ASHP and heating issues in new build house
@guthrie There are 3 houses on the development: different designs and floor area. All have a large dining room at rear.
Interesting point is the 220m3; 250m3 and 280m3 property have same 11kW heat pump. I have questioned that as my understanding is heat pump sizing is critical: it shouldn’t be too small/big.
@allyfish I asked builder for air leak test result; they said can’t find it. My understanding is they don’t need to test all houses on a development. I also asked for SAP report which states air permeability is 4.64 at 50Pa.
We did find areas of missing insulation in main bathroom and a bedroom which have dormer type windows above them. Those ceilings have since been under-drawn with thermal plasterboard. The infra-red survey is something I am considering.
@heacol I’m not sure the results from your Google search are correct. At -2C and 45C water temperatures the pump output is 10.6kW. Therefore, at the design temp of -3C, output will be less than 10.6kW; and definitely not 11kW. In a heat loss survey I had, I was advised that heat pump could only supply 96% of load. I believe regs say it must supply 100%.
Bathroom is 10m3; 25m3 with calculated heat loss (by heat pump supplier figures) of 643W. The column rad was fitted by someone who did not appreciate deltaT. The water going into the rad is about 39C and exits at 36C. Therefore average temp is 37.5C in rad. Design room temp is 22C. That gives deltaT of 15 which massively reduces the actual output of any rad.
It was the heat pump manufacturer/supplier who stated: “if we were to increase the size of the rad (bathroom) this would result in heat pump becoming overworked and running more defrost cycles, taking heat away from the primary circuit”. Is that not a tacit admission that heat pump is under-sized?
There appears to have no joined up thinking on heat pump and rad spec.
The set back on the thermostats is only 1 degree overnight; if there’s a heat demand it’s running 24/7.
@dreg1 . Thanks, I echo @heacol comments. A couple of thoughts you said two things that appear to me contradictory, that the thermostat on the landing controls temperature and that you are using weather comp. I may be wrong but usually it’s one or the other. If you are using weather comp, then it’s tweaking the curve and getting that right to give you the temperature you want. The Thermostats then are simply thermometers telling the temp but not dictating it. I’m not sure what your heatmisers are doing either. I had one silly thought but worth checking, as a modern property I would expect you don’t have chimneys, if not good, if you do are they insulated when not in use? Was thinking of the draughts you were getting.
@heacol I’m not sure the results from your Google search are correct. At -2C and 45C water temperatures the pump output is 10.6kW. Therefore, at the design temp of -3C, output will be less than 10.6kW; and definitely not 11kW. It’s the RASM 4VNE. In a heat loss survey I had, I was advised that heat pump could only supply 96% of load. I believe regs say it must supply 100%.
Bathroom is 10m3; 25m3 with calculated heat loss (by heat pump supplier figures) of 643W. The column rad was fitted by someone who did not appreciate deltaT. The water going into the rad is about 39C and exits at 36C. Therefore average temp is 37.5C in rad. Design room temp is 22C. That gives deltaT of 15 which massively reduces the actual output of any rad.
It was the heat pump manufacturer/supplier who stated: “if we were to increase the size of the rad (bathroom) this would result in heat pump becoming overworked and running more defrost cycles, taking heat away from the primary circuit”. Is that not a tacit admission that heat pump is under-sized?
There appears to have no joined up thinking on heat pump and rad spec.
The set back on the thermostats is only 1 degree overnight; if there’s a heat demand it’s running 24/7.
@terry1812 Thanks for that. My understanding is that the weather comp is dictating the output of the heat pump. I did have a heat pump service engineer tell me that I should not have any thermostats at all. As I have mentioned, I do not think the system has been designed particularly well. On the landing, where the thermostat is for the radiators, there's a rad with a TRV. That's bad design and I'm arranging for that to be corrected. We have a chimney in the lounge for a wood burner which is built into the wall [contemporary style]. I bung insulation in chimney when not in use.
Hi @dreg1 11, Kw or 10.6 is neither here nor there, it is considered to supply 100% of the load and will with ease, if your system is controlled properly, your 1-degree setback could effectively reduce the size of the unit to 9 Kw, or even less as when the setback kicks in, the heat pump switches off until the room thermostat calls for heat again, this couls take 2-3 hours, there for a capacity reduction of 13-14%. Your heat loss calculation is probably 15-20% greater than actual.
I think you answered you own question about your radiator in the bathroom.
The bathroom 643W is included within the 10.3 total load so icreasing the bathroom radiator, will have no effect on the heat pump.
Unfortunatly the design of the system is ver poor and not suited to a low temperature heat pump. I am sorry to say but your heat pump will only work correctly with a correctly designed system.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@dreg1 I am a cynic and believe that only the actual house which is tested will pass the building regs. The other will have considerably less care taken in build and will have draught faults. You already know the builder is sloppy that insulation was missed. You own air link test will cost about £300 and the engineer will keep it running while you find where the faults are.
Read the ashp basics turn up ALL stats to above the room temp you want. Remove ufh manifold controllers balance the flow for heat in each room. Get an extra radiator in the bathroom. Your system has been designed for gas and the guy working on it is still learning. The heat pump probably provides enough heat for the whole house but each room needs enough radiators, no amount of balancing will warm your bathroom without enough emission.
Thick curtains work wonders with lots of glass. https://protonsforbreakfast.wordpress.com/2024/12/18/the-u-value-of-curtains/ The curtains can double your insulation in effect.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
That’s good gives you more capacity. It made me think, have you checked what your total radiator capacity is, because regardless of the heat pump, if the radiators can’t give out the required 10.3kw you aren’t going to get to temperature. That goes for the UFH too, but I’ve no idea how you assess the capacity of UFH. @judith was spot on. Have you been keeping warm. I know it’s started to warm up, but we have had some very cold days.
- 22 Forums
- 2,037 Topics
- 44.4 K Posts
- 32 Online
- 3,250 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
Welcome to the forum@patch and well done for your under...
By Judith , 2 hours ago
-
RE: Air Source Heat Pump - Side Alley Suitability
@jamespa I used an assumed indoor temperature of 18C. I...
By Ad3628 , 4 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 4 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 8 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@editor Attached images of external insulation. Think...
By Dwynwen , 13 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 1 day ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 1 day ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 2 days ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 2 days ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 2 days ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 2 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 3 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 3 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 3 days ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 4 days ago