Posted by: @bobtskutter

You have a plate heat exchanger for system separation don't you? 

Yes, I do. I also have glycol in the primary circuit, and use a specific heat capacity of 4.05 for that (I noticed you use 4.2 ie pure water). The secondary circuit has quite a large volume, I haven't formally worked it out, but there is one huge K3 in the kitchen (15L?) plus several medium sized K3s and a few smaller ones, Perhaps (guessing here a bit) 100L in all just in the rads.

Posted by: @bobtskutter

With a plateHex i get 7.7kg ice, no hex 4kg.

Either way, that is a lot of ice. Credibility/sanity check?

 

Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
jamespipe
(@jamespipe)
Eminent Member Member
182 kWhs
Joined: 2 years ago
Posts: 13
 

Posted by: @transparent

It's mainly sold in Australia & NZ where they want cooling as well as heating.

Mitsubishi heat pumps works great in low temperatures. Requires minimal maintenance. Here in Victoria, they are offered under government rebate program.  

Heat pump installer at ipromiseaustralia.com.au


   
👍
1
ReplyQuote
Page 3 / 3
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Rob is here to help!

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security