@transparent Both, Mitsubishi is inside, Samsung is in the Monoblock unit
@netdonkey Primary pump should run as follows: Heating demand on DHW demand on Defrost demand on Secondary pump should run as follows: He...
@netdonkey OK, so this Grundfoss pump should only turn on an off when required in heating mode as your system runs through a buffer, there will be som...
To add, the primary pump also can run for a while before the system fires up to confirm flow.
@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of ...
Perhaps develop a basic software, free online that allows the customer to put in most of the measurements and basic building fabric, just enough that ...
@jamespa Fair point, its good to know better standards and designs are getting covered under the MCS schemes. Perhaps once it all starts to come toget...
@iantelescope They say its as a result of the combi birth and delta T changing from 11 to 20! as tech got better it required less flow so all of the e...
@vcosmin Many people here will agree with you on that design issue. I watched the video and if they have 7 or 9m pump you should be well covered.
you will need to set the buffer up as a volumiser for the defrost if the installer has said it needs it for defrost and also make sure you have at eas...
@editor I will keep an eye out for that podcast, thank you. Just a side note relevant to buffers, rails separators and volumisers. I may not be corre...
@editor Can you do a podcast on standards of training, whats available, how engineers get trained, where they come from, what level they get trained t...
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 39 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Mmm. I have a service package with Mitsubishi which is...
By Abernyte , 6 minutes ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I couldn't agree more with this. Whilst I still have a...
By JamesPa , 10 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
Central heating still switched off and will be until Oc...
By AllyFish , 51 minutes ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
I think the problem you are having comes down almost en...
By JamesPa , 1 hour ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 16 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 17 hours ago
-
RE: Buffers, hot water and cooling
@jamespa Your reasonably close! Especially with warmer ...
By dgclimatecontrol , 19 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 1 day ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 2 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 3 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 3 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 3 days ago