sensor measuring the water flow temperature and hence fire up the burner again.
I think that you will find that this is normal, particularly if you have the boiler controls set for a low water flow temperature, but you could ask the manufacturer if this is acceptable. It will probably become less pronounced when the outside air temperature is lower and the boiler has to work harder.
Hi Mars,
what you’re referring to is ‘short cycling’ and less desirable on a fossil fuel boiler. Also there is no efficiency gain for running the boiler at a lower flow temperature. As long as the return is below 55deg (assuming it is a condensing boiler) you benefit from the energy recovery of the exhaust.
What is the make and model? Check your manual for the modulation ratio or the minimum heat output. I presume you have the specs of your radiators, at a given temperature delta it will give you the output, add this together for the zone you have active.
or the easier way:
Set flow rate to max 55deg and use your thermostat to provide on / off control.
Thanks guys.
Fortuitously, I had an oil boiler technician visit us today (that's a different story - watch this space) and he said that the short cycling is a no-no and won't do the oil boiler any good in the long run. Just got off the phone with Global Energy Systems and they're going to look into how they manipulate the settings to stop the short cycling.
I'd like to caveat this post by saying we were sold a bivalent system that would be "easy" to switch from ASHP to oil boiler and that the oil boiler would act as a standalone back up. That is certainly not the case – it involves tweaking settings to trick the heat pump into allowing the oil boiler to do the work, and right now the only way it can do that is to come for 4-5 seconds at a time, 3-4 times a minute. Not efficient. No helpful. Not ideal!
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 15 Online
- 5,656 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Anyone still weathering it out with Agile?
Yes, but now try finding a working phone box….
By Majordennisbloodnok , 7 hours ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 9 hours ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 14 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor @sandy I tried contacting them via Whatsapp b...
By brad , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 2 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 2 days ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 2 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 4 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 4 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 5 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 5 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 5 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 6 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 6 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 1 week ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago