Advice please on controls for my Daikin 14kw 3H HT heat pump with 3H HT W internal unit and Megaflo cylinder
@johnmo Hello johnmo. The radiators used to go cold and when I checked the indoor unit the panel showed an error code. Before they did more work on it around last Christmas there were sometimes two errors, and it was difficult to get it to start on a couple of very cold mornings. After that it was usually a flow sensor malfunction code. Pressing reset usually fixed it for a while, but it did sometimes cut out 5 times a day. After they removed the extra circulation pump at the end of May this year there were no more errors and I have never had to re-set it.
That's a low flow condition. Do you have lots of zones (thermostats) if so what's happening is the zones are closing off, and the circulation pump cannot get enough water through the system.
@johnmo Hello again johnmo. That's no longer a problem, as removing the unnecessary pump has now fixed it. My question was whether the plumber was correct in saying that I don't need a weather compensation curve, and the advice that I have had on here so far suggests that I do. The time switch, that he set for twice a day like a gas boiler, and the thermostat inside the front door controlling the whole system also don't seem to be very sophisticated.
Posted by: @joninorkney@johnmo Hello again johnmo. That's no longer a problem, as removing the unnecessary pump has now fixed it. My question was whether the plumber was correct in saying that I don't need a weather compensation curve, and the advice that I have had on here so far suggests that I do. The time switch, that he set for twice a day like a gas boiler, and the thermostat inside the front door controlling the whole system also don't seem to be very sophisticated.
Low and slow is best, running like a gas boiler you will need a second mortgage. So weather compensation is best
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 66 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
Yes, one outside in a sheltered place (mine was in a co...
By cathodeRay , 43 minutes ago
-
Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
We’re pleased to announce that Havenwise are now joinin...
By Mars , 53 minutes ago
-
RE: COP is not the only measure of efficiency
I am a little sceptical of this, not least because, in ...
By jamespetts , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@ashp-bobba Well done for stepping in where most would ...
By JamesPa , 4 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have automated this decision. I have a heat pump with...
By jamespetts , 12 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 13 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 14 hours ago
-
RE: Buffers, hot water and cooling
I agree it seems like a lot of work particularly as its...
By JamesPa , 14 hours ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 18 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 19 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 22 hours ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 23 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 23 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 2 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 2 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 2 days ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 3 days ago