Posted by: @batalto

I believe our annual kw/m2 is quite good in the overall scheme of things

I'm sure that is right. Presumably your recent large extension is well insulated, and you can enjoy the benefits of that.

Posted by: @iaack

One question if I may, where was your old oil boiler located; within you home or in an outbuilding?

Inside. That made it itself an internal heat emitter, but it also sucked in cold air for combustion, so what the net heat contribution was after allowing for both factors is unclear.

Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@derek-m)
Illustrious Member Moderator
13722 kWhs
Veteran Expert
Joined: 3 years ago
Posts: 4165
 

Posted by: @batalto

@cathoderay I believe our annual kw/m2 is quite good in the overall scheme of things

Things do stay the same. My wife still hates the cold. 🙄 

 


   
ReplyQuote
(@iaack)
Eminent Member Member
409 kWhs
Joined: 1 year ago
Posts: 20
 

You suggested a figure of 80% for the efficiency of you oil boiler for converting the fuel to hot water, where does the other 20% of the energy goes, not all up the flue surely. I would bet another 4 to 6% goes to heating the surrounding area. I would also suggest that 4 to 6% of the heat produced by your heat pump and external pipework is also lost to its surroundings, however as its running 24 hours a day, that is not insignificant. Additionally, the heat lost during defrost cycles needs to be accounted for. 

Not switching off the heating at night will mean the building fabric will continue to loose heat at a higher rate and in one direction (outwards) whereas if you switch your heating off the overall heat lost is reduced as heat will now also flow from the building fabric back into your home, the building fabric will cool, the delta t with the outside will reduce and the heat lost to the surroundings reduces, thus improving overall running costs. I don't think its so much of a conundrum, just a few things that all add up to be significant at the end of the day.


   
ReplyQuote



(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
 

@iaack my boiler actually told me the efficiency on the screen - it was 68% and it was a new boiler (only a few years old). Boiler efficiency stats are lies in my view. The packaging claimed over 90%

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
6909 kWhs
Joined: 2 years ago
Posts: 1391
Topic starter  

Posted by: @iaack

I don't think its so much of a conundrum, just a few things that all add up to be significant at the end of the day.

It still was a conundrum when I wrote the original post, but now we may be getting nearer to a solution, which was the whole point of writing the post!

You may well be right (that just a few things do add up), but it is quite a big difference, we are mostly looking 100%+ differences, not just a few percent here or there. Assuming very level conditions, which of course usually don't happen, 24 hour running might be expected to use 50% more total energy than running with an 8 hour overnight setback. But it's complicated by any boost added after the setback, needed to achieve the recovery after the setback. But 50% extra is not the same as 100%+ extra.    

The night setback or rather the lack of it because the heat pump can't recover in a reasonable time is also a running sore which has come up many times. No one appears to be absolutely sure, but in my own mind I have persuaded myself that a boost after a setback will always use less total energy than keeping the heating on 24 hours a day, but there is no easy way to set up that boost on a Midea unit, so I haven't been able to test my theory.

@batalto - indeed. Instead of it being the snake oil salesmen at work, it is the snake gas salesmen at work, and we all know snake gas is even worse than snake oil.

Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@iaack)
Eminent Member Member
409 kWhs
Joined: 1 year ago
Posts: 20
 

@batalto was your boiler located in the middle of your garden, or in your kitchen, utility room or loft. Your missing my point, whatever the boiler efficiency is, its about coversion of fuel energy to hot water + lost energy to surroundings. Where the surroundings are does matter in these circumstances.


   
ReplyQuote
(@batalto)
Famed Member Member
3655 kWhs
Joined: 3 years ago
Posts: 1091
 

@iaack no. It's in the same cupboard as the batteries. Nice and central and warm in the house.

12kW Midea ASHP - 8.4kw solar - 29kWh batteries
262m2 house in Hampshire
Current weather compensation: 47@-2 and 31@17
My current performance can be found - HERE
Heat pump calculator spreadsheet - HERE


   
ReplyQuote