Heat pumps and OPEN VENTED DHW tanks?
I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
Absolutely nothing at all to stop any ashp being used with a vented tank except that I'm not sure anyone advertises a vented tank with a large enough coil. Most tank manufacturers will do specials or you can use a plate heat exchanger instead of a coil (arguably better anyway), or just plumb an 'unvented' tank with a vent (although this is unnecessarily expensive). Really this shouldn't be an issue for any half competent plumber.
Doubtless some will give a spiel about legionella, you should run a legionella cycle in accordance with recommendations (although others may argue that this is unnecessary).
Sadly you are getting the usual nonsense of installers who can't think outside their very small box and insist on using the ashp manufacturers pre plumbed cylinder so that they can put complete rookies on the job whilst still charging a premium.
Permitted development applies only to one heat pump so you will need express consent if you already have one. Once you have express consent MCS isn't necessary unless you want the grant. Sadly (and disgracefully imho) MCS is necessary for installation under pd.
You probably can't duck the loss calcs because emitters need to be sized but it might be possible to persuade an installer to use your actual consumption for the system sizing. Most will probably refuse however because as a customer you can't be trusted and likely over-size as a result.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Gledhill do a range of OV HP tanks .. eg Gledhill SL Plus HP 300HP3SQM EE Open Vented - PLUHP300OV, though these are not, of course, part of any manufacturer's standard kit. Sounds like I figured right - I need planning approval for the second HP. Might be easier just to upgrade the existing one and go A2A for the whole bungalow. I used to despise hot air heating, back when it was gas furnaces, but since I want aircon anyway ..
The fact BUS doesn't apply to A2A is another stupid government decision. Much of the continent (well, Scandinavia) runs on A2A as far as I know, thus avoiding a whole ton of freezup issues.
Legionella and even DHW in total are not really a consideration.. I have enough PV and battery to just run an immersion heater on cheap (thanks Octopus) overnight electrons, and leave the heatpump to do the space heating.
As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Posted by: @dave1234As you say though, finding a flexible installer, out here in the wild especially, is a challenge .. much easier to shift BUS-funded boxes en mass. Even Octopus (as Which recommended) won't play with me, whether because they just don't have anyone out here, or whether because of non standard needs, is hard to tell. Maybe they just don't like anyone who has actually done some research. 🙂
Not sure you are any worse off than those like me who live close to London when it comes to flexible installers. Many including me report similar problems.
Octopus seem to have a fairly good reputation for being tolerably flexible but will only engage if your house fits their current target market.
Few installers, in my experience, like people who have done any research, oresumably because it makes it more difficultf for them to spout bs to get the sale they want. Those that do like such people deserve our custom.
Unfortunately the bus and pd rules, both of which require mcs, have created an industry which some argue is not healthy.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
you can use any manufacturers ashp unvented cylinder as an open vented cylinder have done it numerous times as the water flow rate and pressure is quite bad here in the Sw London area! All that the installer needs to do is not use the expansion vessel and combination valve . Cap the prv and plumb it like an open vented cylinder. It’s surprising how many installers don’t know thisPosted by: @dave1234I am struggling to find an installer, or manufacturer, who can fit me an ASHP in conjunction with a vented DHW tank. Out here in the wilds of Shropshire, 1000 ft up, the water pressure (or even availability) of mains water is iffy so there are two large cold water tanks in the loft. This also avoids the need for pressure relief to the outside world, in the event the immersion heater decides to boil the tank. Am I chasing unicorn poo, or do such systems exist (even on the Welsh marches)?
I guess I need an MCS installer to avoid planning issues, though I may have those anyway since I have a 20 YO A2A aircon system, and I believe I am only allowed one HP under permitted developments? I do have 10 years of energy consumption data from my oil burner (10 kwhr per day per degree day of heating needs) so maybe I can duck the heat loss calculations?
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 463 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Hi all I'm having some trouble with a Grant ASHP and ...
By Renewables345 , 30 minutes ago
-
RE: Underfloor Heating Installation Issues with Heat Pump
We suffered a water leak last year in two rooms and had...
By MartinHook_UK , 41 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 50 minutes ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
*** I now see @jamespa has already posted but will stil...
By cathodeRay , 2 hours ago
-
RE: Tell us about your Solar (PV) setup
@mk4 Charge to 100%, discharge down to 10%.
By bobflux , 2 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 3 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 8 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 14 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 15 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 18 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 19 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 21 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 1 day ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago