Safety update; RCBOs supplying inverters or storage batteries
BEAMA have issued a safety update (March 2024) regarding the use of RCBOs to connect PV inverters or storage batteries.
This is not yet part of the IET Electrical Wiring Regulations, but it is sufficiently serious that an amendment is being expedited.
Overview: household electrical circuits are wired from a Consumer Unit which contains a number of trips.
Most trips are there to prevent excessive current being passed through wires/cables. Those are MCBs (Miniature Circuit Breakers).
It is common for a consumer unit to have one or more RCDs (Residual Current Detectors).
These compare the outgoing current on the Live wire, with that being returned on the Neutral.
If there is an imbalance, the contacts will open to prevent fire or electric shock to someone who has touched a live cable.
Increasingly, electricians are fitting RCBOs for individual power circuits.
These combine the functions of an MCB and RCD.
They will open the contacts either for over-current, or because current is leaking away somewhere.
If a single-circuit RCBO trips out, then at least the lights remain on so you can see what's gone wrong!
RCDs and RCBOs both have a test button.
This should be pressed periodically to check that it will open the contacts to protect against electric shock
When solar panels or storage batteries are installed, it is not mandatory that the circuit is supplied from an RCBO. An MCB is sufficient.
However, many installers do use an RCBO to provide an extra level of safety for when it might be necessary for an inverter to undergo maintenance.
Most Solar Inverters and Storage Batteries are "Grid tied".
They export to the mains supply through the same wires which connect them to the consumer unit.
A grid-tied inverter will have a G98 certificate, and requires permission from the regional DNO to install it.
This common arrangement means that electricity will pass through the RCBO in either direction.
The RCBO contains a small amount of electronics to handle the current sensing.
When there is a fault (either over-current or earth-leakage) a solonoid is energised (switched on), which opens the contacts.
If the RCBO was on a normal power circuit, opening the contacts would remove power from the electronics.
The trip would remain open until the lever was manually moved, and the solonoid would no longer be powered-on.
But if there is power still being applied in the reverse direction by an inverter or storage battery, when the contacts open, the solonoid remains energised.
Such a small solonoid will overheat and burn out.
The circuit can still be re-powered using the lever, but it will no longer be able to protect against electric shock.
The home owner won't know that.
The solution is to use a an RCBO specifically designed for bi-directional use.
A bi-directional RCBO has a third pair of contacts.
When the solonoid operates to open the trip, that 3rd contact set removes power from the electronics, and the solonoid coil is de-energised, preventing burn-out.
How can you tell if an RCBO is bi-directional?
Most RCBOs have arrows to show the direction of current, or have a label which denotes Supply and Load terminals.
A Bi-directional RCBO will not be marked for Supply and Load.
It may also have a set of arrows pointing in both directions.
If an RCBO isn't marked as being bi-directional, then it isn't.
The IET Wiring Regulations aren't retrospective.
When the amendment is released which specifies the need for a bi-directional RCBO, there will still be many thousands of installations which appear to have an operational RCBO, but it will only offer protection against over-current. It won't be acting to prevent fire or avoid electric shock.
It is up to forum members here to spread the word to others and advise that an existing RCBO is exchanged (by an electrician!) for a bi-directional type.
Save energy... recycle electrons!
This photo shows a bi-directional RCBO by Proteus at Redditch.
The symbols are correct, and the third-contact which the solonoid switches is visible in the diagram on the side.
What I still don't like is:
- the terminals being labelled 'In' and 'Out'
- no bi-directional symbol or marking on the part of the RCBO which remains visible to the householder after installation is completed
This particular RCBO is Type A
and Curve C... which defines the time it takes to trip due to over-current.
Most household MCBs and RCBOs are curve-B, which operates faster.
I use Curve-C trips to supply circuits which are likely to have large inductances connected (motors in a workshop or an inverter).
Update 28may24:
I have a response from Proteus Switchgear to say that they are already acting on the BEAMA directive and "will remove the in/out and also add on a bidirectional arrow symbol to the front of compliant devices"
The changes will filter through once existing stocks have been exhausted.
Save energy... recycle electrons!
- 22 Forums
- 2,032 Topics
- 44.3 K Posts
- 38 Online
- 3,237 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
Welcome to the forums. It’s clear that you’ve taken t...
By Mars , 13 minutes ago
-
RE: help sizing rads based on room by room heat loss
By JamesPa , 46 minutes ago
-
Hi Thanks for the reply, the walls are being constru...
By Fingers , 2 hours ago
-
RE: Agile: average import cost vs other tariffs?
@old_scientist I have been imitating a hawk towards the...
By Toodles , 3 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 3 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 7 hours ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 7 hours ago
-
The Rise and Fall of Europe’s Most Generous Green Subsidy
This story came to my attention thanks to Graham Hendra...
By Mars , 7 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 7 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
From the Full SAP Report: Space heating requirements:...
By trebor12345 , 8 hours ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 12 hours ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 14 hours ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 15 hours ago
-
RE: Performance of Heat Pumps in Mild Weather
@heatgeek The flow rate isnt controlled by Mitsub...
By RobS , 17 hours ago
-
RE: Say hello and introduce yourself
I might put a couple of speakers in the ceiling if fund...
By Fingers , 1 day ago
-
RE: Bathroom Radiator replacement
@rob-nezard can you please offer your professional advi...
By Mars , 2 days ago
-
-
RE: Questions on my Hitachi Yutaki SCombi Heat Pump
OK, thats good and low. With low flow temperatures lik...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa “They are all equal but, some are more equal t...
By Toodles , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
@cliffhanger Mine has a 'space heating off' setting! O...
By JamesPa , 2 days ago