Posted by: @cathoderayPosted by: @hughfthe defrost requirement is quite interesting
The defrost cycles appear to be a particular nuisance, because they kick in, as I understand it, at around 5 degrees ambient (and stop at minus something, no longer needed for a reason I can't remember) but the key point is they reduce output when it is most needed. Very crudely, again as I understand it, the unit becomes a cooling unit, sucking heat from the house to achieve the defrost. Clever, or what? Again, it is not always clear whether manufacturers include the defrost effect in their output data. If you plot output by ambient, and see a dip around 0 to 5 degrees ambient, that is most likely the defrost cycles kicking in.
What's odd about that TUV (TUV = ?) table is that there is only one column showing a defrost cycle. But it is also the column with the longest data collection period, 4 hours vs 2 hours for the rest. If my 5 degree threshold is correct, the A7 and A12 tests wouldn't have defrost cycles anyway. One way of getting rid of embarrassing defrost effects at lower ambients would be to run tests that last less than the interval between defrost cycles.
I wonder how many installers tell customers that their ASHP will periodically turn itself into a fridge unit in colder weather.
I thought it impressive that the only condition where a defrost cycle was required, was pushing 55 deg water out at -10deg air temp, after running for 4 hrs. And then it only defrosted once.
It’s all dependent on the humidity of the air of course.
Btw, on the subject of Midea, I got hold of their official (not rewritten by GH) installation manual and all the rating charts are in there, pages of them in fact 🙂
And GH has mentioned that they might sell me one, so I’ll give them a bell later and see what the story is about that.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
I will bow to the experts, but I thought defrost cycles were most needed between plus five degrees and minus whatever, and a unit that didn't defrost at those ambients would sooner or later get into trouble. The main question is whether a manufacturer's output data includes defrost cycle effects.
The official Midea documentation ('Engineering Data') came up earlier in the thread, and yes it is all there, pages of it. But does it say whether those capacity (output) tables do or don't include defrost effects? It don't think it does. You have to plot the data, and make a guess.
I sometimes think GH has a rather optimistic view of Freedom, based on what he did when he was there, rather than how they behave now. They very clearly told me they considered themselves B2B, and weren't prepared to talk to me directly. Extremely short-sighted in this day and age. It will be very interesting to hear what your experience is when you get in touch with them.
Midea 14kW (for now...) ASHP heating both building and DHW
This is (I think) a defrost cycle. The unit sucks warm water back to melt the ice so the flow temp drops. It then has to use energy to warm it up again before settling back down. Because I'm using weather compensation to control things and not thermostats, the house will get a tiny bit cooler when this happens and then warm up again as and when. If I were using thermostats, I think the additional power used would be more. I think the increase in outdoor temp is probably the defrosting warming things up near the sensor.
This was at 3C ambient. The Ecodan databook includes defrost in all its outputs at 2C. (P60 or thereabouts in the link I posted earlier)
Posted by: @cathoderayI will bow to the experts, but I thought defrost cycles were most needed between plus five degrees and minus whatever, and a unit that didn't defrost at those ambients would sooner or later get into trouble. The main question is whether a manufacturer's output data includes defrost cycle effects.
The official Midea documentation ('Engineering Data') came up earlier in the thread, and yes it is all there, pages of it. But does it say whether those capacity (output) tables do or don't include defrost effects? It don't think it does. You have to plot the data, and make a guess.
I sometimes think GH has a rather optimistic view of Freedom, based on what he did when he was there, rather than how they behave now. They very clearly told me they considered themselves B2B, and weren't prepared to talk to me directly. Extremely short-sighted in this day and age. It will be very interesting to hear what your experience is when you get in touch with them.
Defrost is purely a function of evaporator size and airflow. Units need to fit in small spaces, so manufacturers will size the evap coils to be 'large enough' without being massive. Ideally you'd buy a unit twice the size as you need, so that the airflow required is much less (for a given heat output) but this brings the issue of modulation range. A large unit won't modulate down low enough when the heat demand is low and this will result in cycling.
The Midea units, with 16kW on a single fan are probably (just a guess here) going to defrost more than a unit with double height evap coil and twin fans.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @cathoderayI sometimes think GH has a rather optimistic view of Freedom, based on what he did when he was there, rather than how they behave now. They very clearly told me they considered themselves B2B, and weren't prepared to talk to me directly. Extremely short-sighted in this day and age. It will be very interesting to hear what your experience is when you get in touch with them.
Email sent, asking for price and availability of a 10kW and a handful of bits from their price list (that I probably could get from screwfix, but can't be bothered)
EDIT: Email back, they won't sell me one, but they have offered to point me to the plumbers merchants who stock one if I want to self install.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@cathoderay to be fair, many many business are not B2C and the reason is exactly what you are doing. They don't want the cost or time to deal with end users so they provide a product to end sellers so they can deal with the customers. As any business would say, the worst part of any business is the customers and things would be much easier without them
Posted by: @hughfthey have offered to point me to the plumbers merchants who stock one if I want to self install
The thing i would be wary of is having no access to technical support. This forum is excellent, but they maybe something only Midea/Freedom know (particular to the unit) and i doubt a plumbers merchant will know or want to get involved.
Posted by: @bataltothings would be much easier without them
But then there wouldn't be a business either! I do understand the B2B thinking, keep the punters at arms length, but as a punter it is very frustrating. There are many many business who could adopt the B2B model, but who choose to have publicly accessible technical departments, and when it works, it can work very well.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @hughfthey have offered to point me to the plumbers merchants who stock one if I want to self install
The thing i would be wary of is having no access to technical support. This forum is excellent, but they maybe something only Midea/Freedom know (particular to the unit) and i doubt a plumbers merchant will know or want to get involved.
Posted by: @bataltothings would be much easier without them
But then there wouldn't be a business either! I do understand the B2B thinking, keep the punters at arms length, but as a punter it is very frustrating. There are many many business who could adopt the B2B model, but who choose to have publicly accessible technical departments, and when it works, it can work very well.
The fact they won’t sell me one direct and only want me to buy through their merchants has struck them off my list. Plus, the unit is too wide. I’m going to stick with cool energy I think. They’re super helpful on the phone and their 9kW unit is a slightly better size for our space.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @hughfThe fact they won’t sell me one direct and only want me to buy through their merchants has struck them off my list.
Freedom will probably if asked say losing one sale doesn't matter, but they haven't just lost the sale, they have also lost some general goodwill. Obstructionist policies never go down well with punters.
By the bye, the form factor, wider rather than taller, was one of the main reasons I chose the Midea unit, because my property is listed (which means you need LBC and because of that you also need planning permission), and being low profile lessens the visual impact of what is at the end of the day a large steel box with a big grill over a fan on the front. Even if the property wasn't listed, I might well have still chosen the Midea unit because it is low profile, after all, the building is the same whether listed or not. But horses for courses, of course.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayPosted by: @hughfThe fact they won’t sell me one direct and only want me to buy through their merchants has struck them off my list.
Freedom will probably if asked say losing one sale doesn't matter, but they haven't just lost the sale, they have also lost some general goodwill. Obstructionist policies never go down well with punters.
Exactly - I'm pretty active over on buildhub where I've just talked up the Freedom spreadsheet for someone who is doing their own design for their apartment. I said 'don't bother choosing a Midea, they won't sell you one even if it was suitable'...
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.

Posted by: @hughfPosted by: @cathoderayPosted by: @hughfThe fact they won’t sell me one direct and only want me to buy through their merchants has struck them off my list.
Freedom will probably if asked say losing one sale doesn't matter, but they haven't just lost the sale, they have also lost some general goodwill. Obstructionist policies never go down well with punters.
Exactly - I'm pretty active over on buildhub where I've just talked up the Freedom spreadsheet for someone who is doing their own design for their apartment. I said 'don't bother choosing a Midea, they won't sell you one even if it was suitable'...
In fairness, it's probably a contractual thing. My guess is that, with Midea trying to gain market share against the likes of Daikin, Mitsubishi, Vaillant and LG, competing means offering some significant incentives to installers to choose Midea by preference. One of those will likely be a contractual agreement stating Midea won't compete directly with their own installers for customers.
Also, in fairness, anyone building their own house will still likely be buying their materials from a builder's merchant rather than approaching the brick, tile or cement manufacturer directly, so buying through a distribution network is a pretty well established sales model and hardly deliberately obstructionist. Not that I'm defending Midea or any other heat pump manufacturer; I just prefer to pick my fights and there are far more questionable antics the manufacturers get up to than not selling direct to consumers.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
@majordennisbloodnok exactly. Very few things you actually buy direct from the supplier. I'm surprised people take it so personally.
- 21 Forums
- 1,974 Topics
- 43 K Posts
- 55 Online
- 2,304 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@drew-pa that’s one of the cheaper ones so far.
By Mars , 29 minutes ago
-
Grant Aerona fine tuning advice needed
Looking to fine tune my settings. Currently running ab...
By Stopbar , 2 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@adrian it does look like they’ve updated their outgoin...
By Arundalep , 3 hours ago
-
RE: DHW temp Samsung AE120RXYDEG 12kw ASHP with Gen 6 controller
I agree, it doesn't look like that was the culprit, but...
By Old_Scientist , 5 hours ago
-
If you think your heat loss is between 4.5 and 8.5, the...
By JamesPa , 5 hours ago
-
RE: Heat Pump Sizing & Installation Costs
1970s 4-bed detached house approx 168 sq.m internal are...
By JohnR , 10 hours ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
Away at present. Hence the delay. Will get back asap. ...
By cliffhanger , 14 hours ago
-
RE: Setback savings - fact or fiction?
The lower the DT the higher the flow rate. The lower ...
By BobTSkutter , 1 day ago
-
RE: New kitchen with no walls – will fan coil units work?
Thanks. That explains the strangely-shaped 'feet' (loo...
By IanMK13 , 1 day ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
I’ve updated Bodge Buster for 2025 to empower homeowner...
By Mars , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Aira, the Swedish, end to end manufacturer, system desi...
By KevinPotts , 2 days ago
-
Unfortunately for your argument the best performing Dai...
By RobS , 2 days ago
-
RE: Grant ASHP not reaching target temperatures
@mikefl Thank you. I’m not sure how to do these checks ...
By Hillswick , 2 days ago
-
RE: Transforming a Derbyshire Property into an Energy-Efficient Haven
@carpenterstation That's helpful, thank you. The de...
By Morgan , 2 days ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa Homely does address many of these issues, but ...
By Arundalep , 2 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
There is absolutely nothing wrong with buffer tanks in ...
By JamesPa , 3 days ago
-
RE: Replacing knackered oil boiler with ASHP - Perthshire
@abernyte thanks tbh I was more thinking about bolsteri...
By DowallyDrifter , 3 days ago
-
RE: Battery storage to run Heat Pump.
@jeff The government are quite happy for the network ...
By Lucia , 3 days ago
-
RE: Adjusting 6kW Daikin's Weather Compensation Curve
@jamespa I'm grateful for your advice.
By Ubert767 , 3 days ago
-
RE: Say hello and introduce yourself
@carrownisky where are you based? Would you like me con...
By Mars , 3 days ago
Latest Topics
-
Grant Aerona fine tuning advice needed
By Stopbar 2 hours ago
-
Adjusting 6kW Daikin's Weather Compensation Curve
By Ubert767 3 days ago
-
Should I make my radiators smaller?
By Scalextrix 4 days ago
-
Daikin Heat Pump Cycling Frequency?
By Ubert767 5 days ago
-
Battery storage to run Heat Pump.
By Broadsman 6 days ago