Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regarding the use of RCBOs to connect PV inverters or storage batteries.
This is not yet part of the IET Electrical Wiring Regulations, but it is sufficiently serious that an amendment is being expedited.
Overview: household electrical circuits are wired from a Consumer Unit which contains a number of trips.
Most trips are there to prevent excessive current being passed through wires/cables. Those are MCBs (Miniature Circuit Breakers).
It is common for a consumer unit to have one or more RCDs (Residual Current Detectors).
These compare the outgoing current on the Live wire, with that being returned on the Neutral.
If there is an imbalance, the contacts will open to prevent fire or electric shock to someone who has touched a live cable.
Increasingly, electricians are fitting RCBOs for individual power circuits.
These combine the functions of an MCB and RCD.
They will open the contacts either for over-current, or because current is leaking away somewhere.
If a single-circuit RCBO trips out, then at least the lights remain on so you can see what's gone wrong!
RCDs and RCBOs both have a test button.
This should be pressed periodically to check that it will open the contacts to protect against electric shock
When solar panels or storage batteries are installed, it is not mandatory that the circuit is supplied from an RCBO. An MCB is sufficient.
However, many installers do use an RCBO to provide an extra level of safety for when it might be necessary for an inverter to undergo maintenance.
Most Solar Inverters and Storage Batteries are "Grid tied".
They export to the mains supply through the same wires which connect them to the consumer unit.
A grid-tied inverter will have a G98 certificate, and requires permission from the regional DNO to install it.
This common arrangement means that electricity will pass through the RCBO in either direction.
The RCBO contains a small amount of electronics to handle the current sensing.
When there is a fault (either over-current or earth-leakage) a solonoid is switched on, which opens the contacts.
If the RCBO was on a normal power circuit, opening the contacts would remove power from the electronics.
The trip would remain open until the lever was manually moved, and the solonoid would no longer be powered-on.
But if there is power still being applied in the reverse direction by an inverter or storage battery, when the contacts open, the solonoid remains energised.
Such a small solonoid will overheat and burn out.
The circuit can still be re-powered using the lever, but it will no longer be able to protect against electric shock.
The home owner won't know that.
The solution is to use a an RCBO specifically designed for bi-directional use.
A bi-directional RCBO has a third pair of contacts.
When the solonoid operates to open the trip, that 3rd contact set removes power from the electronics, and the solonoid coil is de-energised, preventing burn-out.
How can you tell if an RCBO is bi-directional?
Most RCBOs have arrows to show the direction of current, or have a label which denotes Supply and Load terminals.
A Bi-directional RCBO will not be marked for Supply and Load.
It may also have a set of arrows pointing in both directions.
If an RCBO isn't marked as being bi-directional, then it isn't.
The IET Wiring Regulations aren't retrospective.
When the amendment is released which specifies the need for a bi-directional RCBO, there will still be many thousands of installations which appear to have an operational RCBO, but it will only offer protection against over-current. It won't be acting to prevent fire or avoid electric shock.
It is up to forum members here to spread the word to others and advise that an existing RCBO is exchanged (by an electrician!) for a bi-directional type.
Save energy... recycle electrons!
This photo shows a bi-directional RCBO by Proteus at Redditch.
The symbols are correct, and the third-contact which the solonoid switches is visible in the diagram on the side.
What I still don't like is:
- the terminals being labelled 'In' and 'Out'
- no bi-directional symbol or marking on the part of the RCBO which remains visible to the householder after installation is completed
This particular RCBO is Type A
and Curve C... which defines the time it takes to trip due to over-current.
Most household MCBs and RCBOs are curve-B, which operates faster.
I use Curve-C trips to supply circuits which are likely to have large inductances connected (motors in a workshop or an inverter).
Update 28may24:
I have a response from Proteus Switchgear to say that they are already acting on the BEAMA directive and "will remove the in/out and also add on a bidirectional arrow symbol to the front of compliant devices"
The changes will filter through once existing stocks have been exhausted.
Save energy... recycle electrons!
- 25 Forums
- 1,619 Topics
- 34.9 K Posts
- 107 Online
- 1,889 Members
Join Us!
Latest Posts
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Received my Heat Geek quote this evening. Very detailed...
By Davesoa , 6 mins ago
-
RE: The good, the bad and the not that great – my heat pump installation
Your analysis is right but.. The number of Councill...
By JamesPa , 8 mins ago
-
RE: British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
It's done! Daikin Altherma 6kw; 180 litre Daikin tank...
By Lucia , 9 mins ago
-
RE: Ecodan - flow rates, sensors, settings
My bad…. the FTC6 does have separate speed settings as ...
By SUNandAIR , 15 mins ago
-
RE: Will heat pump heat hot water without increasing the temp in my home?
@toodles no battery. Inverter is wrong type for it. No...
By Ellyse , 29 mins ago
-
RE: Interesting new product for woodburners - Recoheat
There's a really interesting masonary stove that Marti...
By Lucia , 2 hours ago
-
RE: Battery sizing - How low can you go!
@judith Ive just had a quick look and I think its its s...
By bontwoody , 3 hours ago
-
RE: ECO4 Scheme and EPC ratings
What I did hear was the inspection was to be more in-de...
By Toodles , 4 hours ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
@rod Well as long as you are boxing the pipes in, I sup...
By bontwoody , 5 hours ago
-
RE: Air source heat pump roll call
Forum Handle: MikeH Manufacturer: Aira Model:Aira 8...
By MikeH , 7 hours ago
-
I was intrigued by this post so had a look on Amazon as...
By Judith , 8 hours ago
-
Huwaei Luna 2000 Charge and Discharge Limits
I have a Luna 2000 5kWh battery module and have found i...
By bontwoody , 9 hours ago
-
RE: My British Gas – Heat Force ASHP Installation: A Frustrating Experience
@tomaszw For ASHP, in particular, my use of a reputable...
By IanMK13 , 10 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
@transparent To the Homely website hackerchewerly. Now ...
By Toodles , 11 hours ago
-
Thats great to read! Have you any detailed figures? Is...
By Judith , 12 hours ago
-
RE: Calculating inverter size to match battery size
I think I understand C rates now. The C rate is the rat...
By Homonid , 22 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A
Wednesday afternoon, means another podcast episode, and...
By Mars , 23 hours ago
-
Samsung Gen6 Room temp vs Outlet temp
I've been using my samsung gen6 with a room temp contro...
By EcoBaker , 23 hours ago
-
Wow! Great photos - thank you. Let me re-post two of ...
By Transparent , 24 hours ago
-
RE: Say hello and introduce yourself
These comments are pretty important! I'll assume you ...
By Transparent , 1 day ago
Latest Topics
-
Battery sizing - How low can you go!
By bontwoody 4 hours ago
-
Huwaei Luna 2000 Charge and Discharge Limits
By bontwoody 9 hours ago
-
Samsung Gen6 Room temp vs Outlet temp
By EcoBaker 23 hours ago
-
Which liquid is used in the central heating loop?
By TRBob 2 days ago
-
Interesting new product for woodburners - Recoheat
By Tim441 2 days ago
-
alternative to Homely - HavenWise. Anyone used it?
By Tim441 2 days ago
-
Calculating inverter size to match battery size
By Homonid 4 days ago
-
Agile: average import cost vs other tariffs?
By Tim441 6 days ago