Bad COP? Long Pipe Run on Cosy6 Saga Continues.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
With the ASHP installed in a neighbouring street it's going to struggle with heat loss & hydraulic resistance. Clearly no-one had done any proper hydraulic calculations to determine index leg resistance and static head in m, to check against the McDonald's Bin primary pump capacity. If they had, they'd have used hydraulic separation and a secondary pump circuit from the start.
@allyfish That was my thought, looks like the installation is now turning into a canine’s table of comestibles rather than a neat installation with a good COP. I did note the comments passed on from Octopus (if they were interpreted correctly) that the lower flow temperature he had set was counterproductive as far as efficiency is concerned. Maybe the refrigerant or the compressor designs that RED have produced work on slightly different lines to those we have learnt to expect from other manufacturer’s designs? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Presumably the installer would have realised during commissioning that the pump inside the ASHP wasn’t up to the job and witnessed the low flow rate which would have prompted them to reconfigure the pipe work and introduce hydraulic separation?
the installation is now turning into a canine’s table of comestibles
It's a a great big (predictable) PR hole 🐙 dug for themselves - they fell for the fan boi influencer rap, let it get filmed with the 🐙 heat pump Head Honcho while installing it halfway up the street. Now it's covering for one cock-up after another. 🤦🏻♀️
My installation team would never have allowed that to happen they didn't even approve a 10m internal (in my cellar) pipe run that the heat loss surveyor suggested. That's one of many reasons why I liked them. They are heat pump purists. 😁
Meanwhile, it would drive me nuts to have my system out of my control. I want more access to data not less. However, Fan Boi only shares his data with 'members'. 🤓
- 21 Forums
- 1,741 Topics
- 37.2 K Posts
- 57 Online
- 2,033 Members
Join Us!
Latest Posts
-
@raiph I apologise for my incorrect assumption. A PWM p...
By Mike H , 22 minutes ago
-
RE: New Samsung 12KW Heat Pump Help
@mike-h so 2091/2092 were set to 'Use(Signal only ON/OF...
By dinhp , 28 minutes ago
-
RE: Baffled by heat pump size/ choice!
another is to fit waste water heat recovery
By JamesPa , 49 minutes ago
-
RE: Should We Rethink the Name “Heat Pump” for Homeowners?
Not sure you need the "re". Caleferator sounds fine to...
By downfield , 1 hour ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
Thanks for this Mars. I've actually found out the issue...
By dnagre , 22 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent it doesn't sound good 🤔
By Andris , 22 hours ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
The ASHP, just like a boiler, can supply water at only ...
By JamesPa , 24 hours ago
-
RE: Excessive performance/system issues with GSHP
Is the buffer tank in the house? If so, any heat loss s...
By JohnR , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
@transparent - here's the page with more details and im...
By cathodeRay , 1 day ago
-
RE: Vaillant ASHP Weather Compensation with Octopus Cosy
In the Vaillant app go to Settings (the cog wheel icon)...
By JohnR , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks for your reply. I love Octopus Energy and are a ...
By Trevor , 2 days ago
-
RE: Watch Where Your Installer Fits Motorised Valves
The 2000W Karcher will be out shortly!
By Mars , 2 days ago
-
We had a Daikin 8kW ASHP installed two weeks ago. We h...
By R0y124 , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
I did not have the time to check the thermistors Yester...
By ThunderMink , 3 days ago
-
Evening all. Thanks for the replies. Great info....
By TheHolyHeatPump , 3 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
It would be nice if there being lower existing demand o...
By Transparent , 3 days ago
-
RE: Mitsubishi Ecodon stuck on immersion symbol
This how my system is running : Top graph is the am...
By ak2024 , 3 days ago
-
RE: Ecodan help - flow temperature spikes when operating in weather compensation mode
@eleusis it can do it but not in 4 hours, you will need...
By Gary , 3 days ago
-
RE: Most treasured kitchen gadget.
@toodles With the machine its as many as I want or s...
By IRMartini , 3 days ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
@gary The heating bill often looks like we live in a ma...
By ngillam , 3 days ago
Latest Topics
-
Baffled by heat pump size/ choice!
By zuluwarrior 1 day ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 2 days ago
-
By R0y124 2 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 3 days ago
-
By TheHolyHeatPump 4 days ago
-
Flow temperature- At what point?
By Westkent 4 days ago
-
Excessive performance/system issues with GSHP
By didjerama_uk 4 days ago
-
Thermostat setting...still learning
By Profzarkov 4 days ago
-
Watch Where Your Installer Fits Motorised Valves
By Mars 5 days ago
-
Mitsubishi EcoDan ASHP Settings not saving.
By Fez96 5 days ago