Any advice for new solar installation? SW facing extension
- Single storey
- Floor area 40 sq m (8m x 5m)
- Steel framed
- Mono-pitch
- facing - approx South-west
- Low pitch - approx 8 - 12 degrees
- Easijoists roof trusses (weight not an issue)
- Approx roof size 8.2m x 5.5m
- Significant shading from 2 storey existing building until sun comes round. so will need strings, optimisers and/or suitable panel models accordingly? Once sun arrives there is no shading afaik for rest of day
- Needs optimum coverage, sizing, kWh output vs cost
- Target 16 panels
- we think pitch may be around 10 degrees -
- Install on-roof option (metal roof with standing seams)?
- other options?
- Install on-roof option (metal roof with standing seams)?
- Add GivEnergy All-in-one battery (or similar).
1. what do people feel sweet spot is for panels these days - perhaps 415 - 425w?
2. In the scenario above is there any point in adding optimisers?
3. What other options are suggested for batteries that offer EPS capability? I'm thinking Givenergy AIO (cheaper than Tesla). I think Solaredge have a DC coupled offering now but dont know much about prose & cons! Any others to consider?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
What would be the purpose of this new PV array (e.g. trying to extend the time where the heat pump can be run off solar, or maximise income from an export tariff)? You already have quite a significant PV setup, so getting the DNO to agree to more export power (or export equipment) may be tricky.
Have you tried to model this scenario in an online tool (e.g. easy-pv, or else the Solaredge Designer)? This might give a better idea about the benefit of micro-inverters of optimisers, although I guess that it may not offer great RoI (and tie you into a specific ecosystem).
@chickenbig I should have been clearer! This is a separate house that has no solar or batteries currently. I'm hoping DNO will accept around 6.5kw array?
Majority of solar prod will of course be in the summer when ashp not in use but I would hope that we can use a decent part of production in shoulder months and export excess using Octopus Fixed 15p
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441This is a separate house that has no solar or batteries currently.
That makes life a lot easier!
I still think that modelling the roof and shading is the only way to assess whether micro-inverters or optimisers are worth it. You could try hiring someone to perform (and explore) the design. A quick internet searching reveals fiverr and upwork as freelancer platforms, but have not used them. The advantage of this is you could explore many different options rather than be limited by what an actual installer favours.
Is there a particular reason you would favour an all-in-one system? If cost is of concern can I point you to the posts about the DIY Mason Battery 🙂
@chickenbig thanks for thoughts! I will initially talk to installers as well as gathering input here etc. I guess its possible such independent 3rd party input would help - overall I think my scenario is relatively straightforward but definitely want to check I'm not missing something that I come to regret! Clearly no point in adding optimisers if unnecessary but equally would not wish to find out later I should have done it.
I guess my objectives are a mix of maximising solar for home use inc ASHP & EV as well as wishing to have EPS.
AIO has advantages of easier/quicker installation, fast charge/discharge rates as well as whole home EPS. Obviously on a long outage we would need to reduce draw to keep it going - so would switch off ashp if it looked like an issue.
I don't think I have the knowledge/skills/confidence to take on something like the Mason - even though the costs look impressive!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441AIO has advantages of easier/quicker installation, fast charge/discharge rates as well as whole home EPS.
To be fair, hybrid inverters can offer this, and without locking you into a single battery supplier. AIO systems are hybrid inverters and batteries in matching clothes. Having gone through the ordeal of getting a Sunsynk inverter and Mason batteries to work together, I think most of the problems were caused by the installer (poor installation, absence of configuration of firmware and inverter settings, poor configuration of other things). Sunsynk technical support were helpful, although their documentation and product naming were unhelpful. I'm strongly considering getting an 8kW Sunsynk Ecco inverter (and two Mason batteries) for my own home.
A half-way-house between Seplos Mason and AIO is the rack-mounted battery. This is potentially double the price per kWh (e.g. Fogstar https://www.fogstar.co.uk/collections/server-rack-batteries/products/fogstar-energy-48v-15kwh-rack-battery-bundle which has heated batteries, or else stringing together Pylon batteries).
It may be (financially) worth splitting the contract for installing the PV and inverter (and grid/backup connections) from the installation of batteries, even if there is a 20% VAT penalty. Perhaps @sikorsky92 has a price-list they are able to share with you as from their comments they seem to be a Mason builder/installer.
And coming back to "any other AIO to look at", have you seen Livoltek? From the datasheet there are different inverter powers, and batteries can be added in 5.12kWh chunks. https://www.youtube.com/watch?v=A513FwteZjU makes some interesting points about this product which was (is?) still under development.
If you do decide to include optimisers, it would be worth comparing the current warranty coverage of the different options. For example, Tigo TS4 are only 25 years if combined with their CCA/TAP remote monitoring system. TS4 used without internet connection is 5 years.
The CCA/TAP remote monitoring system is warranted for 5 years.
Mitsubishi Ecodan 11.2kW R32 ASHP; Ecodan DHW cylinder; UFH+rads
20x430W Jinko TOPCON Tiger Neo solar; Luxpower 6+4kW hybrid inverter; 20kWh LFP battery storage
PHEV; Zappi charger
@chickenbig thanks.. i will take a look. Lots to learn!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@skd its a good point
I had a small Solaredge system installed in 2015... Installer never properly registered the system and did not setup monitoring... and gone bust.
When i realised earlier this year (after a year!) that prod was down i went on big learning curve. Setup the monitoring ... and found one optimiser had failed. In fairness Solaredge were very helpful and replaced under warranty. Since then a 2nd failed and was replaced as well. Luckily easily accessible from flat roof so managed to do it myself.
So yes, warranty definitely worth looking at.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441warranty definitely worth looking at
And one which pays for scaffolding to access the faulty equipment! Having said that, some SolarEdge installers place the optimizer in the loft space;
although this is in a garage so may not get as hot as in a loft. Web-searching for SolarEdge failures in Australia makes for some interesting reading, although their heat is more extreme than here.
-
Solar Power Output – Let’s Compare Generation Figures
4 weeks ago
-
Plug and play solar. Thoughts?
6 months ago
-
Supplier choices for PV system
2 years ago
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 273 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Mitsu PUHZ-SW120YHA + EHSC-VM20Uk - Performance
@jamespa Thanks for your comments James. The answer t...
By DavidAlgarve , 18 minutes ago
-
RE: Water Hammer After Heat Pump Install
From OPs description I had the impression (quite possib...
By JamesPa , 2 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 20 hours ago
-
RE: Help needed with Grant Aerona 3 issues
Noted. Its a pity you didnt capture the flow rate and ...
By JamesPa , 1 day ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 1 day ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 1 day ago
-
RE: Changing from 4-port buffer to volumizer
@andy1618 see the very sage advice from @editor above. ...
By JamesPa , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 2 days ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 2 days ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 2 days ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
Also, though they weren’t prepared to match the price t...
By Toodles , 2 days ago
-
RE: How long will your energy contract last?
My INTELLI-FIX-12M-25-08-29 has less than 12 months to ...
By Batpred , 2 days ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
Then, perhaps @toodles , you should've made a submissio...
By Transparent , 2 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I am wondering if anyone with an EV could find the 7p/k...
By Batpred , 2 days ago
-
Possibly, but it would also reduce DeltaT across the em...
By JamesPa , 2 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@cathoderay It was reminiscent of the BBC Open Universi...
By Toodles , 2 days ago
-