Welcome to the forum! This is getting too hot - you might end up cooking one of the nippers (if they are nippers). The showers might be OK - unti...
@transparent - here's the page with more details and images on what my heat pump has.
@transparent - I summarised the results here. What we actually found were wiring diagrams showing the PWM control cable (in addition to the power cabl...
@burtis - what seems to be happening in both our heat pumps is the flow rate is somehow capped at the lower end of their respective ranges, with the r...
If you know when it will go into DHW heating mode (because it is on a timer?) then it won't take much to get useful readings, say flow rate, LWT/RWT (...
There is also enough info there to calculate calculate power output, which is LWT/RWT delta t x flow rate/3.6 x circulating fluid specific heat (the d...
If you get this in time, can you do some more screen grabs as the water continues to heat. It would be particularly useful to see what the heat pump c...
I think that is a very good idea. Point out gently that doing these tasks will make life easier for everyone/what if the heat pump does destroy itself...
@burtis - another, more worrying point occurred to me. I think at some point you may have said you asked your installers not to add antifreeze, becaus...
That's interesting. I don't think I've ever seen a flow rate that low. My problem is the flow rate tends to be fixed at around 1.4m^3/h, and that cons...
It has been said that Latin is the last refuge of the linguistic scoundrel, but putting that aside, how about a recaleferator? If they got away with g...
Maybe combine our two ideas, and come up with Energy Teleporter? That sounds like the sort of thing any right thinking person would want for their hom...
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 57 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
That's probably the most important point, maybe see if ...
By cathodeRay , 36 minutes ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 1 hour ago
-
RE: How to choose Towel Rails for an ASHP
@jamespa yes, to essentially prevent them consuming unn...
By Mars , 1 hour ago
-
Thank you for raising your concerns. Customer safety, s...
By Mixergy , 3 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 3 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 4 hours ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 4 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 19 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 21 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 21 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 22 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 1 day ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 5 days ago