Heat pumps and OPEN VENTED DHW tanks?
I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
Absolutely nothing at all to stop any ashp being used with a vented tank except that I'm not sure anyone advertises a vented tank with a large enough coil. Most tank manufacturers will do specials or you can use a plate heat exchanger instead of a coil (arguably better anyway), or just plumb an 'unvented' tank with a vent (although this is unnecessarily expensive). Really this shouldn't be an issue for any half competent plumber.
Doubtless some will give a spiel about legionella, you should run a legionella cycle in accordance with recommendations (although others may argue that this is unnecessary).
Sadly you are getting the usual nonsense of installers who can't think outside their very small box and insist on using the ashp manufacturers pre plumbed cylinder so that they can put complete rookies on the job whilst still charging a premium.
Permitted development applies only to one heat pump so you will need express consent if you already have one. Once you have express consent MCS isn't necessary unless you want the grant. Sadly (and disgracefully imho) MCS is necessary for installation under pd.
You probably can't duck the loss calcs because emitters need to be sized but it might be possible to persuade an installer to use your actual consumption for the system sizing. Most will probably refuse however because as a customer you can't be trusted and likely over-size as a result.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Gledhill do a range of OV HP tanks .. eg Gledhill SL Plus HP 300HP3SQM EE Open Vented - PLUHP300OV, though these are not, of course, part of any manufacturer's standard kit. Sounds like I figured right - I need planning approval for the second HP. Might be easier just to upgrade the existing one and go A2A for the whole bungalow. I used to despise hot air heating, back when it was gas furnaces, but since I want aircon anyway ..
The fact BUS doesn't apply to A2A is another stupid government decision. Much of the continent (well, Scandinavia) runs on A2A as far as I know, thus avoiding a whole ton of freezup issues.
Legionella and even DHW in total are not really a consideration.. I have enough PV and battery to just run an immersion heater on cheap (thanks Octopus) overnight electrons, and leave the heatpump to do the space heating.
As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Posted by: @dave1234As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Not sure you are any worse off than those like me who live close to London when it comes to flexible installers. Many including me report similar problems.
Octopus seem to have a fairly good reputation for being tolerably flexible but will only engage if your house fits their current target market.
Few installers, in my experience, like people who have done any research, oresumably because it makes it more difficultf for them to spout bs to get the sale they want. Those that do like such people deserve our custom.
Unfortunately the bus and pd rules, both of which require mcs, have created an industry which some argue is not healthy.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
you can use any manufacturers ashp unvented cylinder as an open vented cylinder have done it numerous times as the water flow rate and pressure is quite bad here in the Sw London area! All that the installer needs to do is not use the expansion vessel and combination valve . Cap the prv and plumb it like an open vented cylinder. It’s surprising how many installers don’t know thisPosted by: @dave1234I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
- 22 Forums
- 2,035 Topics
- 44.4 K Posts
- 45 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: In the middle of an ASHP installation - a few questions (and issues)
@jamespa yes. The installers tried to limit the max flo...
By benson , 12 minutes ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
File received thank you.
By trebor12345 , 1 hour ago
-
RE: The Great British Heat Pump Quiz
That was fun, thank you @editor. 85%, which is just as ...
By AllyFish , 2 hours ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 5 hours ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 5 hours ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 15 hours ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@toodles what could possibly go wrong if the government...
By Mars , 16 hours ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 17 hours ago
-
Thanks both Some useful tips I’ll keep you informed ...
By Fingers , 20 hours ago
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 23 hours ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 2 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 2 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 2 days ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 2 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 2 days ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 2 days ago