Another 17kw Grant Heat Pump - Advice Needed!
@allyfish Thank you, I've learnt so much more I'm the last week than the time the ashp were installed.
I'm assuming both pump adjustments would have to be like for like?
On a side note since the milder weather I'm finding the radiators warmer than ever.
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
@bretix we're all learning on these systems 🙂 I would set the secondary pump to full flow, always. If the pipe distance between your low loss header (white rectangular box in photos above) and the outdoor unit is quite short, and is larger 28mm pipe, a lower speed setting on the pump inside the ASHP might better balance. Most of the system restriction is on the secondary (radiator and house side) of the system, there's normally much less pressure loss between the low loss header and the ASHP. ASHPs need more flow than fired boilers, because they have a lower deltaT temperature difference between flow and return. For half the delta T you need to double the flow to transfer the same heat energy in kW.
There's not too much to worry about having too high a flow on the primary side, but best to balance primary and secondary if possible. What happens with the low loss header is that water can pass down through it, short circuiting the secondary flow and return. They are designed to do this for installations where the primary ASHP side flow is constant, such as a fixed speed primary pump, like as used in Grant's units, but the secondary side flow might vary due to on/off zoning controls or zone modulating controls like TRVs or UFH control valves. The ASHP sees a slightly higher return water temperature then, but it just modulates down in response. The opposite, having higher flow on the secondary side than the primary, is more of a problem, as the secondary pump starts recirculating return water up through the header, into the secondary flow pipe, and you see a temperature drop - the flow to the radiators on the secondary side is colder than the flow from the ASHP on the primary side. That's not so good, as all the heat energy generated by the ASHP is then not flowing into the emitters.
Check that weather compensation is enabled and set to something sensible, the Grant default settings are a good starting point.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 146 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
In mild conditions, yes I turn the heating off. This i...
By trebor12345 , 3 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
Hi HenriWe were puzzled by a thread being moved into he...
By Sheriff Fatman , 4 hours ago
-
RE: Electricity price predictions
@transparent The Totnes Society seems to operative l...
By Batpred , 5 hours ago
-
RE: Grant Aerona circulation/system pump staying on
My AERONA 3 circulation pump runs constantly whatever t...
By damonc , 6 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Thanks, @sheriff-fatman. Happy for you to search any po...
By Majordennisbloodnok , 8 hours ago
-
Thanks, @cathoderay. I was aware of some changes to ...
By Majordennisbloodnok , 9 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
It's buried within what has become my ongoing post-inst...
By Sheriff Fatman , 13 hours ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 17 hours ago
-
This is what I answered, I really have no hope: "......
By Batpred , 1 day ago
-
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj oh yes they offer Daikin 8kW, they tried to fo...
By AgentGeorge , 1 day ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Good point! Just in case anyone re...
By Batpred , 1 day ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 It would be very useful if you could tell us...
By trebor12345 , 1 day ago
-
RE: Benefits of an extra horizontal loop for GSHP
A correct sized collector is all you need. Saying this,...
By greenlight , 1 day ago
-
RE: Grant Aerona Short Cycling
@mikefl, thanks for sharing your operating data, very i...
By Steam Powered , 1 day ago
-
-
RE: Here is my heat pump installation with questionable COP in Italy
@jamespa Sorry for the late reply, I apologize for the ...
By materox345 , 2 days ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@editor Yes BUT that was 3 years ago installed in Janua...
By rob heatpump bob , 2 days ago
-
Thanks for your response. I have UFH downstairs and ...
By GeorgeA , 2 days ago