Another 17kw Grant Heat Pump - Advice Needed!
@allyfish Thank you, I've learnt so much more I'm the last week than the time the ashp were installed.
I'm assuming both pump adjustments would have to be like for like?
On a side note since the milder weather I'm finding the radiators warmer than ever.
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
@bretix we're all learning on these systems 🙂 I would set the secondary pump to full flow, always. If the pipe distance between your low loss header (white rectangular box in photos above) and the outdoor unit is quite short, and is larger 28mm pipe, a lower speed setting on the pump inside the ASHP might better balance. Most of the system restriction is on the secondary (radiator and house side) of the system, there's normally much less pressure loss between the low loss header and the ASHP. ASHPs need more flow than fired boilers, because they have a lower deltaT temperature difference between flow and return. For half the delta T you need to double the flow to transfer the same heat energy in kW.
There's not too much to worry about having too high a flow on the primary side, but best to balance primary and secondary if possible. What happens with the low loss header is that water can pass down through it, short circuiting the secondary flow and return. They are designed to do this for installations where the primary ASHP side flow is constant, such as a fixed speed primary pump, like as used in Grant's units, but the secondary side flow might vary due to on/off zoning controls or zone modulating controls like TRVs or UFH control valves. The ASHP sees a slightly higher return water temperature then, but it just modulates down in response. The opposite, having higher flow on the secondary side than the primary, is more of a problem, as the secondary pump starts recirculating return water up through the header, into the secondary flow pipe, and you see a temperature drop - the flow to the radiators on the secondary side is colder than the flow from the ASHP on the primary side. That's not so good, as all the heat energy generated by the ASHP is then not flowing into the emitters.
Check that weather compensation is enabled and set to something sensible, the Grant default settings are a good starting point.
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 52 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Who has a V2G EV installation
The EV wall chargers implement the checking for dno lim...
By Batpred , 4 hours ago
-
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 4 hours ago
-
RE: What valves to replace radbots?
Before answering the question definitively, its necessa...
By JamesPa , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@agentgeorge Where there’s muck … 😉 Toodles.
By Toodles , 8 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
@majordennisbloodnok Thanks for the welcome and yes I...
By Mark Nelson , 10 hours ago
-
So after playing about with DHW settings for a while I ...
By bontwoody , 10 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
I’ve got 5.4kW array, 9.6kWh battery, 5kW heat pump, EV...
By Gruff2001 , 13 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 15 hours ago
-
RE: Buying large amp bidirectional RCD and RCBO
The following diagram is taken from the Meter Operator'...
By Transparent , 15 hours ago
-
RE: British Gas Heat Pump Installation Complaint
@steelbadger That's great to know! Thanks for that reas...
By BGNO , 20 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@allyfish It was going so well with month after month s...
By Toodles , 1 day ago
-
RE: Electricity price predictions
As that's an energy issue, it would need the DESNZ to p...
By Transparent , 1 day ago
-
RE: UFH downstairs and radiators upstairs balancing question
Have you tried turning up the stat and turning down the...
By JamesPa , 1 day ago
-
-
RE: Mediation with RECC, what's your experience?
Welcome to the forums @treewizard and sorry to hear abo...
By Mars , 2 days ago
-
RE: New build installation query
That accounts for why you start with an overly-high DHW...
By Transparent , 2 days ago
-
RE: Daikin Altherma 3 / HomeAssistant
I would have thought that (instantaneous) power is a fa...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Alright, I concede that the Toyotas are, as you say a v...
By JamesPa , 2 days ago
-
RE: Is it mad to think there should be a minimum SCOP for UK heat pump installs?
Sadly I think it is mad. If the BUS is not granted for ...
By Judith , 2 days ago