Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regarding the use of RCBOs to connect PV inverters or storage batteries.
This is not yet part of the IET Electrical Wiring Regulations, but it is sufficiently serious that an amendment is being expedited.
Overview: household electrical circuits are wired from a Consumer Unit which contains a number of trips.
Most trips are there to prevent excessive current being passed through wires/cables. Those are MCBs (Miniature Circuit Breakers).
It is common for a consumer unit to have one or more RCDs (Residual Current Detectors).
These compare the outgoing current on the Live wire, with that being returned on the Neutral.
If there is an imbalance, the contacts will open to prevent fire or electric shock to someone who has touched a live cable.
Increasingly, electricians are fitting RCBOs for individual power circuits.
These combine the functions of an MCB and RCD.
They will open the contacts either for over-current, or because current is leaking away somewhere.
If a single-circuit RCBO trips out, then at least the lights remain on so you can see what's gone wrong!
RCDs and RCBOs both have a test button.
This should be pressed periodically to check that it will open the contacts to protect against electric shock
When solar panels or storage batteries are installed, it is not mandatory that the circuit is supplied from an RCBO. An MCB is sufficient.
However, many installers do use an RCBO to provide an extra level of safety for when it might be necessary for an inverter to undergo maintenance.
Most Solar Inverters and Storage Batteries are "Grid tied".
They export to the mains supply through the same wires which connect them to the consumer unit.
A grid-tied inverter will have a G98 certificate, and requires permission from the regional DNO to install it.
This common arrangement means that electricity will pass through the RCBO in either direction.
The RCBO contains a small amount of electronics to handle the current sensing.
When there is a fault (either over-current or earth-leakage) a solonoid is energised (switched on), which opens the contacts.
If the RCBO was on a normal power circuit, opening the contacts would remove power from the electronics.
The trip would remain open until the lever was manually moved, and the solonoid would no longer be powered-on.
But if there is power still being applied in the reverse direction by an inverter or storage battery, when the contacts open, the solonoid remains energised.
Such a small solonoid will overheat and burn out.
The circuit can still be re-powered using the lever, but it will no longer be able to protect against electric shock.
The home owner won't know that.
The solution is to use a an RCBO specifically designed for bi-directional use.
A bi-directional RCBO has a third pair of contacts.
When the solonoid operates to open the trip, that 3rd contact set removes power from the electronics, and the solonoid coil is de-energised, preventing burn-out.
How can you tell if an RCBO is bi-directional?
Most RCBOs have arrows to show the direction of current, or have a label which denotes Supply and Load terminals.
A Bi-directional RCBO will not be marked for Supply and Load.
It may also have a set of arrows pointing in both directions.
If an RCBO isn't marked as being bi-directional, then it isn't.
The IET Wiring Regulations aren't retrospective.
When the amendment is released which specifies the need for a bi-directional RCBO, there will still be many thousands of installations which appear to have an operational RCBO, but it will only offer protection against over-current. It won't be acting to prevent fire or avoid electric shock.
It is up to forum members here to spread the word to others and advise that an existing RCBO is exchanged (by an electrician!) for a bi-directional type.
Save energy... recycle electrons!
This photo shows a bi-directional RCBO by Proteus at Redditch.
The symbols are correct, and the third-contact which the solonoid switches is visible in the diagram on the side.
What I still don't like is:
- the terminals being labelled 'In' and 'Out'
- no bi-directional symbol or marking on the part of the RCBO which remains visible to the householder after installation is completed
This particular RCBO is Type A
and Curve C... which defines the time it takes to trip due to over-current.
Most household MCBs and RCBOs are curve-B, which operates faster.
I use Curve-C trips to supply circuits which are likely to have large inductances connected (motors in a workshop or an inverter).
Update 28may24:
I have a response from Proteus Switchgear to say that they are already acting on the BEAMA directive and "will remove the in/out and also add on a bidirectional arrow symbol to the front of compliant devices"
The changes will filter through once existing stocks have been exhausted.
Save energy... recycle electrons!
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 615 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
To me this feels like a marketing ploy from Heat Geek t...
By Chris , 8 hours ago
-
RE: Is it mad to think there should be a minimum SCOP for UK heat pump installs?
@jamespa, I don’t think that’s quite right. The regulat...
By Mars , 8 hours ago
-
@agentgeorge That’s a ittle too inscrotumable for me… T...
By Toodles , 9 hours ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
We’re really excited to be recording a landmark Homeown...
By Mars , 9 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Thx, but Sven did the hardware development. My role (as...
By Mosibi , 9 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
Are you using Havenwise for Hot Water? I have ...
By F1p , 10 hours ago
-
RE: PV Panels on roof in Conservation Area
@majordennisbloodnok Fnaargh, I was thinking about try...
By colinc , 11 hours ago
-
RE: Electricity price predictions
@jamespa Ah, you mean MPs that have not pro...
By Batpred , 12 hours ago
-
RE: Buying large amp bidirectional RCD and RCBO
Exactly @transparent , this type of RCBOs are not easil...
By Batpred , 12 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - though I realise I am a Canute, I have an...
By cathodeRay , 12 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And just when I think great they’re coming next week to...
By Crimson , 15 hours ago
-
RE: Very Much Awake – Renewing the Heating Industry One Step at a Time
I feel that that attitude shared by Aadil from Heat Gee...
By Toodles , 16 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
and we have some of the strongest tidal flows anywhere ...
By Old_Scientist , 18 hours ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
This looks OK. Overall you have roughly the right amoun...
By Old_Scientist , 19 hours ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
I'm not familiar with Hive thermostats/controllers, but...
By Old_Scientist , 19 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa mine seems changing albeit not by much, 3.21, ...
By AdamK , 2 days ago
-
@majordennisbloodnok The migration hasn't started in th...
By HCas , 2 days ago
-
RE: One room is colder than the rest of the house
@jamespa thanks for all the advice. Just so you know, ...
By AndrewJ , 2 days ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
My MMI is in the loft but I checked the pump flow rate ...
By RadWhisperer , 2 days ago