It's great that Aira continue to add features to the app. Our 8kW efficiency figures are:
Month | Electric Consumption | Heat Delivered | COP |
October 24 | 403 | 1512 | 3.75 |
November 24 | 654 | 2409 | 3.68 |
December 24 | 713 | 2875 | 4.03 |
Has anyone got any information on how/why they justify a buffer tank in their install? Everyone seems really happy with the install and running so I assume the buffer isn't an issue but given the general feeling that buffer tanks shouldn't be used by default this is the one piece of their installation that I find a bit strange.
@andrewj Our installers fitted am LLH; their justification for fitting this efficiency reduction is that ‘It ensures that the heat pump sees a constant load and the actual secondary circuit flow rate is less critical making it much easier to achieve a constant Delta T.’ Not sure that this is the full story but suspect that, as mentioned on this hub numerous times, it reduces the chance of engineer call-outs. 😒 Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles So that would imply what I thought (perhaps I'm too cynical): it is put in to separate problem responsibility between the heat pump and the secondary circuit. Although in the case of Aira, who install both sides and presumably are responsible for warranting both, I don't think that counts for much (as opposed to, say, a Vaillant heat pump and a local installer.) Is it much of an efficiency hit or do they have it technically sussed?
@andrewj In my case, I would put any shortcomings down to the installers but fortunately for us, our system is working very well. I took the measure of optimising the things that the installers run out of time to do😉 for myself. I let them roughtly balance the radiators during a very warm end of day in February (before they all went off home or to the pub or whatever) as I knew there was no way the system would be optimised that afternoon!
I also played with the LWT and at that time, I had to let the MMI controller do what it could to run well. I gradually improved the settings for the WC and then come the following autumn, I had Homely smart control added.
In between times, I bought 4 of the temperature probes and ‘calibrated’ them, (I bundled all the probes together, let them stabilise overnight and noted the disparity in the 4 sets of readings). I taped the probes on all four pipes entering and leaving the LLH and covered each with a few layers of insulating aluminium coated sheet. I then gradually adjusted the secondary pump speed to achieve minimum disparity between the flow in and flow out to the pump - and likewise between the return flow and the LLH return to the heat pump circuit. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@andrewj Well, not everyone. My experience would probably be the one anti heat pump brigade would be keen to highlight. The product is great, the installer who came is really good. But, I don't think Aira have their operations under control.
It's day 9 and my installation is still ongoing. Not because it's a complex installation, but rather because they decided to again send only one engineer on-site this week. With a three storey house and 15 radiators, the one engineer on-site can only run around so much to check for leaks. There was a massive leak in my study and just missed the electrical sockets by sheer luck. It could have been a total disaster. I am having to help the installer with lifting and positioning a large radiator as there's no way he would be able to lift a 70 kg radiator and install by himself. And to top it all, they sent me an invoice to pay for a system that's not even commissioned!
16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
Day nine gone, the heat pump is still not commissioned. There's a sensor problem and there's no electrician onsite to help the lead engineer. Now, they won't come back until Thursday and won't be commissioned until day 11.
Not sure what options are there to explore, complain to MCS, trading standards, Ofgem. Personally, I shouldn't have fallen for the 15 year warranty and should have gone with Octopus or Heat Geek. If their service is as bad as the installation experience, the warranty is not worth the hassle.
16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
@chandykris Sounds like a pretty poor state of affairs. Hopefully once it is in and commissioned it will work fine and this will drift into a bad memory lost in the mists of time. I now have to decide between Octopus or Heat Geek for an install - I think I'll leave Aira and not complicate it further. I don't have all the details yet but I think the juggle will be between cost, confidence and heat pump model!
Thanks @andrewj. Hope my bad experience didn't put you off. Others in the forum have had good experiences, so maybe mine is just an odd one out.
I should have done what Toodles and others had suggested. Lower the flow temperature post installation. Let Octopus design the system at 50 degrees flow temperature, but upgrade the radiators myself at an extra cost and then lower the flow temperature. Well, hindsight is a wonderful thing!
16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
@chandykris sorry to hear this, I hope that progress picks up and Aira will sort your system.
Aira managed to send an engineer at 5:30 pm today and it took a while, but thank Higgs Boson, we have heat! It was up and stunning around 8:30 pm starting with hot water. Then heating kicked off and the house is slowly heating up. Really surprised how quiet the unit is, I can hardly hear it working from the sun room just 1.5m away.
Still loads to do, lagging everything, sorting out some joints, cleaning up everywhere, close the boiler flue hole. But, at least the heat pump is commissioned. Like Andrew said, maybe this will just be a bad memory in the mist of time.
16 * 435 watts PV
6.6 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
-
Heat Pump Paradox: The Industry's Adoption Divide
12 months ago
-
Not So Hot: Too Many Subpar Heat Pump Installations in the UK
1 year ago
-
The Most Popular Heat Pump in the UK: Is It In Your Home?
1 year ago
-
Heat Pumps - An Expensive Folly?
2 years ago
- 22 Forums
- 2,032 Topics
- 44.3 K Posts
- 25 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 hours ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
Welcome to the forums. It’s clear that you’ve taken t...
By Mars , 3 hours ago
-
RE: help sizing rads based on room by room heat loss
By JamesPa , 4 hours ago
-
Hi Thanks for the reply, the walls are being constru...
By Fingers , 5 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 6 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 10 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 10 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 10 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 10 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 10 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 15 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 17 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 17 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 20 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 2 days ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 3 days ago