Still cycling at 8 mins on 20 seconds off with room stats at 25 degrees. Water outlet (flow temp I assume) is up a couple of degrees but the outside temp has also dropped tonight.Â
Posted by: @craig1980Still cycling at 8 mins on 20 seconds off with room stats at 25 degrees. Water outlet (flow temp I assume) is up a couple of degrees but the outside temp has also dropped tonight.Â
Hi Craig,
To try to find the root cause of the problem, it is necessary to observe how your system is actually operating, and compare this against how we think the system should be operating.
Below are a few checks and observations to make.
Carefully time how long the system is 'on' and how long the system if 'off', ideally to the nearest second. We can then see if there is any variations.
Record the changes in the readings displayed on the controller for LWT, outdoor temperature, and any other temperature and flow readings that are available. Pay particular attention to changes from just before the heat pump stops, during the 20 second shutdown period, and after the heat pump restarts.
Â
I have attached a copy of a manual which details all the various parameter settings, which are listed from page 24 onwards.
I would suggest that you go through your system and make a note of all the values.
I have my doubts over this section.Â
Â
Could this be set incorrectly?Â
Its set the same for this and external thermostat application #1 (floor) and #2 (FCU).
I have no UFH so is the "floor" part irrelevant or have the set the zone 1 and 2 up as "floor" and "FCU" respectively?Â
I've also just changed the 2041 Heating water law for auto mode to WL2-FCU from WL1-Floor. Is that the right thing to do as I don't have UFH?Â
My idea was to first gather the information, then give it a close dose of inspection, and then try to decide what needs to be changed.
Based upon normal operation, I would expect your system to perform in the following manner when in WC mode.
The outdoor air temperature sensor measures the ambient air temperature and conveys this reading to the controller. The controller calculates the required LWT. If either of the room thermostats are calling for heat, and the actual LWT is below the calculated value, by a specified margin, then the heat pump will start operation.
When the actual LWT exceeds the calculated value, by a specified margin, the heat pump will stop operation. When the actual LWT falls below the calculated value, plus the specified margin, the heat pump should restart. This process will probably continue during milder ambient temperatures.
What values did you record during the monitoring process?
Â
Posted by: @craig1980@derek-m I'm just doing the monitoring now.Â
Where would I find the LWT? I'm assuming that's leaving water temp? I have my thermometer nowÂ
The LWT is what is labelled Current Water Outlet on the 'normal' display on the controller.
I assume that your heat pump is still switching back on after only 20 seconds?
The objective of the testing, is to see what is happening to the various temperatures around your heat, as it stops and then restarts. Since the heat pump should not normally restart after only 20 seconds shutdown, something must be causing it to do so.
Â
Images of all figures and settings on the field settings manual. I hope it makes sense?
It is on for exactly 7 mins 58 second and off for exactly 20 seconds.Â
Water outlet 24.8 turns off 24.8 turns on at 21.5 indoor temp on wired remote but 18.5 on room stats confirmed by independent stats. Climbs to 27.2 at the middle of the cycle and drops back to 24.8 by the end.Â
Just checked flow and return temps on rad closest to UVC and it's 25.2 -22.6
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 38 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 7 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Yes thats the whole point of the flexis as regards tran...
By JamesPa , 7 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 7 hours ago
-
Mitsu PAR-WT60R Wireless Controller - options
I hope I have satisfactorily installed the above wirele...
By DavidAlgarve , 9 hours ago
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 14 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 1 day ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 1 day ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 1 day ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago