5 degrees (average) outside and I am running at a heating COP of 3 so far, flow temperature of 40 degrees (average). My estimate is I'll use 41kw today to heating based on the formula trendline for my past performance.
Posted by: @batalto5 degrees (average) outside and I am running at a heating COP of 3 so far, flow temperature of 40 degrees (average). My estimate is I'll use 41kw today to heating based on the formula trendline for my past performance.
Hi Batalto,
Based upon the Midea data that you supplied previously, along with your heat loss calculations and heat emitter data, the energy consumption figure would appear to be approximately correct, but the calculated water flow temperature should be approximately 49C at a COP of 3.3.
I wonder if like Kev, the flow and return water temperature sensors are not indicating the true temperature.
@derek-m I think it's the difference between lab conditions and actual... Much like MPG claims with cars. Real world experience says you'll never actually get that. Also the losses in the system won't help such as my low loss header
Posted by: @batalto@derek-m I think it's the difference between lab conditions and actual... Much like MPG claims with cars. Real world experience says you'll never actually get that. Also the losses in the system won't help such as my low loss header
The spreadsheet that I produced and sent to you some time ago, incorporated the data that you provided about your system. At an ambient temperature of 5C, the calculated energy consumption would be 42kWh as against your estimated 41kWh, but the water flow temperature would need to be 49C. So unless your heat emitter data was incorrect, I would expect your water flow temperature to be much higher than 40C.
If you have a suitable thermometer then try measuring the temperature.
@derek-m yes but that data came from the manufacturer about their performance based on lab testing. I can imagine in the real world the system is simply less efficient than they really claim. However I can test the temperature easily enough. There is a thermometer about... Somewhere
My estimate is based on the real world trend line from my results. Hopefully it should be more accurate, but the r of that data is something like 75, so it's not 100% accurate and certainly has error bars.
In the spreadsheet the required water flow temperature is calculated based upon your heat loss data, your estimated total heat output from the heat emitters and the indoor air temperature, it therefore is not dependent on the manufacturers data.
Posted by: @batalto@derek-m yes but that data came from the manufacturer about their performance based on lab testing. I can imagine in the real world the system is simply less efficient than they really claim. However I can test the temperature easily enough. There is a thermometer about... Somewhere
My estimate is based on the real world trend line from my results. Hopefully it should be more accurate, but the r of that data is something like 75, so it's not 100% accurate and certainly has error bars.
Hi Batalto,
I am not trying to prove anyone wrong. My objective in producing the spreadsheets, was for people to have a model, showing how their system could possibly perform if correctly installed and optimised. This would allow any large deviations from the anticipated performance to be identified and possibly investigated and rectified. People who suspect that their system is not operating efficiently, need something against which they can check the performance. I very much doubt that the vast majority of installers of domestic heating systems, fully understand how to accurately measure temperature, and where and how such measurements should be made to ensure maximum accuracy. If the control system is not receiving the correct information from the various sensors, then how can you expect it to control your system at its optimum.
The data published by manufacturers should have been obtained by testing in an independent testing facility, using calibrated standard test equipment, so will be more accurate than anything that can be achieve in normal operation.
Much of my career has been spent achieving the best accuracy in the measurement of numerous variables, particularly temperature, pressure flow and level. Whilst working on a new build power station in Pakistan, one of my task was to set up an on-site calibration facility, so I made an in depth study of Metrology, to enable me to ensure that the calibration of the site test equipment achieved the required level of accuracy.
@derek-m as ever I'm always appreciative of the knowledge on this forum. All I was trying to say is that all models are built on a range of assumptions. I'm finding that real world outcomes will give me the best idea of what the system is actually doing. That said I do have a meat thermometer. Perhaps I'll just test the inlet and outlet temperatures.
However I fear if the heat pump isn't accurately measuring it's temperatures what hope do I have!!!
Hi Batalto,
Your ASHP will still operate, even if the temperature measurements are not accurate. From the point of view of the heat energy output of the ASHP, and hence the determination of the COP value, the important parameters are the volumetric flow of the water, and the Delta T between the water flow temperature and the water return temperature. If these two temperature measurements are consistently offset from the true value by say 5C, then the heat energy output measurement should be reasonably accurate within the specified tolerances. Of course inaccuracies in the heat energy output measurement could occur if the Delta T varied due to variations in the readings rather than a true change in temperature.
I would suggest that you locate the temperature sensors in question, and see where and how they are installed. If they are just zip-tied to pipes, particularly plastic ones, then this could lead to inaccurate readings and also delay the reaction time, which could lead to further inaccuracies in heat energy output and COP measurement.
Posted by: @batalto5 degrees (average) outside and I am running at a heating COP of 3 so far, flow temperature of 40 degrees (average). My estimate is I'll use 41kw today to heating based on the formula trendline for my past performance.
I'm heading for about 40kWh today but average temp has been 3C (I think I'm a bit further north!). I've also been tinkering with the compensation curve and have overshot room temps again; it's 22-23C in the house at the moment. 😐
@kev-m we are now at 49kW used and the average ambient has dropped to 4°
Heat delivered 145kW COP: 2.95
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 402 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Flow rate discrepancy between ASHP and manifold
@bornagain I had considered that, but have air release ...
By AshRolls , 1 minute ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
Fair enough. I recommend quizzing him to get your mone...
By JamesPa , 52 minutes ago
-
RE: Solar panels on side of house to heat water
Yes, I have one in my Thermal Store. In the days befo...
By Transparent , 3 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@simonwig Thanks for the bump. Not sure why I didn't se...
By HCas , 4 hours ago
-
RE: Are Water Companies Delivering Bricks?!
...which in turn reminds me of a Thelwell cartoon I onc...
By Majordennisbloodnok , 4 hours ago
-
RE: Our journey through Octopus tariffs 2020-2025
I mentioned above "2025 move to Intelligent Go meant ...
By Tim441 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — thank you, that is useful information you hav...
By cathodeRay , 7 hours ago
-
RE: Grant Aerona circulation/system pump staying on
My parameters are: 42 00 = 0 (so the next three value...
By MikeFl , 7 hours ago
-
RE: Electricity price predictions
My apologies. I should've written "The number and dep...
By Transparent , 8 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
If it happens only when it gets cold then it maybe that...
By JamesPa , 8 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
Has anyone got past this screen to set up the integrati...
By AlanW1212 , 8 hours ago
-
RE: Heat Pump Training vs. Real-World Installation
@lucia have you discoveredfor how green each of our ene...
By Judith , 9 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
You seem to be on the right track... Installers are rec...
By Batpred , 17 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
there's a detect cycle setting (4200) on the old grant ...
By damonc , 19 hours ago
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman It's also worth highlighting that th...
By Lucia , 20 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
. It does but, unless there has been a firmware updat...
By JamesPa , 23 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Yesterday it was chilly and the cosy6 had a Cop of 4.3 ...
By AgentGeorge , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Same here! This month 187kw.
By Andris , 1 day ago
-
@jamespa Ah, they do indeed do firmware updates very oc...
By Toodles , 1 day ago