Pipes and cables exposed on roof
Hi Hope someone can help. We've saved up and had a local installer put solar thermal on our roof for hot water. But the pipes and wires are visible on top of the roof at the front of the house as you walk/drive up to the house. They look all ragged and are just attached with lots and lots of cable ties. Is this normal? We've said we're worried birds/weather might damage them, and asked for the installer to cover them in some sort of tubing, but they have refused, saying they've always done it this way and have never had any problems. Does this look standard practice? Don't know as have never seen any other solar thermal pipes on roofs. Thanks, Michelle
Apologies for not responding earlier to this @michellec
There are three factors which dictate the pipe coverings for solar thermal:
- adequate insulation... especially on the heat output leading back into the house
- preventing ingress of rain
- preventing degradation by the UV component in sunlight
I can see how the installers have used a secondary layer of plastic to keep rain and sunlight off the inner insulation.
So they're clearly aware of the issues.
But I don't understand why they didn't use UV-resistant nitrile-rubber insulation in the first place.
That looks like the standard black Class-O closed-cell insulation, but is usually marked specifically for 'solar' or 'external'.
In any case, it's still important that the upper end of the insulation tube is sealed, usually with mastic.
Otherwise rain will get between the insulation and the pipe. As it runs out, it carries away the heat.
I don't like seeing nylon cable ties used on insulation because it compresses the 'foam', reducing its insulating properties.
Cable-ties can also become brittle in sunlight.
The sides of the split in the insulation should be stuck together.
If the split doesn't already have pre-glued strips, then apply your own glue.
The correct glue for nitrile rubber is a contact adhesive.
Whereabouts are you in the UK?
The slate roof suggests Wales or the West Country.
Is the scaffolding still in place for you to get these photos?
Save energy... recycle electrons!
@transparent Thank you so much for replying. Yes the scaffold is still there (the roof they did is still leaking!) Can the insulation you describe be put on now? Could you recommend someone in the southwest (we are near Bude)? Many thanks, Michelle
Hi Michelle,
It's a pity you didn't mention that earlier.
There was a visit by a renowned exponent of good building practice holding a walkabout seminar at Nansledan earlier this week.
That's just 40-miles along the coast from you.
He'd brought along a couple of civil servants from London, to show them how things should be done...
Yes, the UV-resistant pipe insulation can be fitted now.
Are you sure that you don't want to put it in place yourself?
It's not that difficult a job.
Alternatively, you need a teenager with OCD!
I don't know of a builder/plumber who undertakes pedantically-correct work in Bude.
But the usual approach in the West Country is to ask at the post office or the pub.
This an area of UK where you can still get recommendations by simply talking with neighbours. 🙂
Save energy... recycle electrons!
@michellec I suspect @transparent means neat and tidy work, which you have reasonably expected. Plus with the detailed implementation to keep water out and heat in.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
No Michelle, I'm not making any assessment of your own skills 🤣
The issue here is that work you need doing is pretty straightforward.
There will plenty of people who would have a go at it.
But the quality of the work is important.
For many years I was working with a German software programmer.
His coding was amazingly slick and accurate...
... as was his grasp of the English language, because he used to correct my grammar.
That's the sort of approach needed to properly insulate those two pipes.
Save energy... recycle electrons!

@michellec, this is an area where the classic 80:20 rule is most evident - 80% of the benefit for 20% of the effort.
Any tradesperson will inevitably be applying the rule since their time costs you and them money, but the insulation job you describe is DIY- friendly enough that, with that bit of pedantry applied, brings that other 20% well within reach. It’s not that you have been pedantic thus far but rather that you could probably afford the extra time to apply the attention to detail that marks out a piece of work as first-rate.
Context matters, of course; I am pedantic to the point of anal retention with my woodwork but rather slapdash with any plumbing I (rarely and under duress) undertake.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
- 21 Forums
- 1,960 Topics
- 42.5 K Posts
- 49 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@johnr An extra rad was installed in the lounge when th...
By BAMi , 6 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 39 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 11 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 15 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 20 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 23 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 24 hours ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
Latest Topics
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 minutes ago
-
SolarPV tables / online calculator
By MichelleC 7 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 19 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 21 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago