Pipes and cables exposed on roof
Hi Hope someone can help. We've saved up and had a local installer put solar thermal on our roof for hot water. But the pipes and wires are visible on top of the roof at the front of the house as you walk/drive up to the house. They look all ragged and are just attached with lots and lots of cable ties. Is this normal? We've said we're worried birds/weather might damage them, and asked for the installer to cover them in some sort of tubing, but they have refused, saying they've always done it this way and have never had any problems. Does this look standard practice? Don't know as have never seen any other solar thermal pipes on roofs. Thanks, Michelle
Apologies for not responding earlier to this @michellec
There are three factors which dictate the pipe coverings for solar thermal:
- adequate insulation... especially on the heat output leading back into the house
- preventing ingress of rain
- preventing degradation by the UV component in sunlight
Â
I can see how the installers have used a secondary layer of plastic to keep rain and sunlight off the inner insulation.
So they're clearly aware of the issues.
But I don't understand why they didn't use UV-resistant nitrile-rubber insulation in the first place.
That looks like the standard black Class-O closed-cell insulation, but is usually marked specifically for 'solar' or 'external'.
Â
Â
In any case, it's still important that the upper end of the insulation tube is sealed, usually with mastic.
Otherwise rain will get between the insulation and the pipe. As it runs out, it carries away the heat.
Â
I don't like seeing nylon cable ties used on insulation because it compresses the 'foam', reducing its insulating properties.
Cable-ties can also become brittle in sunlight.
The sides of the split in the insulation should be stuck together.
Â
If the split doesn't already have pre-glued strips, then apply your own glue.
The correct glue for nitrile rubber is a contact adhesive.
Â
Whereabouts are you in the UK?
The slate roof suggests Wales or the West Country.
Is the scaffolding still in place for you to get these photos?
Â
Save energy... recycle electrons!
@transparent Thank you so much for replying. Yes the scaffold is still there (the roof they did is still leaking!) Can the insulation you describe be put on now? Could you recommend someone in the southwest (we are near Bude)? Many thanks, Michelle
Hi Michelle,
It's a pity you didn't mention that earlier.
There was a visit by a renowned exponent of good building practice holding a walkabout seminar at Nansledan earlier this week.
That's just 40-miles along the coast from you.
He'd brought along a couple of civil servants from London, to show them how things should be done...
Â
Yes, the UV-resistant pipe insulation can be fitted now.
Are you sure that you don't want to put it in place yourself?
It's not that difficult a job.
Alternatively, you need a teenager with OCD!
I don't know of a builder/plumber who undertakes pedantically-correct work in Bude.
But the usual approach in the West Country is to ask at the post office or the pub.
This an area of UK where you can still get recommendations by simply talking with neighbours. 🙂Â
Â
Save energy... recycle electrons!
@michellec I suspect @transparent means neat and tidy work, which you have reasonably expected. Plus with the detailed implementation to keep water out and heat in.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
No Michelle, I'm not making any assessment of your own skills 🤣Â
The issue here is that work you need doing is pretty straightforward.
There will plenty of people who would have a go at it.
But the quality of the work is important.
Â
For many years I was working with a German software programmer.
His coding was amazingly slick and accurate...
... as was his grasp of the English language, because he used to correct my grammar.
That's the sort of approach needed to properly insulate those two pipes.
Save energy... recycle electrons!

@michellec, this is an area where the classic 80:20 rule is most evident - 80% of the benefit for 20% of the effort.
Any tradesperson will inevitably be applying the rule since their time costs you and them money, but the insulation job you describe is DIY- friendly enough that, with that bit of pedantry applied, brings that other 20% well within reach. It’s not that you have been pedantic thus far but rather that you could probably afford the extra time to apply the attention to detail that marks out a piece of work as first-rate.
Context matters, of course; I am pedantic to the point of anal retention with my woodwork but rather slapdash with any plumbing I (rarely and under duress) undertake.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
- 21 Forums
- 1,983 Topics
- 43.2 K Posts
- 31 Online
- 2,309 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@sunandair I can't get my system higher than 35 or 3...
By davidnolan22 , 40 minutes ago
-
RE: Confused about Samsung Gen6 Hot Water Controller
As far as I am aware the only way to persuade the heat...
By DerekDeLeon , 2 hours ago
-
RE: Nibe F2040 ASHP PCB failure
@delta I’ve raised this with NIBE today. Their team is ...
By Mars , 10 hours ago
-
RE: Are MCS are finally improving (some of) their guidelines?
Encouragement of installers to take account of the emit...
By JohnR , 10 hours ago
-
RE: Smart TRV experiences (ideally integrating with Midea heat pump)
Yes, I'd read that and already knew that LSVs exhibit a...
By madbilly , 10 hours ago
-
In our case the pipe run for the heat pump is short and...
By madbilly , 10 hours ago
-
Plug and play solar. Thoughts?
What do you think of these plug-and-play Balcony Solar...
By Lucia , 13 hours ago
-
@toodles no, unfortunately we don’t have access to the ...
By Simon and Zoe , 13 hours ago
-
RE: The EPC Dilemma: How Current Ratings Fail Heat Pumps
Hi, im not an expert on EPCs but today got a D for my 1...
By rodwebster , 14 hours ago
-
@sandman1600 What I mean is, your UFH power is 79wm2...
By davidnolan22 , 14 hours ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you James for such a complete write up. We also h...
By Judith , 15 hours ago
-
RE: Ecodan Auto Adapt Questions
It wasnt me that mentioned this, was someone else, I wa...
By JamesPa , 15 hours ago
-
RE: Renewables & Heat Pumps in the News
In a move that potentially promises to benefit homeowne...
By Mars , 15 hours ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
I have the same, so equally interested in the answer. ...
By JamesPa , 15 hours ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
Somebody has to pay for their ignorance! In fairness ...
By JamesPa , 20 hours ago
-
Thats simply not true (to any material extent), which i...
By JamesPa , 1 day ago
-
Database of heat pump performance data?
Hi all, I really like Heatpunk, especially the way th...
By madbilly , 1 day ago
-
RE: Air source heat pump roll call
Good idea 🙂 Manufacturer: MideaModel:10kW R32 Monob...
By madbilly , 1 day ago
-
RE: What is the best approach for primaries in heat pump installations?
Don't forget there is no such thing as zero loss insula...
By Judith , 1 day ago
-
RE: Battery storage to run Heat Pump.
@transparent Flexibility Services are different to w...
By Lucia , 2 days ago
Latest Topics
-
Plug and play solar. Thoughts?
By Lucia 13 hours ago
-
By JamesPa 16 hours ago
-
Vaillant water pressure gauge vs Analogue gauge
By jeegnesh 17 hours ago
-
Database of heat pump performance data?
By madbilly 1 day ago
-
By madbilly 1 day ago
-
Confused about Samsung Gen6 Hot Water Controller
By ntruby 2 days ago
-
help with new bathroom and towel radiator
By AdamK 3 days ago
-
Grant Aerona fine tuning advice needed
By Stopbar 3 days ago