@bontwoody In truth it is a very widely held misconception, whether we are talking about boilers or heat pumps, that turning off the heating for (sa...
Agree (assuming that 'draw' in the second sentence should read 'deliver'). So in the second instance at COP=4.5, 81kWh would be delivered for 12k...
Referring to the above Im going to try to clear up some basics, with apologies to any physicists or engineers reading! Firstly energy is measured (f...
If oversized then it is indeed quite possible that an overnight setback will save energy, because you are reducing the inherent inefficiency of cyclin...
If the energy is delivered at cop4 is xkWh then you must supply x/4kWh. If the same amount of energy is delivered at cop 6 you must supply x/6kWh. I...
Er no, you are confusing power and energy. You pay for energy not power. If 24kWh is required then the input energy is 24/cop. So if the cop is 6...
Sorry but that is simply not true and worse still is quite seriously misleading. Whilst the heating is off the house continues to lose heat. It l...
I just ran the numbers through my WC simulator. This calculates, based on Ecodan R32 data, the efficiency gain from various WC curves relative to fix...
It is a cop out and as I say upthread will incur a penalty of 3-6% or more if it's more than a a couple of degrees out. However installers don't was...
This is the 'alternative method' I refer to in a post above. Care needs to be taken with the choice of room stat. Some 'clever' ones, as they appro...
According to his post a few pages back the speeds of both pumps are controlled by an Arduino based system. I did ask what behaviour it targets but go...
Thanks. Doing this would, as you say, eliminate another variable and I did consider suggesting it (and, if this were my system, it is what I would do...
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 43 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 1 hour ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 18 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 20 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 22 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 1 day ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 5 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 6 days ago