@cathoderay In my opinion 'cycling' is not the same as 'setback'. A heat pump cycles to prevent the IAT from increasing too high, whereas a setback ...
Hi Ray, I actually didn't state that using setback would be a mug's game. Please don't miss quote me. Any reduction in IAT will reduce heat loss, ...
Based upon the data table for an 8.5kW Ecodan, running at maximum output at a LWT of 45C, it should require approximately 2.7kW of electrical energy. ...
Can you provide closeup photo's of your zone 1 heatmiser in the on and off condition. You need to educate your guest about heat pumps.
I would suggest that you ask your installer to rectify the problem. Once the on - off problem is resolved, you may wish to consider operating your sys...
Looking at the data tables for a 8.5kW Ecodan, your heat pump was probably running at full output and developing something in the order of 10kW of the...
@jamespa Hi James, You are indeed correct, the WC 'curve' is a straight line calculation based upon the values in cells I5 and I6 and K5 and K6. ...
I would suggest that you check the setting of the upper limit for the LWT in the controller. Do you have any of the following in your system? Buffer...
@cathoderay I suspect that the second increase in LWT occurs after your heating system and heat emitters are fully up to temperature, hence the RWT ...
@sunandair What is the water flow rate? It would be interesting to see what effect reducing the flow rate would have. Also what is happening with ...
@jamespa Hi James, I have now completed a WC version of the modelling tool, which I think works quite well. If you have the time and inclination...
Having read the blog and watched the video, it has convinced me to never buy anything from grant. 🙄
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 11 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Humming sound on new install.
One other thing, I haven’t balanced the rads yet so cur...
By AdamK , 5 hours ago
-
Funny story Graham, when I started looking to ...
By DREI , 5 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Possibly not the answer you might want, but if it were ...
By Temperature_Gradient , 7 hours ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 9 hours ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 11 hours ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 11 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Yes Octopus only have the £9 a month service plan for t...
By NJT , 13 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 13 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 13 hours ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 1 day ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 1 day ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 2 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 3 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 3 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 3 days ago