RE: My horrific Samsung heat pump installation and experience

You simply can't use your existing thermostat other than if you set it well above the desired temperature to act solely as a limiter. It's clever mod...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

Before I comment substantially can you clarify this. Are you saying you have already the external thermistor. How do you know the errors were due to...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

PS to above. So far as I can see from the installation diagram, the connection between the remote controller and the heat pump is 2 wire. So you cou...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

Apart from the location which is a poor one (could it be changed?) then, so far as I can see, the manual does not imply or state the material conclus...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

Your conclusion is not correct. Setbacks amount to switch offs in practice and these can be programmed vis the Samsung timer. They should anywa...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

@iantelescope Thanks for the manuals and details of your current settings. I have read through the latter and there are a couple of comments I wo...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

Thats very helpful thanks as a) it confirms the key thing that I had inferred from others, namely that it is possible to use WC and the internal...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

Doing this will increase your electricity consumption by 15%. This is a direct result of thermodynamics not engineering and you will not circumvent i...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

So far as I can see from the pictures the mode in all of these is set to heat not auto. My understanding from manual is that WC operates only when t...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

@iantelescope Ok. From various pieces of evidence it is more or less certain that the system as it will be after your replumbing can operate in WC...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

Sorry but, for any given room temperature, the oil filled radiator won't save on electricity if your heat pump is working correctly. Your heat pump s...

1 year ago
Reply
RE: My horrific Samsung heat pump installation and experience

What is the backup heating powered by and where is the diagram from. I do understand that you can offset the water law of course. I wouldn't call th...

1 year ago