Heat pumps and OPEN VENTED DHW tanks?
I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
Absolutely nothing at all to stop any ashp being used with a vented tank except that I'm not sure anyone advertises a vented tank with a large enough coil. Most tank manufacturers will do specials or you can use a plate heat exchanger instead of a coil (arguably better anyway), or just plumb an 'unvented' tank with a vent (although this is unnecessarily expensive). Really this shouldn't be an issue for any half competent plumber.
Doubtless some will give a spiel about legionella, you should run a legionella cycle in accordance with recommendations (although others may argue that this is unnecessary).
Sadly you are getting the usual nonsense of installers who can't think outside their very small box and insist on using the ashp manufacturers pre plumbed cylinder so that they can put complete rookies on the job whilst still charging a premium.
Permitted development applies only to one heat pump so you will need express consent if you already have one. Once you have express consent MCS isn't necessary unless you want the grant. Sadly (and disgracefully imho) MCS is necessary for installation under pd.
You probably can't duck the loss calcs because emitters need to be sized but it might be possible to persuade an installer to use your actual consumption for the system sizing. Most will probably refuse however because as a customer you can't be trusted and likely over-size as a result.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Gledhill do a range of OV HP tanks .. eg Gledhill SL Plus HP 300HP3SQM EE Open Vented - PLUHP300OV, though these are not, of course, part of any manufacturer's standard kit. Sounds like I figured right - I need planning approval for the second HP. Might be easier just to upgrade the existing one and go A2A for the whole bungalow. I used to despise hot air heating, back when it was gas furnaces, but since I want aircon anyway ..
The fact BUS doesn't apply to A2A is another stupid government decision. Much of the continent (well, Scandinavia) runs on A2A as far as I know, thus avoiding a whole ton of freezup issues.
Legionella and even DHW in total are not really a consideration.. I have enough PV and battery to just run an immersion heater on cheap (thanks Octopus) overnight electrons, and leave the heatpump to do the space heating.
As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Posted by: @dave1234As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Not sure you are any worse off than those like me who live close to London when it comes to flexible installers. Many including me report similar problems.
Octopus seem to have a fairly good reputation for being tolerably flexible but will only engage if your house fits their current target market.
Few installers, in my experience, like people who have done any research, oresumably because it makes it more difficultf for them to spout bs to get the sale they want. Those that do like such people deserve our custom.
Unfortunately the bus and pd rules, both of which require mcs, have created an industry which some argue is not healthy.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
you can use any manufacturers ashp unvented cylinder as an open vented cylinder have done it numerous times as the water flow rate and pressure is quite bad here in the Sw London area! All that the installer needs to do is not use the expansion vessel and combination valve . Cap the prv and plumb it like an open vented cylinder. It’s surprising how many installers don’t know thisPosted by: @dave1234I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
- 26 Forums
- 2,227 Topics
- 49.5 K Posts
- 83 Online
- 5,892 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa ok got home and I can indeed set the flow temp...
By AdamK , 1 hour ago
-
I'll leave it tonight and post the graph tomorrow to se...
By bontwoody , 1 hour ago
-
RE: New Fogstar 15.5kWh upright solution
That's odd. I can't see anything in the Sunsynk manua...
By Transparent , 2 hours ago
-
It’s my sole reason to always deter homeowners from goi...
By Mars , 3 hours ago
-
Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
I ended up with a Solis S6-EH1P8K-L-PLUS (8 kW) hybrid ...
By Batpred , 4 hours ago
-
RE: Options on flushing my system
@grantmethestrength with your pragmatic approach and &#...
By SUNandAIR , 5 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
@batpred For the moment I'm sticking with what I have, ...
By bubuontheweb , 7 hours ago
-
RE: Electricity price predictions
Nice to be back on track! If we all had the interest, s...
By Batpred , 7 hours ago
-
RE: Say hello and introduce yourself
I think this is where we may differ. Nothing makes sen...
By JamesPa , 8 hours ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
Enable installer mode - 5678 Enter the Space Heating/...
By RadWhisperer , 8 hours ago
-
Is your installer MCS certified? If so, they should reg...
By Old_Scientist , 8 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas So the answer from Mitsu was: To Confirm you ca...
By bontwoody , 10 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Grant Aerona 3 10 HPID10R32
By MDG , 11 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I don't know! The Midea manuals and what actually happe...
By cathodeRay , 12 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
If you’re interested in finding out which of your neigh...
By AgentGeorge , 13 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
It is a crazy situation. It also seems not enough 400kv...
By Batpred , 15 hours ago
-
RE: Rate the quality of your heat pump design and installation
More like Octopus wanted to fit a Cosy 6 at the end of ...
By RadWhisperer , 18 hours ago
-
RE: How good is the app support for your heat pump?
Yes. Personally I would only use a heating control app ...
By Batpred , 1 day ago