New Fogstar 15.5kWh upright solution
I think this is getting confusing.
Sometimes you guys are stating readings reported by a battery, and then you refer to parameters set within the inverter.
Measuring SoC is tricky.
Doing so over long periods of time without re-defining it by charging the battery(ies) to 'full' is nigh on impossible.
Let's assume that the figures you're stating here are within plus/minus 5%
almost all the 'inaccuracies' we've just discussed are actually within the range of acceptability.
Firstly, I agree with @ggw that it's the inverter which is 'in control'.
but then let's consider this...
Posted by: @adrianmcCan the battery force charge its self
Theoretically it's possible, but I haven't heard of that being implemented.
The BMS in that battery would need to have been pre-loaded with the command-set for your particular model of inverter.
It would then need to select the Modbus command from that set and send it to the inverter across the CAN or RS485 connection.
The inverter could then start charging the battery from the grid...
... until something else then happened.
And what is that something else?
Does the battery initiate another command?
At what point?
How can it know its SoC accurately enough whilst still being re-charged at high current?
Or would the inverter intervene anyway?
Might it read its own configuration settings and stop the grid-charge because a particular parameter had been reached?
Matching batteries and inverters is normally not undertaken at that level.
They wouldn't normally send commands to each other.
Their 'compatibility' is rarely more than just sending data from the battery to the inverter, which you can then see on the inverter's App.
Save energy... recycle electrons!
Our hybrid inverter is a sunsynk, and while it states the SOC monitored by the (Seplos mason) battery I’m pretty sure it uses its own voltage measurement to indicate full/empty, and takes emergency measures based on it. The voltage levels it uses are “hidden” - you have to swap to batt=Pb voltage control, set the levels, then swap back to Li bms. Weird, and when it works (it is), it’s not something I’d like to mess with.
Hi,
I have been reading all the posts abotu Fogstart 15.5 kwh battery. I would like to get one without solar. Ideally I would like someone to install but I don't see anyone at the moment.
What is the max charge and discharge power from this battery, from the spec sheet it says 200A, but not about peak/continuous charge and discharge power? Somewhere I don't recall it was mentioned that it is under 2kw that seems quite low.
If I want to DIY install can I not go over 3.6kw inverter? Do I have to get G99 prior before if I want any thing higher?
Thank you.
Hi @littlefinger and well done for finding an appropriate topic in which to post 🙂
Firstly, the Fogstar storage batteries have no direct connection to either the grid or to solar panels.
You require a separate inverter to achieve that.
The 200A maximum charge/discharge from Fogstar's batteries is a feature imposed by the inbuilt Battery Management System (BMS) from Pace.
That 200A is the maximum sustainable current.
It's unlikely that you'd ever want to pull that many amps from your battery.
200A at 52v is over 10kW.
I don't know from where you got the 2kW figure. It's not correct.
The limit of 3.68kW and G99 are factors which apply to inverters which export to the grid.
If you wish to do a DIY installation and you don't intend sending power back to the grid, then neither of these issues is relevant.
Tell us a bit more about what you'd like to achieve, preferably without too much technical stuff!
We can get more technical when we understand what you'd like to do.
Save energy... recycle electrons!
@transparent Wow that was quick. Thank you.
Below is the reply from Fogstar I just received
forums can be a minefield of misinformation.
So the max input in Kw for a 200A bms is 2.4Kw
It's a little over 2.4 as lithium operate at 13.2v (meadan voltage range)So in answer
2.4Kw (2400w) max charge and discharge.
Hope this clarifies.
Any resources on how to calculate there figures from spec sheet?
At the moment I have install home battery storage at lower cost and came to know about Fogstar battery.
After reading this thread and other online forums it looks like Sunsynk Hybrid inverter is good choice.
My immediate goal is to shift my grid import to off-peak, while keep my options open for future expansion for extra batteries and Solar. There is possibility of getting EV but not right now.
From what I understand, G99 is required even if you do not want to export if inverter is over 3.68kW
I'm thinking of having either 8kW Ecco Hybrid Inverter or 8kW Hybrid Inverter (not sure what the difference, except for one is smaller than other) or Sunsynk-LifeLynk-XL.
Would G99 approval specify how much one can export? That is can I get approval to export without solar so if I add solar later I do not have to apply again.
Cheers
That reply from Fogstar is in response to a question about a battery rated at 13.2v,
which tells me that it's probably four LiFePO4 cells in series.
The Fogstar 15.5kWh battery bundle uses sixteen LiFePO4 cells in series, each rated at 3.2v (nominal):
Power in watts (or kilowatts) = Volts x Amps
Yes the SunSynk 8kW inverter is a good choice for an off-grid system.
The SunSynk inverters do have the capability to export to the grid.
So you would still need to obtain G99 consent from your DNO, even 'tho you will configure the export to be Zero.
That's the most common arrangement for SunSynk installations in the UK.
You state the inverter model number on the G99 Form, and the DNO will look this up on the ENA Database.
SunSynk's export-limitation feature has already obtained ENA approval to operate with Zero-export.
So you will be given G99 approval regardless of the power-rating of the inverter.
Once you have DNO consent for Sunsynk inverter(s) operating with Zero-export, you do not need to reapply if
- you add solar input
- you add another SunSynk inverter in parallel configuration
- you add further battery storage
Your off-grid system might then look something like this:
Save energy... recycle electrons!
- 22 Forums
- 2,047 Topics
- 44.7 K Posts
- 10 Online
- 3,274 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Yes, the "zoning with ASHP" topic again...
James, On your question: Please explain why a highe...
By HarryRea , 3 hours ago
-
RE: Commencing on an ASHP Installation Process
I think you may very well be right and of course A2A ca...
By JamesPa , 5 hours ago
-
-
RE: Renewables & Heat Pumps in the News
Yes, it's far too much money. DESNZ will no doubt wis...
By Transparent , 11 hours ago
-
That all sounds very believable. Presumably mixing of ...
By JamesPa , 14 hours ago
-
RE: Battery sizing - How low can you go!
@bontwoody Hope this is legible
By ChandyKris , 19 hours ago
-
RE: Agile: average import cost vs other tariffs?
@old_scientist We are with SSEN and our G99 application...
By Toodles , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Yes. Storing the solar generation within the home is gr...
By Transparent , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15, @heacol cover your area… I’d strongly recom...
By Mars , 2 days ago
-
RE: Warm weather and heat pumps.
@editor Oh nothing right now because $ needed for struc...
By Lucia , 2 days ago
-
RE: Potentially more choice including air to air heat pump grants
@jeff Such documents are far too wordy for my ‘daily re...
By Toodles , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@grahaml I cannot agree that it is a small percentage o...
By benson , 3 days ago
-
RE: Samsung Gen6 16kW tribulations
@emceed, can you please give us an update on your syste...
By Mars , 4 days ago
-
What's the problem you are trying to solve. The answer...
By JamesPa , 6 days ago
-
Good luck. For what it is worth my system was very def...
By JamesPa , 7 days ago
-
RE: Massive Electricity Cost for Running My Air Source Heat Pump
I agree @mark-h The Building Regs are now very readable...
By Transparent , 1 week ago
-
RE: Help me understand my Mitsubishi Ecodan system
@carpenterstation When changing settings in the ser...
By RobS , 1 week ago
-
RE: Ecodan Legionella cycle - immersion heater problem
Thanks for letting us know @clockworks I admire your ...
By Transparent , 1 week ago
-
RE: Revised version of MCS-020 (noise standards for heat pumps)
As you say this is no change, which I personally think ...
By JamesPa , 1 week ago