Best control strategies for heat pumps that are way oversized
If I have read and copied the Midea data tables correctly, I am not sure I can see much 'efficiency' difference between a smaller heat pump running flat out and a large heat pump running at a lower output. The data here is from Midea's 8kW foot warmer (on the left) vs their 16kW roaster (on the right). Copying PDF tables is always a hit and miss affair, but these tables are just about readable, and what you want to do is, comparing across the same OAT and LWT, find matching outputs (the CAP or capacity column (in Watts), the other two are COP, and PI which is power input in Watts), and then look at the COP and PI values. Of course, none of the outputs match, making this very much a Mark I Eyeball exercise, but in general the 8kW COPs are perhaps slightly worse than the 16kW for similar outputs. For example, at an OAT of 10 and a LWT of 40, the 8kW unit can put out 7774W at a COP of 4.48 using 1735W (the 'norm' row) while the 16kW unit can put out 7441W at a COP of 4.59 using 1620W (the 'min' row) (relevant cells highlighted in attached image). The outputs are not identical, with the 16kW model output slightly lower, and the difference in COP is small, and furthermore these are 'lab' results, ie controlled conditions, not typical real world conditions.
I would much rather have observational data from real world installation...
Midea 14kW (for now...) ASHP heating both building and DHW
A few Mitsubishi figures from their data book for comparison...
5kW output at 12C OAT:
5kW unit is COP of 6.15
11.2kW unit is COP of 5.9
5kW output at -7C OAT:
5kW unit is COP of 3.0
11.2kW unit is COP of 2.9
The 11.2kW is the closest to double the 5kW in Mitsubishi's R32 range, the 6kW is a software limited 8.5kW so not a good comparison.
Comparing the Mitsubishi 8.5kW to the 14kW for an output of 8kW, at 12C and -7C, gives the same COP values.
So a larger unit running at approx. 50% vs smaller unit at approx. 100% doesn't seem to always result in greater efficiency.
I feel the best first question after establishing that a heat pump is over-sized (even massively so say 3x) is does that affect efficiency?
John Cantor covers this well in this YouTube session https://m.youtube.com/watch?v=0oszaqP0TI4
the critical aspect being is it at the limit of its turn down range and then short cycling (which is inefficient). If it isn’t inefficient then the being over-sized is fine, but often isn’t.
Then forcing the cycling to effectively a shorter time on period would be a good first tactic. This would work best with high thermal mass, eg. UFH or solid brick house with good insulation. Aligning the on time to cheap electric is an opportunity.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
Posted by: @judithThen forcing the cycling to effectively a shorter time on period would be a good first tactic. This would work best with high thermal mass, eg. UFH or solid brick house with good insulation. Aligning the on time to cheap electric is an opportunity.
Pretty much I'm coming to that conclusion, TBH it was my hunch when I started this thread but I wanted (and still want) to see if anyone comes up with anything different. So far not but it's still open to debate.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @judithThen forcing the cycling to effectively a shorter time on period would be a good first tactic. This would work best with high thermal mass, eg. UFH or solid brick house with good insulation. Aligning the on time to cheap electric is an opportunity.
Pretty much I'm coming to that conclusion, TBH it was my hunch when I started this thread but I wanted (and still want) to see if anyone comes up with anything different. So far not but it's still open to debate.
I agreed with your approach on the other thread and so pulling out the general case is a better way of capturing it.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
On LG ashp they have a "silent mode" that operates at reduced power (intended to reduce noise at night) and some users use successfully to reduce cycling etc in oversized pumps.
I dont know if other ashp have similar function?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 Re the silent mode, It made me think have a missed something, but i have looked it up, on the Viessmann all the silent mode does is restrict the fan speed, this doesn't reduce the minimum capacity of the compressor therefore doesn't effect minimum output. When the pump is trying to go as low as it can, to reduce output, the fan is already at a reduced speed.
@mikef interesting!
As mentioned .. from info in LG user group it does reduce cycling and output. But I don't use it myself as my heat pump seems approx right size.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
On this forum with advanced monitoring available a Mitsubishi user whose pump was oversized recommended the cloud based auto-adaptation function to improve COP.
It tends to more technical discussions there
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 381 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
Out of interest, why did you buy the Aerona 3 R32, rath...
By GrahamF , 17 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 59 minutes ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Hi @bobflux thanks for pointing out the difference in t...
By DaveC , 1 hour ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@bobflux With my limited HA skills I can't ad...
By Ubert767 , 2 hours ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
I'm going to install Thermacome ACOSI+ radiant ceiling....
By bobflux , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 5 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 7 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 12 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 19 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 23 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 23 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 1 day ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago