Pipes and cables exposed on roof
Hi Hope someone can help. We've saved up and had a local installer put solar thermal on our roof for hot water. But the pipes and wires are visible on top of the roof at the front of the house as you walk/drive up to the house. They look all ragged and are just attached with lots and lots of cable ties. Is this normal? We've said we're worried birds/weather might damage them, and asked for the installer to cover them in some sort of tubing, but they have refused, saying they've always done it this way and have never had any problems. Does this look standard practice? Don't know as have never seen any other solar thermal pipes on roofs. Thanks, Michelle
Apologies for not responding earlier to this @michellec
There are three factors which dictate the pipe coverings for solar thermal:
- adequate insulation... especially on the heat output leading back into the house
- preventing ingress of rain
- preventing degradation by the UV component in sunlight
I can see how the installers have used a secondary layer of plastic to keep rain and sunlight off the inner insulation.
So they're clearly aware of the issues.
But I don't understand why they didn't use UV-resistant nitrile-rubber insulation in the first place.
That looks like the standard black Class-O closed-cell insulation, but is usually marked specifically for 'solar' or 'external'.
In any case, it's still important that the upper end of the insulation tube is sealed, usually with mastic.
Otherwise rain will get between the insulation and the pipe. As it runs out, it carries away the heat.
I don't like seeing nylon cable ties used on insulation because it compresses the 'foam', reducing its insulating properties.
Cable-ties can also become brittle in sunlight.
The sides of the split in the insulation should be stuck together.
If the split doesn't already have pre-glued strips, then apply your own glue.
The correct glue for nitrile rubber is a contact adhesive.
Whereabouts are you in the UK?
The slate roof suggests Wales or the West Country.
Is the scaffolding still in place for you to get these photos?
Save energy... recycle electrons!
@transparent Thank you so much for replying. Yes the scaffold is still there (the roof they did is still leaking!) Can the insulation you describe be put on now? Could you recommend someone in the southwest (we are near Bude)? Many thanks, Michelle
Hi Michelle,
It's a pity you didn't mention that earlier.
There was a visit by a renowned exponent of good building practice holding a walkabout seminar at Nansledan earlier this week.
That's just 40-miles along the coast from you.
He'd brought along a couple of civil servants from London, to show them how things should be done...
Yes, the UV-resistant pipe insulation can be fitted now.
Are you sure that you don't want to put it in place yourself?
It's not that difficult a job.
Alternatively, you need a teenager with OCD!
I don't know of a builder/plumber who undertakes pedantically-correct work in Bude.
But the usual approach in the West Country is to ask at the post office or the pub.
This an area of UK where you can still get recommendations by simply talking with neighbours. 🙂
Save energy... recycle electrons!
@michellec I suspect @transparent means neat and tidy work, which you have reasonably expected. Plus with the detailed implementation to keep water out and heat in.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
No Michelle, I'm not making any assessment of your own skills 🤣
The issue here is that work you need doing is pretty straightforward.
There will plenty of people who would have a go at it.
But the quality of the work is important.
For many years I was working with a German software programmer.
His coding was amazingly slick and accurate...
... as was his grasp of the English language, because he used to correct my grammar.
That's the sort of approach needed to properly insulate those two pipes.
Save energy... recycle electrons!
@michellec, this is an area where the classic 80:20 rule is most evident - 80% of the benefit for 20% of the effort.
Any tradesperson will inevitably be applying the rule since their time costs you and them money, but the insulation job you describe is DIY- friendly enough that, with that bit of pedantry applied, brings that other 20% well within reach. It’s not that you have been pedantic thus far but rather that you could probably afford the extra time to apply the attention to detail that marks out a piece of work as first-rate.
Context matters, of course; I am pedantic to the point of anal retention with my woodwork but rather slapdash with any plumbing I (rarely and under duress) undertake.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 314 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Predicted Heat Loss from MCS calcs vs EPC vs actual
My gut feeling is that the heat pump is right sized. ...
By Tim441 , 12 minutes ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
@jamespa Thanks for taking the time to answer. I wasn'...
By iotum , 32 minutes ago
-
RE: Heat pump not reaching flow temperature
Peak Energy Products most recent accounts (to June 2024...
By JamesPa , 39 minutes ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 2 hours ago
-
RE: Running from backup generaor in powercut?
@batpred In our case, 3 times each day when the Octopus...
By Toodles , 2 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Hi @sheriff-fatman Cycling at 5C and below is usuall...
By RobS , 3 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
The diagram describes what happens inside the Solis. Al...
By Batpred , 4 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Here's the latest Fogstar ready built pack....
By Bash , 4 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick yes, even though the current system is ru...
By Tim441 , 4 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Solis confirmed that the S6 works with a single battery...
By Batpred , 5 hours ago
-
RE: Who has a V2G EV installation
I am wondering if in any V2X, would the car battery eve...
By Batpred , 5 hours ago
-
RE: Setback savings - fact or fiction?
Yes, by calculating it manually from the minute data, w...
By cathodeRay , 7 hours ago
-
Fan unit Making terrible noise HELP!!
One of a pair of fan units on an Earth Save Classic II ...
By GutoFfowc , 7 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
OK. I think your system, which seems well designed, is...
By JamesPa , 9 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 22 hours ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 1 day ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 1 day ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk I'm observing my own system at low temperatures ...
By dr_dongle , 1 day ago