Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regarding the use of RCBOs to connect PV inverters or storage batteries.
This is not yet part of the IET Electrical Wiring Regulations, but it is sufficiently serious that an amendment is being expedited.
Overview: household electrical circuits are wired from a Consumer Unit which contains a number of trips.
Most trips are there to prevent excessive current being passed through wires/cables. Those are MCBs (Miniature Circuit Breakers).
It is common for a consumer unit to have one or more RCDs (Residual Current Detectors).
These compare the outgoing current on the Live wire, with that being returned on the Neutral.
If there is an imbalance, the contacts will open to prevent fire or electric shock to someone who has touched a live cable.
Increasingly, electricians are fitting RCBOs for individual power circuits.
These combine the functions of an MCB and RCD.
They will open the contacts either for over-current, or because current is leaking away somewhere.
If a single-circuit RCBO trips out, then at least the lights remain on so you can see what's gone wrong!
RCDs and RCBOs both have a test button.
This should be pressed periodically to check that it will open the contacts to protect against electric shock
When solar panels or storage batteries are installed, it is not mandatory that the circuit is supplied from an RCBO. An MCB is sufficient.
However, many installers do use an RCBO to provide an extra level of safety for when it might be necessary for an inverter to undergo maintenance.
Most Solar Inverters and Storage Batteries are "Grid tied".
They export to the mains supply through the same wires which connect them to the consumer unit.
A grid-tied inverter will have a G98 certificate, and requires permission from the regional DNO to install it.
This common arrangement means that electricity will pass through the RCBO in either direction.
The RCBO contains a small amount of electronics to handle the current sensing.
When there is a fault (either over-current or earth-leakage) a solonoid is energised (switched on), which opens the contacts.
If the RCBO was on a normal power circuit, opening the contacts would remove power from the electronics.
The trip would remain open until the lever was manually moved, and the solonoid would no longer be powered-on.
But if there is power still being applied in the reverse direction by an inverter or storage battery, when the contacts open, the solonoid remains energised.
Such a small solonoid will overheat and burn out.
The circuit can still be re-powered using the lever, but it will no longer be able to protect against electric shock.
The home owner won't know that.
The solution is to use a an RCBO specifically designed for bi-directional use.
A bi-directional RCBO has a third pair of contacts.
When the solonoid operates to open the trip, that 3rd contact set removes power from the electronics, and the solonoid coil is de-energised, preventing burn-out.
How can you tell if an RCBO is bi-directional?
Most RCBOs have arrows to show the direction of current, or have a label which denotes Supply and Load terminals.
A Bi-directional RCBO will not be marked for Supply and Load.
It may also have a set of arrows pointing in both directions.
If an RCBO isn't marked as being bi-directional, then it isn't.
The IET Wiring Regulations aren't retrospective.
When the amendment is released which specifies the need for a bi-directional RCBO, there will still be many thousands of installations which appear to have an operational RCBO, but it will only offer protection against over-current. It won't be acting to prevent fire or avoid electric shock.
It is up to forum members here to spread the word to others and advise that an existing RCBO is exchanged (by an electrician!) for a bi-directional type.
Save energy... recycle electrons!
This photo shows a bi-directional RCBO by Proteus at Redditch.
The symbols are correct, and the third-contact which the solonoid switches is visible in the diagram on the side.
What I still don't like is:
- the terminals being labelled 'In' and 'Out'
- no bi-directional symbol or marking on the part of the RCBO which remains visible to the householder after installation is completed
This particular RCBO is Type A
and Curve C... which defines the time it takes to trip due to over-current.
Most household MCBs and RCBOs are curve-B, which operates faster.
I use Curve-C trips to supply circuits which are likely to have large inductances connected (motors in a workshop or an inverter).
Update 28may24:
I have a response from Proteus Switchgear to say that they are already acting on the BEAMA directive and "will remove the in/out and also add on a bidirectional arrow symbol to the front of compliant devices"
The changes will filter through once existing stocks have been exhausted.
Save energy... recycle electrons!
I had a read and I still cannot understand the below. We are talking about the direction of power flows. An alternating current changes direction 100 times a second. So the issue cannot be about the direction of the current.
But if there is power still being applied in the reverse direction by an inverter or storage battery, when the contacts open, the solenoid remains energised.
As it is about DC currents, why not describe it as such?
And it does seem thar this Beama originated confusion was related to a British electrical labelling standard?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
See matching discussion here in the topic about Plug'n'Play Balcony Solar kits.
Save energy... recycle electrons!
Thanks for the clear explanation @transparent. I think I agree with two sides of this issue:
There is a risk that when a unidirectional rcbo/rcd trips out or is flicked off with an inverter connected and running, that inverter may continue to backfeed for long enough to destroy the rcd solenoid inside the rcbo rendering it non functional as a protective device. It also would be odd if this prevents the engagement of the wider public with solar.
Risk management is standard practice in such circumstances - eg: we're happy to use non earthed power supplies in our home, simply by using higher levels of insulation internally - all those usb chargers, laptop supplies, so many things! These are still sold to people for use without an RCD. There must be some way that an inverter can pose an acceptable risk to a unidirectional rcd/rcbo, and if necessary some new standard imposed for UK legal balcony solar - whilst simultaneously phasing out unidirectional devices. For example, a new standard mandating the power down on disconnect to be much faster than the present 0.5s. Of course the inverter could be faulty; this feature could be 100% tested. A fault could develop - so could a fault with the insulation I mentioned above.
I had a look for bidirectional rcbos, and they don't seem to be obbviously more expensive, screwfix have them for £17 ish. Other distributers are available:-)
We have an EV charger, which has an expensive type B rcd which can trip in the case of dc leakage, which normal rcd/rcbo's may not. I think that most power electronics devices (solar inverters, inverter heatpumps...) are recommended to have type B. I think type B are £200 ish, probably this reduces adoption!
Posted by: @roblThere is a risk that when a unidirectional rcbo/rcd trips out or is flicked off with an inverter connected and running, that inverter may continue to backfeed for long enough to destroy the rcd solenoid inside the rcbo rendering it non functional as a protective device.
Are you saying that an RCD solenoid would burn only when a current is not flowing through it? So (and I am taking the risk of making the options up):
- if inverter power is off, it would not burn
- if inverter power is fed from the load side, and not used from grid side, it burns
- if inverter power is fed from the load side, and used from the grid side, it does not burn
So in this latter case, how much power would need to be drawn from the grid side in order for it to not burn?
It would be great if we could access a single test report for a product version with such a risk.
Whether power flows in one or the reverse direction does not change the physics that an AC current changes direction 100 times a second...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Below is a simplified problematic RCD circuit I ‘found’. The trigger is the difference between L and N currents, which is then amplified using a power supply from the output, which remains possible for 1/2s after switch off so could burn out the coil. I imagine speed is crucial, so it can’t drive anywhere near continuously. I must admit it looks like it should only cause the coil to fail if there is an actual RCD trip current AND the inverter power is on, rather than the more general case I mentioned before, apols.
Posted by: @roblFor example, a new standard mandating the power down on disconnect to be much faster than the present 0.5s. Of course the inverter could be faulty;
And that's the nub of the problem, isn't it?
Even if such a Balcony Solar Standard were imposed, I'm not convinced that the IET would accept it.
The Wiring Regulations are valid based on 'ignorance' of the appliances which get connected.
The assumption is "safety first", and that means the rules are there to cope with an appliance which is not complying with a 'standard' as it should.
Posted by: @batpred- if inverter power is fed from the load side, and used from the grid side, it does not burn
So in this latter case, how much power would need to be drawn from the grid side in order for it to not burn?
Please recheck the schematic of the bi-directional RCBO at the top of this page.
The issue has nothing to do with the amount of power being drawn, but what happens when the contacts have opened in response to an earth-leakage fault.
Save energy... recycle electrons!
@transparent I do like the safety first precautionary approach. We could do with it in other aspects of life (PFC's, CO2 emissions...). I trust a balanced approach will be taken of risk versus PV adpotion. In my experience, once an individual is engaged in green topics - be it PV, EV, a heatpump, diy loft insulation - they've started on a journey that keeps going. I think individuals are more engaged if hands on, rather than paying someone - so I really hope this is all possible somehow, even though I myself am unlikely to do it even if available.
I don't think expensive type B (DC capable) devices are very common*, and all the usual cheap parts can be "blinded" by a DC leakage path which is very concievable with earthed PV panels, even if bidirectional. As mentioned before, you can use non-earthed devices without an RCD at all - it's easy to see this causing a serious problem that's only "discovered" when charging your iphone while touching a radiator.
*actually - I just googled it, and I think they are now mandated. I'm guessing most installs avoid the whole issue by having MCB only for solar/battery/heatpump installs.
Thanks, that makes sense. The issue would occur just after the RCD trips (probably depending on the coil material, etc), in case the inverter is still providing power. We should bear in mind that all inverters approved for domestic use have anti-islanding, so when they detect a loss of grid, they should stop providing power within a certain time. I deduct it could also depend on how quickly the inverter stops providing power. And it would also be obvious that the RCD is faulty whenever the RCD test button is pressed.
As the real risk depends on the coil material and heat dissipation and the inverter timings involved, I can only hope that the IET made the decision after careful risk analysis of the equipment combinations (RCD and inverter) that had been historically deployed at the time. And how the risk would evolve.
So the IET officially named these as "bi-directional" RCDs which essentially requires that all installations use them and so are able to cope with an inverter where anti-islanding is not active. This also has the effect of allowing inverters with that type of fault to continue to work undetected (most would as they are probably on MCBs). I am glad I do not have any role in advising government in these matters!
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @robl*actually - I just googled it, and I think they are now mandated. I'm guessing most installs avoid the whole issue by having MCB only for solar/battery/heatpump installs.
Yes, for sites with multi generation sources that seems to be the case. Thankfully all MCBs are bi-directional!
I assume heatpumps will be fine on an RCD...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @roblIn my experience, once an individual is engaged in green topics - [...] - they've started on a journey that keeps going. I think individuals are more engaged if hands on, rather than paying someone
So that again comes back to the Public leading the way, rather than having Net Zero strategies imposed on them...
... in which case we're going to need
- more hands-on community energy groups
- a nationwide Energy Knowledge dissemination program
There are a number of reputable manufacturers in China who offer Type-B RCDs
Geya, Chint and Tongou are worthwhile considering.
I haven't yet found a Chinese manufacturer of bi-directional RCBO units.
But at least their uni-directional ones are properly labelled for 'load' and 'supply'.
Save energy... recycle electrons!
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 991 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 18 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 18 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago