Okay Dave, If your system is out of warranty then the first problem is easily resolved. At a convenient time, power your system down, wait 10 minute...
@davew Hi Dave, Obviously if it was my system I would have probably installed it myself and confirmed that the wiring was correct. You are indeed ...
Is the blue line the setpoint and the black one the measured value? What is the resolution of the display, is it +/- 0.5C or +/- 0.1C? Edit. I thi...
So as you stated, the compressor is making a soft start at 36Hz, and then gradually ramping up to 52Hz, where it appears to remain constant, until the...
@cathoderay As you have probably noticed, I have been busy answering queries from new forum members, though I have been giving some thought to your ...
Out of interest, what is the setting of the 'room temp control' time interval on your system?
How is your system set to operate at the moment? Is it in heating or DHW? Do you intend to provide the requested photo's? Do you have any thermometers...
Thank you, good thinking. It would be useful to compare your findings with other systems if anyone has the time to spare. I presume that this is compr...
I presume that you have them switched off or disabled at the moment?
Thanks Mike, much appreciated. 👍
As usual the words sound quite good, and are in the correct order, but I suspect they will have the same set of idiots try to put the words into pract...
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 37 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Powerwall 3 or Myenergi or something else?
Having had a chance to test this now, I can confirm tha...
By Old_Scientist , 11 minutes ago
-
Mitsu PAR-WT60R Wireless Controller - options
I hope I have satisfactorily installed the above wirele...
By DavidAlgarve , 14 minutes ago
-
WC curve best discovered by experiment anyway as any lo...
By JamesPa , 5 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@editor your engineer's attitude is truly horrifying. ...
By GrahamF , 22 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 24 hours ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 1 day ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 1 day ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 1 day ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 2 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 2 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 2 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 2 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 3 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 3 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 5 days ago