Below is an extract from the MIM-E03CN manual, which is the recommended controller for use with your heat pump.
Do you only have the one water pump?
Is your system still short cycling at the same frequency?
One possible problem could be incorrect settings within the controller. If possible go into the installer menu and make a note of any parameter settings that you can find, and then post the results.
@derek-m I have two pumps I believe. You can see both pumps in this pic.Â
I am still getting short cycling, yes.Â
What settings do you mean, sorry?Â
It's entirely possible the settings are incorrect, I've had to wing it to get as far as I have.Â
What is the temperature setting of the two thermostats, and what is their make and model?
@derek-m okay, I'm not at home at the moment. I'll do it later and report back. I've made various adjustment to water law which is Samsung for WC. The temp in the house is nice and the COP is acceptable too. Just the cycling. Thanks again
The Joule Samsung instructions are available on line, they don’t use a PWM pump. They have a separate interface PCB that comes after the MIM. I’ll see if I can find a link.
I would be inclined to get the installer to wire/plumb it up as per the Midsummer wholesale instructions that give details on how to fit a PWM pump and use the Samsung controller as the room stat.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 34 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
It's the UK Government who want to set your heating sch...
By Transparent , 1 hour ago
-
RE: Humming sound on new install.
@jamespa this is the third attempt to sort the flexis a...
By AdamK , 1 hour ago
-
I agree with @jamespa. If you are not using the tank ...
By Old_Scientist , 2 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 16 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 19 hours ago
-
I didn't want to say that, bus since you have said it n...
By JamesPa , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
Mostly, I think, but with some caveats. I set the TI...
By cathodeRay , 22 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 2 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 2 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 2 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 2 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 3 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 3 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 4 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 4 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 4 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 4 days ago