Another 17kw Grant Heat Pump - Advice Needed!
@allyfish Thank you, I've learnt so much more I'm the last week than the time the ashp were installed.
I'm assuming both pump adjustments would have to be like for like?
On a side note since the milder weather I'm finding the radiators warmer than ever.
2 10kw Grant Aerona3
Heat loss calc 16.5 kw @ -2.8 degrees
4.32 PV
@bretix we're all learning on these systems 🙂 I would set the secondary pump to full flow, always. If the pipe distance between your low loss header (white rectangular box in photos above) and the outdoor unit is quite short, and is larger 28mm pipe, a lower speed setting on the pump inside the ASHP might better balance. Most of the system restriction is on the secondary (radiator and house side) of the system, there's normally much less pressure loss between the low loss header and the ASHP. ASHPs need more flow than fired boilers, because they have a lower deltaT temperature difference between flow and return. For half the delta T you need to double the flow to transfer the same heat energy in kW.
There's not too much to worry about having too high a flow on the primary side, but best to balance primary and secondary if possible. What happens with the low loss header is that water can pass down through it, short circuiting the secondary flow and return. They are designed to do this for installations where the primary ASHP side flow is constant, such as a fixed speed primary pump, like as used in Grant's units, but the secondary side flow might vary due to on/off zoning controls or zone modulating controls like TRVs or UFH control valves. The ASHP sees a slightly higher return water temperature then, but it just modulates down in response. The opposite, having higher flow on the secondary side than the primary, is more of a problem, as the secondary pump starts recirculating return water up through the header, into the secondary flow pipe, and you see a temperature drop - the flow to the radiators on the secondary side is colder than the flow from the ASHP on the primary side. That's not so good, as all the heat energy generated by the ASHP is then not flowing into the emitters.
Check that weather compensation is enabled and set to something sensible, the Grant default settings are a good starting point.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 50 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
I don’t think he does, because he's a very arrogant ind...
By Mars , 9 minutes ago
-
@rhh1, got a reply from Daikin. There brand manager was...
By Mars , 14 minutes ago
-
MCS certificate SCOP vs real-world performance
Every MCS-accredited installation comes with a certific...
By Mars , 22 minutes ago
-
RE: Mitsu PAR-WT60R Wireless Controller - options
@abernyte Thank you for passing on your experience and ...
By DavidAlgarve , 1 hour ago
-
RE: Powerwall 3 or Myenergi or something else?
Yes I was thinking of outdoor, IP65 batteries with buil...
By Temperature_Gradient , 2 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Water pump will certainly make a hum (which could conce...
By JamesPa , 5 hours ago
-
@jamespa Thanks. Yeah any adjustments Ive made at pr...
By cliffhanger , 5 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 4 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago